Old June 28th, 2007, 10:07 AM   #1
plcnovel
Member
Pakistan

plcnovel is offline
 
Join Date: Feb 2006
Location: LHR
Posts: 215
PID Output and Valves

Hi There
I am having some problems in stroking the valves from the pid controller in plc. I am using Controllogix platform. None of the valves are having any positioners on them (simple I/P, and they are fairly big size pressure/temperature control valves). The problem i am experiencing is , none of these valves will actually start to move untill PID output reaches around 35% to 45%. Once the valves are moved from the fully closed position, then they seem to follow the pid output without any problems. But just at the starting they are late to react. Is there anyway i can achieve the solution to this problem through my logic? I will appreciate your help and time. Thanks in advance

Regards
  Reply With Quote
Old June 28th, 2007, 11:09 AM   #2
nswu1
Member
United States

nswu1 is offline
 
nswu1's Avatar
 
Join Date: Oct 2005
Location: louisiana
Posts: 271
Check the pressure range of the actuators, and the output pressure from your regulated I/P transducer. I would bet the supply pressure is set to low. Another thing might be not enough volume to the actuator.
  Reply With Quote
Old June 28th, 2007, 11:13 AM   #3
dmroeder
Lifetime Supporting Member
United States

dmroeder is offline
 
dmroeder's Avatar
 
Join Date: Apr 2006
Location: Vancouver, WA
Posts: 2,050
Certainly that valve has some kind of positioner on it?

Ideally I would think that you would want to calibrate it, rather than try to adjust for it in the program. What happens when the calibration drifts further? Then you have to go back into the program and adjust again. At least with proper calibration, you wouldn't have to mess with PLC logic to get your loop working properly.

Maybe I just don't understand the situation.

edit: I guess I type slow. Good suggestion nswu1
  Reply With Quote
Old June 28th, 2007, 11:25 AM   #4
Ken Moore
Member
United States

Ken Moore is offline
 
Ken Moore's Avatar
 
Join Date: May 2004
Location: Upstate South Carolina
Posts: 2,346
Sounds like your I/P and control valves aren't using the same control range.
Is you I/P 3-15 psig, what about the valves are they set up for 3-15? Sounds like they may be 9-15.
__________________
"To give real service you must add something that cannot be bought or measured with money; and that is sincerity and integrity."
- Donald A. Adams

  Reply With Quote
Old June 28th, 2007, 12:23 PM   #5
curlyandshemp
Lifetime Supporting Member
Canada

curlyandshemp is offline
 
curlyandshemp's Avatar
 
Join Date: Jul 2005
Location: Toronto
Posts: 1,873
Quote:
Originally Posted by plcnovel
Hi There
I am having some problems in stroking the valves from the pid controller in plc. I am using Controllogix platform. None of the valves are having any positioners on them (simple I/P, and they are fairly big size pressure/temperature control valves). The problem i am experiencing is , none of these valves will actually start to move untill PID output reaches around 35% to 45%. Once the valves are moved from the fully closed position, then they seem to follow the pid output without any problems. But just at the starting they are late to react. Is there anyway i can achieve the solution to this problem through my logic? I will appreciate your help and time. Thanks in advance

Regards
check the basics first:

-Confirm the pressure output of the I/P with a pressure gauge in series with the air signal to the valve

-Confirm the ma readings from your analog output to the actuator

If necessary,rescale your analog output instead of 0-20ma ( 4 -20ma ) to start at 10ma or whatever output it takes to get the actuator to move.

Ian
__________________
Work to Ride,
Then Ride to Work

I would rather have a bottle in front of me..
than have a frontal lobotomy
  Reply With Quote
Old June 28th, 2007, 01:45 PM   #6
milldrone
Member
United States

milldrone is offline
 
milldrone's Avatar
 
Join Date: Mar 2005
Location: in the dog house
Posts: 1,293
curlyandshemp,

Your my hero!
__________________
Vaughn

If you can read this, thank a teacher.
  Reply With Quote
Old June 28th, 2007, 02:23 PM   #7
danny.michael
Lifetime Supporting Member
United States

danny.michael is offline
 
Join Date: Sep 2006
Location: Alabama
Posts: 204
I would highly recommend adding positioners to the valve actuators. If you are having problems when the valves are new, just wait until they have some age on them. Tuning the PID loops will be a pain without positioners.
  Reply With Quote
Old June 28th, 2007, 07:11 PM   #8
mellis
Member
United States

mellis is offline
 
Join Date: Nov 2004
Location: Cincinnati, Ohio
Posts: 808
Before you go changing *ANYTHING* about the valves...

Are the valves under operating conditions? That is do they have the normal pressure drop across the valve? Control valves have what is called a "bench set". This is the amount of extra spring force required to hold the valve closed against the specified shutoff pressure. If there is no pressure on the valve (like during pre-startup checkout) you will see the behavior you describe. It is normal. When you have pressure present, it will balance out the spring, and the valve will come off its seat with a much lower signal. It probably won't be at 4.1 ma, but it should a lot closer than 35%.

Back in the old days, Fisher used to recommend not using a positioner on fast flow or pressure loops. Positioners were generally recommended on temperature loops. Now, it's very common to see positioners on all control valves.
  Reply With Quote
Old June 28th, 2007, 07:44 PM   #9
curlyandshemp
Lifetime Supporting Member
Canada

curlyandshemp is offline
 
curlyandshemp's Avatar
 
Join Date: Jul 2005
Location: Toronto
Posts: 1,873
Quote:
Originally Posted by plcnovel
Hi There
I am having some problems in stroking the valves from the pid controller in plc. I am using Controllogix platform. None of the valves are having any positioners on them (simple I/P, and they are fairly big size pressure/temperature control valves). The problem i am experiencing is , none of these valves will actually start to move untill PID output reaches around 35% to 45%. Once the valves are moved from the fully closed position, then they seem to follow the pid output without any problems. But just at the starting they are late to react. Is there anyway i can achieve the solution to this problem through my logic? I will appreciate your help and time. Thanks in advance

Regards
More basics stuff:

can you post:
-what analog output card you are using
-what I/P
-what Control valve
-the application

Is this one valve or multiple valves that have the same issue? I have seen a pinhole or a kink in an airline to the control valve cause the exact same problem you desribe.

Also from past experience I have found that most 3-15PSI control valves are actually 0 - 17PSI, meaning at 4ma ( 3psi ) there is a slight leaking through the valve. We solved that by using a solenoid to supply air to the I/P. Whenever the I/P is not in use, solenoid OFF, no air. Then at 20ma (15PSI) the valve was not fully open. In the old days most I/Ps had a span adjustment that allowed the 20ma signal span to be raised. Now most AB 4-20ma outputs will actually give you 21ma if you supply the analog output channel the max value .

Ian
__________________
Work to Ride,
Then Ride to Work

I would rather have a bottle in front of me..
than have a frontal lobotomy
  Reply With Quote
Old June 29th, 2007, 09:44 AM   #10
plcnovel
Member
Pakistan

plcnovel is offline
 
Join Date: Feb 2006
Location: LHR
Posts: 215
Thank you very much for your input guys. I am using 1756-OF8 control logix analog output card, and the application is the temperature loop for the reboiler. The thing is, as you guys suggested earlier, i can scale my card output from 4ma to something higher than 4ma to lift the valve from its seat. But on it way back, when the output is 0%, then valve would still be open adding heat to the reboiler which we dont want. So how can i solve this problem. To me the valves are not linear at all.



Regards







Quote:
Originally Posted by curlyandshemp
More basics stuff:

can you post:
-what analog output card you are using
-what I/P
-what Control valve
-the application

Is this one valve or multiple valves that have the same issue? I have seen a pinhole or a kink in an airline to the control valve cause the exact same problem you desribe.

Also from past experience I have found that most 3-15PSI control valves are actually 0 - 17PSI, meaning at 4ma ( 3psi ) there is a slight leaking through the valve. We solved that by using a solenoid to supply air to the I/P. Whenever the I/P is not in use, solenoid OFF, no air. Then at 20ma (15PSI) the valve was not fully open. In the old days most I/Ps had a span adjustment that allowed the 20ma signal span to be raised. Now most AB 4-20ma outputs will actually give you 21ma if you supply the analog output channel the max value .

Ian
  Reply With Quote
Old June 29th, 2007, 10:03 AM   #11
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: Vancouver, WA, US
Posts: 6,718
I always tell my customers to get linear valves.

These kinds of problems go away and the machine runs better for the rest of its lifetime.
  Reply With Quote
Old June 29th, 2007, 10:15 AM   #12
plcnovel
Member
Pakistan

plcnovel is offline
 
Join Date: Feb 2006
Location: LHR
Posts: 215
Quote:
Originally Posted by Peter Nachtwey
These kinds of problems go away and the machine runs better for the rest of its lifetime.
Thanks Peter, i do agree with you , but now i am in this situation where none of the valves are lifting from its seat until abt 35 to 40% output. Any solution to make these nonlinear valves to work properly?
  Reply With Quote
Old June 29th, 2007, 10:16 AM   #13
curlyandshemp
Lifetime Supporting Member
Canada

curlyandshemp is offline
 
curlyandshemp's Avatar
 
Join Date: Jul 2005
Location: Toronto
Posts: 1,873
Use a soloneoid that is controlled by a PLC output to supply air to the I/P. Whenever the heating loop is not required, AIR OFF, and also use logic to test if the temperature is getting too hot. Normally I take the required SETPOINT add 5c or 10c and compare TEST SETPOINT against PROCESS VARIABLE. If the PROCESS VARIABLE is greater than TEST SETPOINT for XX seconds, shut off the air to the I/P

Are you sure the valve actuator is not sticking ?

Ian
__________________
Work to Ride,
Then Ride to Work

I would rather have a bottle in front of me..
than have a frontal lobotomy
  Reply With Quote
Old June 29th, 2007, 10:50 AM   #14
kamenges
Member
United States

kamenges is offline
 
kamenges's Avatar
 
Join Date: Nov 2002
Location: Brillion, WI
Posts: 3,654
Ian's last line is a big thing to look at. Without a positioner on the valve, your plc output is simply creating a force balance condition between the pneumatic actuator and any internal forces wanting to keep the valve closed. In a perfect world this force balance would linearly map pressure to position. In your case it sounds like there is a valve force offset so the force balance relationship is being skewwed.

Another possibility is the valve is designed to be a positive seal valve. This will apply extra closing force to make sure flow is stopped. You stated a couple of posts ago that if the PLC output doesn't go to zero on the way back to closed that you will still get media flow. Have you confirmed this? It is possible you simply have a spring force bias and that you need some minimum actuation pressure to get the valve to move. If that is the case your solution is easy.

If you do have binding you need to get rid of it. It's not worth messing around for a month coming up with a software fix for a bad component.

This shouldn't happen because of valve design, but it may be that the pressure of your media is helping to seal the valve closed. If this is the case, you would expect the valve to require some minimum pressure to open. However, when it opens it will open in a step, probably pretty close to the position expected from the command you give. As you decrease your output from this initial open point toward zero, the valve will act correctly until some lower limit, at which point it will snap shut.

Keith
  Reply With Quote
Old August 3rd, 2007, 10:09 AM   #15
plcnovel
Member
Pakistan

plcnovel is offline
 
Join Date: Feb 2006
Location: LHR
Posts: 215
I am sorry guys i got back to this thread very late. Actually i was in the process of getting some data about the valaves Bench settings and Transducers pressure settings. Here are the numbers:


Operating Range (I/P output) 6-30 Psi
Bench setting for the valve 14 - 30 psi
PLC card output (4-20 mA to I/P)

Which means that valve will not start to open until I/P has a pressure around 14 psi(about 9mA output from Output card, 33%). If the I/P operating range is not equal to Valve Bench Settings, experts say we need to add a positioner, What are your comments on it? Also if the positioner is needed, can we eliminate the need of it and work around in our plc logic or output card span to make these I/P/Valves working properly. Thanks a lot for your input
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Modicon PID Loops rgive LIVE PLC Questions And Answers 6 August 25th, 2009 03:20 PM
TI-505 PID problem karivelm LIVE PLC Questions And Answers 4 January 15th, 2007 04:41 PM
Simatic 545 Pid maintpro LIVE PLC Questions And Answers 7 August 17th, 2005 08:31 AM
Steam heating PID systems maintpro LIVE PLC Questions And Answers 3 November 10th, 2004 01:06 PM
Proportional valve driver control with PID lanman LIVE PLC Questions And Answers 6 February 25th, 2004 10:05 PM


All times are GMT -5. The time now is 02:56 AM.


.