AB slc5/04 communication

hello all, I have a slc5/04 that i need to download the logic from. I am trying to figure out what I need to communicate with this bad boy. it has a panelview 1000 connected to the rs232 port. I tried disconnecting the panelview and doing a autconfig with the rs232 driver using a regular cp3 cable and it did not work. I know that you need this cable:
http://www.rockwellautomation.com/su...84-PCMK_IM.pdf
to use the dh programming port but I was wondering f there was any way around buying the expensive cable?
  Reply With Quote
Old May 1st, 2007, 05:02 PM   #2
Christoff84
Lifetime Supporting Member + Moderator
Canada

Christoff84 is offline
 
Christoff84's Avatar
 
Join Date: Jun 2006
Location: Cambridge, ON
Posts: 379
You can try using the AB PIC driver with the cp3 cable. Most likely if the DF1 driver didnt work then the serial port is set to DH485.
  Reply With Quote
Old May 1st, 2007, 05:07 PM   #3
Ken Moore
Member
United States

Ken Moore is offline
 
Ken Moore's Avatar
 
Join Date: May 2004
Location: Upstate South Carolina
Posts: 2,334
What is the exact part number of the panel view? The part number will tell you what the communication protocol is. DF1 or DH485
__________________
"To give real service you must add something that cannot be bought or measured with money; and that is sincerity and integrity."
- Donald A. Adams

  Reply With Quote
Old May 1st, 2007, 05:13 PM   #4
diat150
Lifetime Supporting Member
United States

diat150 is offline
 
Join Date: Mar 2006
Location: Louisiana
Posts: 1,237
Im not sure of the part number, I will have to get that next time. so it sounds like I should be able to talk with the processor if the serial port is setup as rs232?
  Reply With Quote
Old May 1st, 2007, 05:26 PM   #5
Christoff84
Lifetime Supporting Member + Moderator
Canada

Christoff84 is offline
 
Christoff84's Avatar
 
Join Date: Jun 2006
Location: Cambridge, ON
Posts: 379
You will be able to talk to the PLC no matter which protocol it is running. It will just effect which driver you use in RSLinx.
  Reply With Quote
Old May 1st, 2007, 05:59 PM   #6
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,007
Exactness begets precision

If the PanelView part number ends in 5 or 9, it's a DH485 protocol unit and you need to use the "1747-PIC/AIC+" driver in RSLinx with an integral RS232 port on your PC.

If the PanelView part number end in 16, it's a DF1 Full Duplex protocol unit and you can use the DF1 Full Duplex driver in RSLinx.

Because you already tried the DF1 Full Duplex driver and were unsuccessful, it's a safe bet that the SLC-5/04 Channel 0 is configured for DH485 protocol.

You have two additional options:

1. The "PIC driver" can be difficult to configure in Windows 2000/XP because of the hardware access it requires. A-B makes a 1747-UIC USB/DH485 converter that converts between DF1 protocol on USB and DH485 protocol on RS232 or RS485. This is the choice for most modern DH485 users.

2. The PanelView Standard terminals with version 3.0 or better firmware support ATA Flash memory cards, including CompactFlash cards in PCMCIA Type II carriers. This is my preferred method for uploading and downloading *.PVA configuration files to and from Standard PanelView Terminals.
__________________
- "Simpler is better, except when complicated looks really cool."
  Reply With Quote
Old May 1st, 2007, 06:43 PM   #7
diat150
Lifetime Supporting Member
United States

diat150 is offline
 
Join Date: Mar 2006
Location: Louisiana
Posts: 1,237
thanks for the help. I did have trouble getting the aic driver to install. I had to log onto my adminstrator account for it to even load up. Not sure if it will even work right when i do get back around to it.
  Reply With Quote
Old May 1st, 2007, 08:25 PM   #8
OZEE
Member
United States

OZEE is offline
 
Join Date: Mar 2006
Location: Kansas
Posts: 1,695
Quote:
Originally Posted by diat150
I have a slc5/04 that i need to download the logic from.
Just a nit-picky technicality... You download TO a PLC, you upload FROM it. You'll save lots of future confusion if you'll reference the directions correctly.

There are lots of examples of people uploading to a PLC and wondering why the processor memory is blank. Or downloading from a PLC and wondering why their offline program changes are gone.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Communication between Siemens PLC en AB PLC through profibus? pietervdb LIVE PLC Questions And Answers 3 March 14th, 2007 06:16 AM
Modicon TSX Microscan to AB Micrologix communication kulkago1 LIVE PLC Questions And Answers 2 July 27th, 2006 08:44 AM
Communication on ethernet between AB PLC and Siemens PLC Chandrashekhar_basap LIVE PLC Questions And Answers 4 May 28th, 2006 03:03 PM
AB communication cable indra LIVE PLC Questions And Answers 10 September 24th, 2005 05:33 AM
Rs485 Communication With Micrologix Ab pcontrol LIVE PLC Questions And Answers 1 January 1st, 2003 11:50 PM


All times are GMT -5. The time now is 12:05 PM.


.