Greetings!
We have a small conveyor made up of metal bins that catch product with an indexing motion. It is controlled by an Ultra3000i indexing servo drive. Today, a technician told me that he has never seen the drvie fault, even when the conveyor gets in a serious bind, it just rips itself apart.
He asked me to try to limit the drive current so that it would fault rather than create so much damage. I found a cable and fired up the laptop with Ultraware, connected to the drive and found the only place I could adjust any current setting was under the "Faults" branch "user current limit". The value in the drive was 255 amps! The drive/motor tab showed a peak current limit of 32amps.
I monitored the drive in normal operation and found the peak current to be 9 amps. I set the user current limit to 15 amps for now. I am not sure if what I did will help. Apparently, the bins on this conveyor come loose and hang up on the frame at least once a week so I should find out soon enough.
Can anyone tell me if I adjusted the correct parameter?
Thanks,
Paul
Old December 19th, 2006, 03:03 PM   #2
mgvol
United States
mgvol is offline
mgvol's Avatar
I do believe that is right. BTW, I just opened a "dummy" ULTRA 3000 project in Ultraware, and it looks as if 255A is the default.
Old December 19th, 2006, 03:53 PM   #3
agarb
United States
agarb is offline
Wrong spot. Double-click on the drive in workspace and change the current limits.
By changing the "User Current Fault", I suspect you will make more work for yourself. Everytime it happens, you'll have to come out and hook up to the drive to clear the fault.
By the way, I couldn't find the Current Limits the first time I looked for them. I had to call A/B.
Old December 19th, 2006, 03:55 PM   #4
Gerry
New Zealand
Gerry is offline
You should also look at the position error settings.
Old December 19th, 2006, 04:00 PM   #5
OkiePC
United States
OkiePC is offline
OkiePC's Avatar
Thanks guys, I will get right on it...can I change those settings online? while running?
Or must I stop the drive and/or download?
Old December 19th, 2006, 04:06 PM   #6
agarb
United States
agarb is offline
It's been awhile since I messed with an Ultra3000, but you should be able to do it online. Just becareful to save your settings properly. (By dragging the on-line drive to the off-line drive.) This is very non-intuitive.
Old December 19th, 2006, 04:07 PM   #7
OkiePC
United States
OkiePC is offline
OkiePC's Avatar
Quote:
Originally Posted by agarb
...Just becareful to save your settings properly. (By dragging the on-line drive to the off-line drive.) This is very non-intuitive.
Yeah, I spent nearly an hour figuring that out the one other time I have been online with one of these drives...thanks again...Paul
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
motor alternating directsoft 32 on a DL06 DRThorne LIVE PLC Questions And Answers 15 November 9th, 2006 08:05 PM
OT Limiting current output of VFD rta53 LIVE PLC Questions And Answers 7 October 6th, 2006 11:27 AM
Relay outputs for solenoid valves Biker LIVE PLC Questions And Answers 41 October 8th, 2005 12:13 AM
3 Phase Current sparky64 LIVE PLC Questions And Answers 6 September 9th, 2004 09:30 AM
On the subject of inrush current Steve Bailey LIVE PLC Questions And Answers 24 September 1st, 2003 06:19 PM