Correct calculation for Star Delta sizing - Contactor & Overload
Hi guys,
I've only a lil` experience in motor sizing & calculation for contactor and overload. Hope you guys can show me the correct or proper calculation. My current calcluation as below, please correct me if I'm wrong. For a 45kW motor: Amp = 45000/(415*1.732*0.85) = 74Amp Main and Delta contactor & overload: = 74/1.732 = 42.8Amp With 10% spare: = 48Amp Star contactor and overload: = 74/2 = 37Amp With 10% spare: = 41Amp AB contactor: 1) 100-C60T10 x 2 pcs 2) 100-C43T10 x 2 pcs 3) 193-TCC45 (30 - 45) Amp Question: 1) The overload should be sizing according to Main amp, 42.8Amp (48Amp with 10% spare) or the Star amp, 37Amp (41Amp with 10% spare)? Thank you. |
|
|
|
#2 |
|
Lifetime Supporting Member + Moderator
|
I think you would need two overload relays, one for Delta contactor, and one for the Star contactor. Size each one according to your calculations and the local codes & laws.
|
|
|
|
#3 | |
|
Lifetime Supporting Member
|
Quote:
Alternatively, we fit one Thermal/Magnetic motor circuit breaker upstream of the 3 motor contactors rated for FLC. Hope this helps.....
__________________
Rob Howdle .........For the Boys in Royal Blue !! Last edited by Kidblue; May 5th, 2007 at 02:03 AM. |
|
|
|
|
#4 |
|
Member
![]() Join Date: Apr 2006
Location: Chester
Posts: 44
|
Follow the link below to the Moeller wiring book chapter on Motor protection:
http://www.moeller.net/binary/schabu/sb0801g.pdf Regards Pouch |
|
|
|
#5 |
|
Member
|
Kid blue is on the right track
if you divide by Sqrt of 3 or 1.732 or 1 over Sqrt 3 all come out as .58 or 58% The voltage across the windings is line voltage 415 in delta your phase voltage is 240 in star because of the higher voltage in delta the current will also be higher so the 1 overload in phase current is .58 of the line voltage Thermal/Magnetic motor circuit breaker upstream of the 3 motor Contactors does remove the confusion involved in setting overloads Note 3 contactors you show you are intending to have 4 The price you are considering paying for contactors timers and wiring could buy you a soft starter We only use Star Delta now where long star up times in minutes occur such a some cenrifuges we havent wired one new in 20 years |
|
|
|
#6 | |
|
Lifetime Supporting Member + Moderator
|
Quote:
__________________
Regards Dave "When you are courting a nice girl an hour seems like a second. When you sit on a red-hot cinder a second seems like an hour. That's relativity." Albert Einstein (1879-1955) |
|
|
|
|
#7 | |
|
Lifetime Supporting Member + Moderator
|
Okay, I am WRONG again! Flyers confused me when he mentioned having two overloads:
Quote:
I am sorry, and I will not attempt to answer questions like this again. I am too old to cut the mustard, and my knowledge is as obsolete as the rest of me. Last edited by Lancie1; May 5th, 2007 at 04:53 PM. |
|
|
|
|
#9 |
|
Lifetime Supporting Member + Moderator
|
Flyers.
For a star-delta starter you have the possibility to place the overload protection in two positions, in the line or in the windings. In the line is the same as just putting the overload before the motor as with a DOL starter. The rating must be the same as FLC. The disadvantage is that if the overload is set to FLC, then it is really not protecting the motor while it is in delta (setting is x1.732 too high). In the windings means that the overload is placed after the point where the wiring to the contactors are split into main and delta. The overload then allways measures the current inside the windings, and is thus allways correct. The setting must be x0.58 FLC (line current). The disadvantage is that you must use separate shortcircuit and overload protections. Also, I would use 0.80 for estimating cos phi x efficiency and not 0.85 for a 45 kW motor. Better to be safe than sorry. In principle you dont have to add 10%, but I do normally take the next size contactor if the rating is too close to the actual load. Estimated motor line FLC is then 45000W/(415V*1.732*0.80) = 79 A. Main and delta contactor should be at least FLC * 0.58 = 46 A. Star contactor should be at least FLC * 0.33 = 26 A. That Moeller instruction that pouch linked to tells it all. I got that book as a gift once, and I look into it on occasions. What is the application ? Nowadays, the only place where we use star-delta is with (very) large fans. Everywhere else low-cost softstarters are taking over.
__________________
Jesper
|
|
|
|
#10 |
|
Member
![]() Join Date: Sep 2006
Location: Amk
Posts: 293
|
Lancie1: Sorry for the confussion over the number of overloads. No you are not too old, just that I'm too fresh in this motor calculation thingy.
Kidblue: Yes, you are right, we normally put a FLC MCCB before the 3 main contactor and the overload will be located at the main contactor. pouch: Thanks for your link, very good write up, I've no time to go thru them throughly, but just browse thru it. WIll read them when I have the time...great one! Gil47/504bloke: Thx for your reply. Thomas: Thx for your link too. JesperMP: I do not know the STAR contactor calculation is divide by 3, i taught it is divided by 2. I'll check out the ebook linked. Thx. |
|
|
|
#11 |
|
Member
![]() Join Date: Sep 2006
Location: Amk
Posts: 293
|
Costing, comparing contactors + overload with soft starter for 45KW motor:
Estimate (list price): 100-C60T10 x 2 pcs = USD250 100-C30T10 x 1 pc = USD60 193-TCC60 x 1 pc = USD70 100-MCA00 x 1 pc = USD12 TOTAL = USD(250+60+70+12) = USD392 While soft starter list price: 150-F85NBD (17A to 85A) x 1 pc = USD3140 For PowerFlex 400: 22C-D088A103 x 1 pc = USD 5430 It looks like soft starter is still a lot more expensive compare to contactor + overload. The only advantage I can see is space saving & less maintenance with using soft starter in this situation. The 45kW is to drive a shedder blade (to cut rubbish). Or do I miss anything in the above calculation because some of you guy mention s/starter cost about the same as contactor + overload. Please highlight me. Thank you. Last edited by flyers; May 13th, 2007 at 09:01 PM. |
|
|
|
#12 |
|
Member
|
Shop around some more for a softstart. I don't know if they are available in your area but theses guys; www.benshaw.com will set you up for a lot less then that. Also look at Siemens, Cutler Hammer, Telemechanique....
Don't forget to price in the additional wiring that will be needed with a contactor/overload.
__________________
Windows XP Professional x64: Windows is now a 64 bit tweak of a 32 bit extension to a 16 bit user interface for an 8 bit operating system based on a 4 bit architecture from a 2 bit company that can't stand 1 bit of competition. Last edited by allscott; May 13th, 2007 at 11:42 PM. |
|
|
|
#13 | |
|
Lifetime Supporting Member
|
Quote:
You might want to check with RAM industries. We have 3 of their DBS systems here that are outstanding. Their pricing is apx half what an AB soft starter costs, and they incorporate some really nice features like emergency DOL starting should the electronics fail... |
|
|
|
|
#14 |
|
Lifetime Supporting Member + Moderator
|
Hello Flyers.
Your prices for softstarters seems a bit high. And the Powerflex is a VFD, not a softstarter. We use the new Siemens 3RW40 range extensively now. It is the low cost type, but with integral bypass contactor, so it makes for a very compact setup. List price for a 200-460v 75kW (134A) 3RW4055-6BB44 is approx 1200 USD. It is the smallest in this range with an integral bypass. There is another lowcost range without the integral bypass 3RW30. List price for a 200-460V 55kW (75A) 3RW3045-1AB14 is approx 750 USD. If you add the extra panel space and wiring time, the softstarter is practically on par with an yD starter. If your factor in that both contactors and softstarters are heavily discounted, then the panel space and installation cost weighs even more against yD. Other manufacturers also have lowcost ranges.
__________________
Jesper
|
|
|
|
#15 |
|
Member
|
One last thing to add;
Are you sure you can't start the motor across the line? IF you are sure then disregard if you are not then we can debate that as well.
__________________
Windows XP Professional x64: Windows is now a 64 bit tweak of a 32 bit extension to a 16 bit user interface for an 8 bit operating system based on a 4 bit architecture from a 2 bit company that can't stand 1 bit of competition. |
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Correct cable sizing? | flyers | LIVE PLC Questions And Answers | 18 | April 1st, 2007 08:06 AM |