PlC5 Ethernet, a warning, a story, and a question

First the warning. PLC 5 series F revison A Ethernet processors have a problem in which if the ethernet port is flooded with traffic it can cause a memory dump and fault the controller. This can be fixed with a firmware upgrade which tech support will help you fix.

How do I know this? Hence the story.

The company I work for decided to "upgrade" 5 production lines from enhanced controllers to ethernet controllers, this decision was made before I joined the company. The purpose of the upgrade was to allow connectivity to our Lan. All of the lines now have a PLC5 ethernet controller connected to an industrial HMI running wonderware via a 3 com smart switch. The HMI's are running personal Oracle and are updating our Alpha oracle at predetermined times. 3 of the lines are 5/20's one is a 5/40, and the other is a 5/80.

The lan network in this plant is a mess. There is Cat5 strung like chicken wire everywhere. The server room consists of a window NT4.0 file server, an Alpha server, 4 old 10MBPS hubs and a WAN link to our corporate office.

On Tuesday, which I am refering to as black tuesday, we had a problem with our lan which caused a hub to start spewing bad packets across our netowrk. The PLC 5/80 and 5/40 and 1 - 5/20 responed by faulting and dumping their programs. The two other 5/20's stopped communicating with their HMI but continued running.

Now the question;

How do I protect the HMI-PLC connection in the event of a Lan problem. I knew enough when entering this project that a 3Com smart switch between the manufacturing network and business network was not enough protection. Being new at the company and not having enough network knowledge to put up a good fight, I couldn't push very hard at corporate IT for a proper solution. I knew that there were enough hard wired controls to prevent this from being a safety concern, however shutting down 2 of these lines is a big deal. It takes 12 - 16 hours to start up one of these lines and if anything goes wrong you have to start over.

From my limited knowledge of ethernet I think that I want a router to segregate the two networks, however somehow this is against company policy? IT told me that the smart switch would protect the HMI to PLC connection, I guess they were wrong costing us $$$$$$$$$. I know this issue has been discussed before but I have searched and can not find a thread that relates. As I said, I knew this wasn't a good setup but thought if anything went wrong with the lan the PLC would shut off it's Ethernet port, not dump the program.

Any advice, links, etc... on what I should do with our network would be greatly appreciated

thanks
__________________
Windows XP Professional x64: Windows is now a 64 bit tweak of a 32 bit extension to a 16 bit user interface for an 8 bit operating system based on a 4 bit architecture from a 2 bit company that can't stand 1 bit of competition.
  Reply With Quote
Old December 8th, 2006, 01:36 AM   #2
rPraveenkum
Member
India

rPraveenkum is offline
 
rPraveenkum's Avatar
 
Join Date: Aug 2006
Location: Chennai
Posts: 876
Always don't Interconnect office lan with the Industrial lan this will Help always
__________________
.................................................. .................................................. ..........................................
.................................................. .................................................. ..........................................
PRAVEEN KUMAR
http://www.praveen.envy.nu
Life is like butterfly, handle with care - Praveen
  Reply With Quote
Old December 8th, 2006, 04:44 AM   #3
OZEE
Member
United States

OZEE is offline
 
Join Date: Mar 2006
Location: Kansas
Posts: 1,669
Not being entirely sure of how your Oracle is retrieving data from the PLC's, but you need to isolate their system from yours.

What info do they need? Come up with a method of concentrating that data into a separate computer or PLC that acts as a "gateway". This "gateway" should have two network cards - each network having different IP address structures. Then their Oracle can come into your gateway on the "other" network.

Also, they should be polling their data at a reasonable rate. How often do they need how much data?
  Reply With Quote
Old December 8th, 2006, 06:46 AM   #4
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 3,639
Sounds like a situation where I'd install a managed router between the line (PLC's & HMI's) and the Enterprise network.

The router should be configured to allow only traffic to flow between the Database server(s) and the PLC/HMI network. This is best accomplished using MAC filtering, but that will have to be updated any time the Enterprise connection changes. IP filtering should also work, but is slightly less immune to packet storms.

One absolute though, there should be NO HUBS in ANY ETHERNET NETWORK ANYMORE. Switches cost a tiny bit more than hubs, and hubs are evil.

One other thing to keep in mind, is you can get some seriously nasty packet storms, even on a fully switched network, if you don't have switches that support STP*, or the individual 'Workgroup Switches' do not concantenate into a STP* switch.

*STP = Spanning Tree Protocol, and allows for Star networks to be connected via multiple routes. Without STP, connecting Port 1 on a switch to Port 2 on the same switch (or any such 'connect to self', as in an Ethernet ring configuration) is absolutely disasterous.
  Reply With Quote
Old December 8th, 2006, 09:19 AM   #5
allscott
Member
Canada

allscott is offline
 
allscott's Avatar
 
Join Date: Jul 2004
Posts: 1,157
The Alpha is pulling basic production data such a line speed, length produced, downtime, etc....

There is about 100 tags of data polled out of every machine every two hours by the Alpha server.
__________________
Windows XP Professional x64: Windows is now a 64 bit tweak of a 32 bit extension to a 16 bit user interface for an 8 bit operating system based on a 4 bit architecture from a 2 bit company that can't stand 1 bit of competition.
  Reply With Quote
Old December 8th, 2006, 12:05 PM   #6
averytc
Member
United States

averytc is offline
 
averytc's Avatar
 
Join Date: Jul 2002
Posts: 114
We upgraded our only 5/40 to a 5/40E (Used Series C, Rev. D) this year. The HMI still uses DH+, and the Ethernet is used for data logging and PLC communication. We have a managed switched network with a router between the company network and the PLC network. If I tried to do much more than data logging, it would dump. I did the upgrade and all is now well, so the upgrade does work.

rdrast is right. I would address your network issues also.

Good luck!

Last edited by averytc; December 8th, 2006 at 12:08 PM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 08:11 PM.


.