Greetings!
We have a small conveyor made up of metal bins that catch product with an indexing motion. It is controlled by an Ultra3000i indexing servo drive. Today, a technician told me that he has never seen the drvie fault, even when the conveyor gets in a serious bind, it just rips itself apart. He asked me to try to limit the drive current so that it would fault rather than create so much damage. I found a cable and fired up the laptop with Ultraware, connected to the drive and found the only place I could adjust any current setting was under the "Faults" branch "user current limit". The value in the drive was 255 amps! The drive/motor tab showed a peak current limit of 32amps. I monitored the drive in normal operation and found the peak current to be 9 amps. I set the user current limit to 15 amps for now. I am not sure if what I did will help. Apparently, the bins on this conveyor come loose and hang up on the frame at least once a week so I should find out soon enough. Can anyone tell me if I adjusted the correct parameter? Thanks, Paul |
|
|
|
#2 |
|
Member
|
I do believe that is right. BTW, I just opened a "dummy" ULTRA 3000 project in Ultraware, and it looks as if 255A is the default.
|
|
|
|
#3 |
|
Member
![]() Join Date: May 2006
Location: USA
Posts: 204
|
Wrong spot. Double-click on the drive in workspace and change the current limits.
![]() By changing the "User Current Fault", I suspect you will make more work for yourself. Everytime it happens, you'll have to come out and hook up to the drive to clear the fault. By the way, I couldn't find the Current Limits the first time I looked for them. I had to call A/B. Last edited by agarb; December 19th, 2006 at 03:58 PM. |
|
|
|
#4 |
|
Member
![]() Join Date: Jun 2002
Location: Auckland
Posts: 1,134
|
You should also look at the position error settings.
|
|
|
|
#5 |
|
Lifetime Supporting Member
|
Thanks guys, I will get right on it...can I change those settings online? while running?
Or must I stop the drive and/or download? |
|
|
|
#6 |
|
Member
![]() Join Date: May 2006
Location: USA
Posts: 204
|
It's been awhile since I messed with an Ultra3000, but you should be able to do it online. Just becareful to save your settings properly. (By dragging the on-line drive to the off-line drive.) This is very non-intuitive.
|
|
|
|
#7 | |
|
Lifetime Supporting Member
|
Quote:
|
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| motor alternating directsoft 32 on a DL06 | DRThorne | LIVE PLC Questions And Answers | 15 | November 9th, 2006 08:05 PM |
| OT Limiting current output of VFD | rta53 | LIVE PLC Questions And Answers | 7 | October 6th, 2006 11:27 AM |
| Relay outputs for solenoid valves | Biker | LIVE PLC Questions And Answers | 41 | October 8th, 2005 12:13 AM |
| 3 Phase Current | sparky64 | LIVE PLC Questions And Answers | 6 | September 9th, 2004 09:30 AM |
| On the subject of inrush current | Steve Bailey | LIVE PLC Questions And Answers | 24 | September 1st, 2003 06:19 PM |