Old September 24th, 2007, 11:35 AM   #1
JOLTRON
Lifetime Supporting Member
United States

JOLTRON is offline
 
JOLTRON's Avatar
 
Join Date: Aug 2006
Location: MI
Posts: 438
S7 300 to S7 200 ethernet

Is it possible to send information from a S7 300 plc to a 200 series plc thru ethernet. I have an add on machine that I would like to send a part number, and pass/fail information. I would like to have it entered into the datablock maybe in the V memory.

Thanks,
  Reply With Quote
Old September 24th, 2007, 12:11 PM   #2
rsdoran
Lifetime Supporting Member
United States

rsdoran is offline
 
rsdoran's Avatar
 
Join Date: Apr 2002
Location: Birmingham, AL
Posts: 7,372
Take a look at the CP-243 https://a248.e.akamai.net/cache.auto.../CP243-1_e.pdf
__________________
http://www.patchn.com Industrial Electrical & Maintenance @ www.patchn.com "Tell me and I forget, show me and I remember, involve me and I understand."
  Reply With Quote
Old September 24th, 2007, 02:52 PM   #3
curlyandshemp
Lifetime Supporting Member
Canada

curlyandshemp is offline
 
curlyandshemp's Avatar
 
Join Date: Jul 2005
Location: Toronto
Posts: 1,611
Quote:
Originally Posted by JOLTRON
Is it possible to send information from a S7 300 plc to a 200 series plc thru ethernet. I have an add on machine that I would like to send a part number, and pass/fail information. I would like to have it entered into the datablock maybe in the V memory.

Thanks,
You will find configuring the ethernet communication from the S7-200 to the S7-300 far simplier than other way around.
MicroWin has an Ethernet wizard that guides you through the steps. Step7-300, without the manuals and a lot of patience, good luck.

Step 7 MicroWin for S7-200 was developed in US, whereas Step 7 for S7-300 was developed in Germany. American software is always more intiutive and user friendly.

Ian
__________________
Work to Ride,
Then Ride to Work
  Reply With Quote
Old September 24th, 2007, 02:55 PM   #4
craig_avanzar
Member
United States

craig_avanzar is offline
 
craig_avanzar's Avatar
 
Join Date: Sep 2007
Location: san antonio, texas
Posts: 151
Quote:
Originally Posted by curlyandshemp
You will find configuring the ethernet communication from the S7-200 to the S7-300 far simplier than other way around.
MicroWin has an Ethernet wizard that guides you through the steps. Step7-300, without the manuals and a lot of patience, good luck.

Step 7 MicroWin for S7-200 was developed in US, whereas Step 7 for S7-300 was developed in Germany. American software is always more intiutive and user friendly.

Ian
I heered that. Got the t-shirt and a key chain.
  Reply With Quote
Old October 2nd, 2007, 06:07 AM   #5
JOLTRON
Lifetime Supporting Member
United States

JOLTRON is offline
 
JOLTRON's Avatar
 
Join Date: Aug 2006
Location: MI
Posts: 438
Alrighty, I have the basic concept of how it works. My next question is, If I am using the S7-200 series PLC to "GET" information from the S7-300 series, how do I specifie that I want to pull it from a specific address (ex P#db200.dbx40.0) Or the other way around how would I "PUT" it into a specific VB from the 300 to the 200.

Thanks,
-Joel
  Reply With Quote
Old October 2nd, 2007, 09:38 AM   #6
curlyandshemp
Lifetime Supporting Member
Canada

curlyandshemp is offline
 
curlyandshemp's Avatar
 
Join Date: Jul 2005
Location: Toronto
Posts: 1,611
Quote:
Originally Posted by JOLTRON
Alrighty, I have the basic concept of how it works. My next question is, If I am using the S7-200 series PLC to "GET" information from the S7-300 series, how do I specifie that I want to pull it from a specific address (ex P#db200.dbx40.0) Or the other way around how would I "PUT" it into a specific VB from the 300 to the 200.

Thanks,
-Joel
The ethernet wizard in MicroWin steps you through the procedure. In S7-300 you need to configure a connection # that the MicroWin will use in the wizard.
__________________
Work to Ride,
Then Ride to Work
  Reply With Quote
Old October 24th, 2007, 08:10 AM   #7
JOLTRON
Lifetime Supporting Member
United States

JOLTRON is offline
 
JOLTRON's Avatar
 
Join Date: Aug 2006
Location: MI
Posts: 438
While I'm setting up the connection in the S7200 it is asking me where it would like to pull the data from. This looks like it needs to be a type of VB (Ex: VB3) but the S7-300 uses DB's as DB501.dbx0.0 How do i get around this?

Thanks,
-Joel
  Reply With Quote
Old October 24th, 2007, 09:58 AM   #8
curlyandshemp
Lifetime Supporting Member
Canada

curlyandshemp is offline
 
curlyandshemp's Avatar
 
Join Date: Jul 2005
Location: Toronto
Posts: 1,611
Quote:
Originally Posted by JOLTRON
While I'm setting up the connection in the S7200 it is asking me where it would like to pull the data from. This looks like it needs to be a type of VB (Ex: VB3) but the S7-300 uses DB's as DB501.dbx0.0 How do i get around this?

Thanks,
-Joel
Try this link to Siemens support.

It has step by step instructions
__________________
Work to Ride,
Then Ride to Work
  Reply With Quote
Old October 24th, 2007, 01:11 PM   #9
JOLTRON
Lifetime Supporting Member
United States

JOLTRON is offline
 
JOLTRON's Avatar
 
Join Date: Aug 2006
Location: MI
Posts: 438
Thanks alot man. It was the TSAP that was confusing me. Got her all cleared up now.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
S7 & Controllogix over Ethernet beethoven_ii LIVE PLC Questions And Answers 15 March 13th, 2008 02:49 PM
Simulating a S7 200 prog. on 300 simulator geirove LIVE PLC Questions And Answers 13 November 7th, 2006 12:43 AM