Test pen lighted when testing 24V DC?

Hi guy,

Sorry, this is not a PLC question, but it's something regarding wirings & power.

I'm checking a system which consists of many remote indicators. All indicators are 24V DC or AC supported. But the system are using 24V DC. When I test the supply at the indicator connector (2 wires), the test pen lighted up.

I taught test pen only lighted when we test on AC system? How can it be? Some other colleague also get a minor short when accidentally touched the cable (which lighted the test pen).

Any comments on this system wiring? Thank you.
  Reply With Quote
Old July 10th, 2007, 04:34 AM   #2
aikona
Member
South Africa

aikona is offline
 
aikona's Avatar
 
Join Date: Oct 2003
Location: B2220 plaas dorpie
Posts: 182
Forget the test pen and use a proper digital meter

Eric
__________________
Waar is die Biltong -
  Reply With Quote
Old July 10th, 2007, 07:40 AM   #3
TPS Reports
Member
United States

TPS Reports is offline
 
TPS Reports's Avatar
 
Join Date: Nov 2006
Location: New Orleans, LA
Posts: 18
Grab a Fluke meter or something similar with an actual AC/DC selector. Test pens should only be used to test if something is "hot" or not (usually 120/240 AC, etc.)
  Reply With Quote
Old July 10th, 2007, 08:55 AM   #4
rsdoran
Lifetime Supporting Member
United States

rsdoran is offline
 
rsdoran's Avatar
 
Join Date: Apr 2002
Location: Birmingham, AL
Posts: 7,372
Quote:
Originally Posted by TPS Reports
Grab a Fluke meter or something similar with an actual AC/DC selector. Test pens should only be used to test if something is "hot" or not (usually 120/240 AC, etc.)
I do not trust these things so only believe them when they show hot. The reason they may "light" on DC is because there is some form of AC riding on the DC, this could happen if the DC common is connected to ground or errouneously combined with the neutral of a single phase ckt, there could be other reasons too.

As suggested, when you obtain a power reading when you think you should not then use a voltage meter to get more precise reasons. If still unsure may want to use an oscilloscope and check for AC on the DC ckt.
__________________
http://www.patchn.com Industrial Electrical & Maintenance @ www.patchn.com "Tell me and I forget, show me and I remember, involve me and I understand."
  Reply With Quote
Old July 10th, 2007, 09:17 AM   #5
ckchew666
Member
Malaysia

ckchew666 is offline
 
ckchew666's Avatar
 
Join Date: Aug 2003
Location: Malaysia
Posts: 591
Hi guys,

Thanks for your replies. I'll check it with the multimeter.

One of my colleague told me that DC high amp, it'll lighted up the test pen (HOT). I taught it was true.
  Reply With Quote
Old July 10th, 2007, 09:55 AM   #6
JvdV
Member
Netherlands

JvdV is offline
 
JvdV's Avatar
 
Join Date: Apr 2003
Location: Halsteren
Posts: 95
Wink

Some test pens react on magnetic fields as well.

Nice to test if solenoid valves without indicators are powered. As far for testing / indicating life circuits..........it was nice knowing you, I will start ordering some flowers
  Reply With Quote
Old July 10th, 2007, 10:14 AM   #7
ckchew666
Member
Malaysia

ckchew666 is offline
 
ckchew666's Avatar
 
Join Date: Aug 2003
Location: Malaysia
Posts: 591
Quote:
Originally Posted by JvdV
Some test pens react on magnetic fields as well.

Nice to test if solenoid valves without indicators are powered. As far for testing / indicating life circuits..........it was nice knowing you, I will start ordering some flowers
sorry, there is no valve, basically are all pilot lamp/indicators only.

"it was nice knowing you, I will start ordering some flowers " What do you mean by this? I don't get it
  Reply With Quote
Old July 10th, 2007, 05:42 PM   #8
JvdV
Member
Netherlands

JvdV is offline
 
JvdV's Avatar
 
Join Date: Apr 2003
Location: Halsteren
Posts: 95
High currents produce a magnetic field als well (all currents produce a magnetic field, but big currents produce significant currents)

The flowers part, in the netherlands it's custom to send some flowers to a friends funeral. And sinds yuo work with a .........you get the idea I think.
  Reply With Quote
Old August 20th, 2009, 03:02 AM   #9
tscoffee115
Member
Antigua and Barbuda

tscoffee115 is offline
 
Join Date: Aug 2009
Location: tscoffee115
Posts: 1
Hi there, Would a new one like me be welcome here?
Thanks so much in deed.


calcul pret assurance simulation taux emprunt ********** - Taux emprunt **********. Comparez les offres d’emprunt **********, simulation emprunt **********, taux emprunt **********calcul pret assurance simulation taux emprunt **********
  Reply With Quote
Old August 20th, 2009, 10:24 AM   #10
leitmotif
Member
United States

leitmotif is offline
 
Join Date: Nov 2004
Location: Seattle Wa. USA
Posts: 3,680
Yes you would be welcome

Dan Bentler
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Water meter & PLC hashem LIVE PLC Questions And Answers 14 April 29th, 2013 11:56 PM
Problems with Siemens CP340 RS232C communication Borte LIVE PLC Questions And Answers 10 February 17th, 2010 04:16 AM
Max distance fot transffering a 24V DC signal Gromit LIVE PLC Questions And Answers 6 June 5th, 2007 09:10 AM
Small and Cheap 24V DC Power Supply Matthias von Zorn LIVE PLC Questions And Answers 7 October 5th, 2004 09:26 PM
Analog, 24v dc, and 115ac in the same conduit olias LIVE PLC Questions And Answers 15 May 14th, 2004 07:38 PM


All times are GMT -5. The time now is 06:56 AM.


.