Modbus on PLC5
Allscott linked to the "classic" Modbus module that Prosoft makes. They work and work well.
I'd recommend using the newer (well, 5 years old) platform, the "Multi-Vendor Interface" from Prosoft.
The MVI71-MCM is Prosoft's current technology module to allow a PLC-5 controller to communicate over serial Modbus.
I think the MVI-series are also a little less expensive than the older 3100 series modules.
I like the MVI series because the same internal x386 system-on-chip platform and firmware are used in several form factors (SLC, PLC, FLEX, Compact, ControlLogix). That makes it easier for me to program and troubleshoot, and easier for Prosoft to build and support.
If you have a network connection (ControlNet or EtherNet/IP or DH+) there are more options from Prosoft, HMS Fieldbus, Real-Time Automation and Datalink. But the in-rack Prosoft card is the most straightforward way to add Modbus communications to a PLC-5 controller.
Actually the project is interfacing a V-Pac controller with an existing PLC5 - PC SCADA- Control setup, so Modbus is the way to go.
I have a PLC5/80E that I want to poll a Modbus device into using a Digi1. I have setup the message as a multihop going to the IP adress of the...
1,421
hi, i need to establish communication between PLC5/40 and experion that uses MODBUS TCP/IP. what do i need or what can i do?
2,173
Good day guys. I have a third party device with its Modbus registers which I want to copy/set up on a plc because I need to convert my Modbus tcp...
92
I'm a beginner in the automation field and I've set up an automation system connecting several devices (datalogger, radio, etc.) via Modbus RS485...
174
I Am looking to get ahold of the modbus map for an air compressor. I HAve emailed the vendor as well, just wondering if any of my friends here...
82
