Correct calculation for Star Delta sizing - Contactor & Overload
Hi guys,
I've only a lil` experience in motor sizing & calculation for contactor and overload. Hope you guys can show me the correct or proper calculation. My current calcluation as below, please correct me if I'm wrong.
For a 45kW motor:
Amp = 45000/(415*1.732*0.85)
= 74Amp
Main and Delta contactor & overload:
= 74/1.732
= 42.8Amp
With 10% spare:
= 48Amp
Star contactor and overload:
= 74/2
= 37Amp
With 10% spare:
= 41Amp
AB contactor:
1) 100-C60T10 x 2 pcs
2) 100-C43T10 x 2 pcs
3) 193-TCC45 (30 - 45) Amp
Question:
1) The overload should be sizing according to Main amp, 42.8Amp (48Amp with 10% spare) or the Star amp, 37Amp (41Amp with 10% spare)?
Thank you.
Old May 5th, 2007, 01:50 AM   #2
Lancie1
United States
Lancie1 is offline
Lancie1's Avatar
I think you would need two overload relays, one for Delta contactor, and one for the Star contactor. Size each one according to your calculations and the local codes & laws.
Old May 5th, 2007, 02:00 AM   #3
Kidblue
England
Kidblue is offline
Kidblue's Avatar
It's not the way i've always done it. Normally fit one overload (usually on the LINE or MAIN contactor) and normally rate at 0.58 of the FLC.
Alternatively, we fit one Thermal/Magnetic motor circuit breaker upstream of the 3 motor contactors rated for FLC.
Hope this helps.....
__________________
Rob Howdle
.........For the Boys in Royal Blue !!
Old May 5th, 2007, 02:30 AM   #4
pouch
United Kingdom
pouch is offline
Follow the link below to the Moeller wiring book chapter on Motor protection:
http://www.moeller.net/binary/schabu/sb0801g.pdf
Regards
Pouch
Old May 5th, 2007, 02:55 AM   #5
Gil47
New Zealand
Gil47 is offline
Gil47's Avatar
Kid blue is on the right track
if you divide by Sqrt of 3
or 1.732
or 1 over Sqrt 3 all come out as .58 or 58%
The voltage across the windings is line voltage 415 in delta
your phase voltage is 240 in star
because of the higher voltage in delta the current will also be higher
so the 1 overload in phase current is .58 of the line voltage
Thermal/Magnetic motor circuit breaker upstream of the 3 motor Contactors does remove the confusion involved in setting overloads
Note 3 contactors you show you are intending to have 4
The price you are considering paying for contactors timers and wiring could buy you a soft starter
We only use Star Delta now where long star up times in minutes occur such a some cenrifuges we havent wired one new in 20 years
Old May 5th, 2007, 03:05 AM   #6
504bloke
England
504bloke is offline
504bloke's Avatar
Thats how we do it.
__________________
Regards
Dave
"When you are courting a nice girl an hour seems like a second. When you sit on a red-hot cinder a second seems like an hour. That's relativity."
Albert Einstein (1879-1955)
Old May 5th, 2007, 04:47 PM   #7
Lancie1
United States
Lancie1 is offline
Lancie1's Avatar
Okay, I am WRONG again! Flyers confused me when he mentioned having two overloads:
I see now there must be only one. Here in the US and back in the good old days, most motor starters had built-in attached overload relays, so I automatically assumed if there were two contactors then there must be two separate overloads. I forgot that the IEC and modern types have separate user-added overloads.
I am sorry, and I will not attempt to answer questions like this again. I am too old to cut the mustard, and my knowledge is as obsolete as the rest of me.
Old May 5th, 2007, 10:19 PM   #8
Thomas Sullens
United States
Thomas Sullens is offline
This will help you.
Old May 6th, 2007, 03:19 AM   #9
JesperMP
Denmark
JesperMP is offline
JesperMP's Avatar
Flyers.
For a star-delta starter you have the possibility to place the overload protection in two positions, in the line or in the windings.
In the line is the same as just putting the overload before the motor as with a DOL starter. The rating must be the same as FLC.
The disadvantage is that if the overload is set to FLC, then it is really not protecting the motor while it is in delta (setting is x1.732 too high).
In the windings means that the overload is placed after the point where the wiring to the contactors are split into main and delta. The overload then allways measures the current inside the windings, and is thus allways correct. The setting must be x0.58 FLC (line current).
The disadvantage is that you must use separate shortcircuit and overload protections.
Also, I would use 0.80 for estimating cos phi x efficiency and not 0.85 for a 45 kW motor. Better to be safe than sorry.
In principle you dont have to add 10%, but I do normally take the next size contactor if the rating is too close to the actual load.
Estimated motor line FLC is then
45000W/(415V*1.732*0.80) = 79 A.
Main and delta contactor should be at least
FLC * 0.58 = 46 A.
Star contactor should be at least
FLC * 0.33 = 26 A.
That Moeller instruction that pouch linked to tells it all. I got that book as a gift once, and I look into it on occasions.
What is the application ?
Nowadays, the only place where we use star-delta is with (very) large fans. Everywhere else low-cost softstarters are taking over.
__________________
Jesper
Old May 13th, 2007, 11:40 AM   #10
flyers
Singapore
flyers is offline
Lancie1: Sorry for the confussion over the number of overloads. No you are not too old, just that I'm too fresh in this motor calculation thingy.
Kidblue: Yes, you are right, we normally put a FLC MCCB before the 3 main contactor and the overload will be located at the main contactor.
pouch: Thanks for your link, very good write up, I've no time to go thru them throughly, but just browse thru it. WIll read them when I have the time...great one!
Gil47/504bloke: Thx for your reply.
Thomas: Thx for your link too.
JesperMP: I do not know the STAR contactor calculation is divide by 3, i taught it is divided by 2. I'll check out the ebook linked. Thx.
Old May 13th, 2007, 08:58 PM   #11
flyers
Singapore
flyers is offline
Costing, comparing contactors + overload with soft starter for 45KW motor:
Estimate (list price):
100-C60T10 x 2 pcs = USD250
100-C30T10 x 1 pc = USD60
193-TCC60 x 1 pc = USD70
100-MCA00 x 1 pc = USD12
TOTAL = USD(250+60+70+12) = USD392
While soft starter list price:
150-F85NBD (17A to 85A) x 1 pc = USD3140
For PowerFlex 400:
22C-D088A103 x 1 pc = USD 5430
It looks like soft starter is still a lot more expensive compare to contactor + overload. The only advantage I can see is space saving & less maintenance with using soft starter in this situation. The 45kW is to drive a shedder blade (to cut rubbish).
Or do I miss anything in the above calculation because some of you guy mention s/starter cost about the same as contactor + overload. Please highlight me. Thank you.
Old May 13th, 2007, 11:39 PM   #12
allscott
Canada
allscott is offline
allscott's Avatar
Shop around some more for a softstart. I don't know if they are available in your area but theses guys; www.benshaw.com will set you up for a lot less then that. Also look at Siemens, Cutler Hammer, Telemechanique....
Don't forget to price in the additional wiring that will be needed with a contactor/overload.
__________________
Windows XP Professional x64: Windows is now a 64 bit tweak of a 32 bit extension to a 16 bit user interface for an 8 bit operating system based on a 4 bit architecture from a 2 bit company that can't stand 1 bit of competition.
Old May 14th, 2007, 08:46 AM   #13
OkiePC
United States
OkiePC is offline
OkiePC's Avatar
Quote:
No, I think you are right for a 60HP application. When you get up to around 150HP and larger, the soft starters will become more economical than the contactors.
You might want to check with RAM industries. We have 3 of their DBS systems here that are outstanding. Their pricing is apx half what an AB soft starter costs, and they incorporate some really nice features like emergency DOL starting should the electronics fail...
Old May 14th, 2007, 12:24 PM   #14
JesperMP
Denmark
JesperMP is offline
JesperMP's Avatar
Hello Flyers.
Your prices for softstarters seems a bit high.
And the Powerflex is a VFD, not a softstarter.
We use the new Siemens 3RW40 range extensively now.
It is the low cost type, but with integral bypass contactor, so it makes for a very compact setup.
List price for a 200-460v 75kW (134A) 3RW4055-6BB44 is approx 1200 USD.
It is the smallest in this range with an integral bypass.
There is another lowcost range without the integral bypass 3RW30.
List price for a 200-460V 55kW (75A) 3RW3045-1AB14 is approx 750 USD.
If you add the extra panel space and wiring time, the softstarter is practically on par with an yD starter.
If your factor in that both contactors and softstarters are heavily discounted, then the panel space and installation cost weighs even more against yD.
Other manufacturers also have lowcost ranges.
__________________
Jesper
Old May 14th, 2007, 08:06 PM   #15
allscott
Canada
allscott is offline
allscott's Avatar
One last thing to add;
Are you sure you can't start the motor across the line? IF you are sure then disregard if you are not then we can debate that as well.
__________________
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Correct cable sizing? flyers LIVE PLC Questions And Answers 18 April 1st, 2007 08:06 AM