GE AF300 G11 VFD, 230 VAC, 3phase .25HP
Does any one know if you can wire this drives iput single phase? Thats what i am being told by a rep but cant find any docs to support, i would really like to know before i buy it. I am just putting a small demonstrator together, any help appreciated.
|
|
|
|
#2 |
|
Lifetime Supporting Member + Moderator
|
A couple of weeks ago I had a 460 volt AF300 P11 and motor in my office to do some bench testing. I don't have three phase power in my office, so I connected 110 VAC to the secondary of a small control power transformer and connected the primary to the drive. It worked fine driving a motor under no-load conditions.
Most VFDs can be operated on single phase. It makes sense when you think about how they work. VFDs rectify the incoming AC to DC and then manufacture a waveform at the output terminals. |
|
|
|
#3 |
|
Member
|
Thanks Steve
|
|
|
|
#4 |
|
Member
|
Using a single phase step up transformer will do the job under no load conditions. The rectifier diodes in the inverter can withstand the higher current (you're using only 4 diodes in single phase in stead of 6 when using 3 phase supply).
You might get 'under voltage' errors when running full load: Rectifying 3-phase AC results in a DC voltage with a mere 3% ripple, single phase rectifiers will have ripple near 50%. Try to add an extra capacitor to the DC bus, if these errors occur. |
|
|
|
#5 |
|
Member
![]() Join Date: May 2002
Location: Kalamazoo MI
Posts: 1,915
|
As a general rule, a drive rated for three phase input power should be derated 50% when operated on single phase power of the same voltage.
Adding a capacitor to the DC bus is not a good idea. The drive warranty will almost certainly be voided and the charging and discharging circuitry will be stressed beyond the design levels. Buying a drive that is properly sized to the load AFTER the derate mentioned above is the right way to go. |
|
![]() |