Let's look at the Path for your MSG instruction. This tells the message how to navigate from the initiating controller to the target controller, including the hops across the backplane and across the IP network.
CIP Paths are well explained in the Help file for RSLogix 5000. They are simply pairs of numbers with a Module Port and an Network Address. Port 1 is the backplane, Port 2 is the network port. Backplanes are considered networks too, with slot numbers for addresses. Path elements are separated by commas.
For your setup, the path would be
1, 1, 2, 10.133.22.13, 1, 0
the initial "1, 1" might be replaced with the name of your local EtherNet/IP module if it's in the I/O tree.
Produced and Consumed Tags might be an alternate method of exchanging data between these controllers, if they are on the same local IP subnet.