Cimplicity hmi commoncation with mp2300 servo controler from yasakawa on modbus tcp

hii
i have a servo controler mp2300 from Yaskawa.
i want to connact with cimplicity hmi through modbus tcp protocol.
i open mudbus tcp request from mp2300 and configer the cimplicity hmi to work with modbus tcp/ip .
the problem is that when i config the point on cimplicity i get error massage -"point found to be invalid "
when i use address 0XXXX or 0XXXXX
4XXXX or 4XXXXX
i will appreciate if some body can help me
eli
  Reply With Quote
Old October 18th, 2007, 11:40 AM   #2
iansabey
Member
England

iansabey is offline
 
Join Date: Feb 2006
Location: Nottingham
Posts: 3
Never used a cimplicity but there's more than one type of notation.
Have you tried 4:XXXX

Good luck
Ian.
  Reply With Quote
Old October 18th, 2007, 11:47 AM   #3
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: Vancouver, WA, UMSA, United Marxist States of America
Posts: 5,845
There are multiple levels of conformance. The lowest level 0 requires only reads and writes of multiple registers, not I/O.
As suggested above you should stick to the 4x registers.
  Reply With Quote
Old October 18th, 2007, 12:44 PM   #4
LadderLogic
Member
United States

LadderLogic is offline
 
LadderLogic's Avatar
 
Join Date: Jun 2003
Location: Chicagolandia
Posts: 1,045
One should also realize that Yaskawa's addresing is 0-based, while a typical Modbus addressing is 1-based. So, if you want to access PLC's internal register MW1012, you would most likely have to configure it as 401013 (or 4:1013) in your HMI. Just do some experimenting.

There are HMI's on the market that can communicate with Yaskawa MP controllers via Ethernet using straight Yaskawa's addresing, e.g., Pro-face 3000 series. But if you have to do it with Cimplicity, you have to do it with Cimplicity...

And, BTW, I assume you did not forget to create a subroutine (what Yaskawa calls a "drawing") with MSG-RCV command as well as did not forget to configure a network connection accordingly. Just checking. This controller will not communicate with an HMI unless the correct "responder" code is running (it is a Japanese thing, I guess).
__________________
Don't trust, don't fear, don't beg...

Last edited by LadderLogic; October 18th, 2007 at 12:48 PM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Mitsubishi Q Series Modbus TCP module QJ71MT91 set up help req'd... Pocko LIVE PLC Questions And Answers 0 July 30th, 2006 02:45 AM
MODBUS TCP gurus cjh LIVE PLC Questions And Answers 1 August 19th, 2004 06:18 AM
Profibus - Modbus TCP translator ewm3 LIVE PLC Questions And Answers 5 May 6th, 2004 11:31 PM


All times are GMT -5. The time now is 04:04 AM.


.