LOTO question

I have what may seem like a dumb question to a lot of your guys but here goes.
We have a LOTO system in place and depending on what you are working on decides what you lock out. But, The cabinets with the switch on the doors puzzle me. I am wireing up a 480 drop off of one of them now and if I lock the door then I can not open it to work. If I open it then put the lock on the right place it does nothing for me since all one has to do is turn the knob with a pair of grips, and power is back on regardless of the lock being in place.

Anyone else have this situation and what do you do about it?
  Reply With Quote
Old October 9th, 2006, 06:55 PM   #2
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 3,974
Where is the cabinet power coming from? can you lock it out at the bucket feeding the cabinet?

Also the majority of the mains that I have seen, you can lock out at the main, not just on the outside of the cabinet....so what I have done, is open the cabinet and place the lock on the switch...not on the handle on the door
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers (New ControlLogix), Fluke Meters, Programming Lessons, MicroLogix 1400, 1100, 1000 and 1762-I/O.... all your automation needs
  Reply With Quote
Old October 9th, 2006, 07:06 PM   #3
plcnewbie
Member
United States

plcnewbie is offline
 
plcnewbie's Avatar
 
Join Date: Jan 2005
Location: Missouri
Posts: 220
Some of the mains give you that option and some do not have it. I wonder why then they put the switches on the doors at all.Maybe we need to rethink some of the procedures on a few of our machines??
  Reply With Quote
Old October 9th, 2006, 07:14 PM   #4
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 3,974
Just looked the ones that don't, the LOTO procedure points to the main that is feeding the cabinet

And yes, I am also not a fan of the twist lock on the door style either
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers (New ControlLogix), Fluke Meters, Programming Lessons, MicroLogix 1400, 1100, 1000 and 1762-I/O.... all your automation needs
  Reply With Quote
Old October 9th, 2006, 09:47 PM   #5
monkeyhead
Member
United States

monkeyhead is offline
 
monkeyhead's Avatar
 
Join Date: Sep 2004
Location: I'm right here
Posts: 656
Our policy is to lock out the source breaker if work inside the cabinet needs to be done. Each cabinet gets it's own breaker in the source distribution panel.

Locking out the cabinet so a field device can be serviced can be done with the handle lockout point on the cabinet. But this is not a suitable lockout point for work inside the cabinet because of the issues you mentioned above.

The idea is that if working in the cabinet everything must be dead including the power feed.

On some of our machines, we've mounted a seperate lockable disconnect to the side of the cabinet, so the power feed can be locked out without having to run back to the source breaker.
  Reply With Quote
Old October 9th, 2006, 09:48 PM   #6
Doug_Adam
Member
Australia

Doug_Adam is offline
 
Doug_Adam's Avatar
 
Join Date: Sep 2002
Location: Perth
Posts: 949
We try to engineer around this. Some methods we use are:
1, Switch on the side of the cabinet, not on the door. Only works if there is room on the side, and no plans to ever mount another cabinet on that side
2, Mount the whole CB on the door. This way, when the door opens, the CB comes with it and can remain locked. The down side is that it is only feasible for small cabinets.
3, Separate door for the isolator, this is best for the larger sized feeds. You can work on everything except the CB/isolator. Down side is that this method is difficult to re-fit on a board, you generally have to buy a special board for this to work.
4, Tag out the open board. Once you have opened the board and switched off the power, put danger tags on the isolation handle and the isolator or CB. This is not as good as lock out, but it is leagle for situations where lock out is not practicable (in Western Australia).
  Reply With Quote
Old October 9th, 2006, 10:04 PM   #7
Jim Dungar
Member
United States

Jim Dungar is offline
 
Join Date: Apr 2002
Location: WI
Posts: 1,152
There are some mechanisms that can be locked with the door open. Square D's 9421 line of breaker mechanisms is one style, I am not sure but I think the fusible ones from Ferraz are also.

NFPA 79 makes a statement suggesting(?) the lockout means to be independent of the door, so maybe they will become more common.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
1756-ENBT Yellow Question Mark Coachman LIVE PLC Questions And Answers 4 October 9th, 2006 04:47 PM
OT..Question for Elevator Mike!! darrenj LIVE PLC Questions And Answers 35 March 30th, 2006 02:09 AM
DDE Excel question mrdmrd LIVE PLC Questions And Answers 3 December 7th, 2005 06:56 AM
Interesting question? sirhiss2 LIVE PLC Questions And Answers 6 December 1st, 2005 08:30 AM
Omron PLC and ethernetmodule question wwauters LIVE PLC Questions And Answers 3 February 21st, 2005 11:35 PM


All times are GMT -5. The time now is 01:07 AM.


.