Question Remote I/O

Im am designing a system containing a compactlogix controller with controlnet communication. I have some 24V I/O (8 inputs and 8 outputs) 1000 meters (3280 feet) away from the controller. I am looking for some recommendations on how to communicate with the I/O. The communication doesnt have to be fast, the I/O is mostly pushbuttons and lights. Should I go with controlnet? I might have to get a repeater (control net on coax is only good for 1000 meters). Should I go with remote I/O (I would need to purchase a card )? I am also not sure about the I/O module choice either. Point I/O or Flex I/O? any help is appreciated. thanks
  Reply With Quote
Old October 18th, 2007, 11:30 AM   #2
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 10,788
As you have already ControlNet onboard the CompactLogix then that is the natural choice.
You can extend the ControlNet with fiber repeaters. Here is a document explaining it:
http://literature.rockwellautomation...n001_-en-p.pdf
__________________
Jesper

Last edited by JesperMP; October 18th, 2007 at 11:36 AM.
  Reply With Quote
Old October 18th, 2007, 11:34 AM   #3
LJBMatt
Member
United States

LJBMatt is offline
 
Join Date: Apr 2004
Location: Dayton, OH
Posts: 430
Well is there a pupose you are using a Controlnet processor? If you use a processor with Ethernet/IP you could run fiber out to your remote station. There is no AB "Remote I/O" for compactlogix. Running coax that far will be more expensive than a fiber run i would imagine.
__________________
Matt Stefanski

Go Dayton Flyers!
  Reply With Quote
Old October 18th, 2007, 09:26 PM   #4
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 7,494
For I/O, and since you already have controlnet, definitely cast my vote for that over ethernet.

Use ethernet for HMI, programming terminal, and any peer to peer stuff so you don't have to buy a PC card for controlnet.

Get the ControlNet Media planning guide from ab.com too...There will be more planning and work in the media installation versus the ole blue hose RIO, but it's a super fast, reilable network in my limited experience. Easy to diagnose and keep downtime to a minimum.

The only failures I have seen were both acoompanied by flashing red LEDs on the faulty segment pointing to a failure of a passive tap, and the other was a "failed" repeater (not a fiber optic one).

It is very simple to dial the node number on any c-net network device with a screwdriver and plug and play...much more maintenance tech friendly IMHO. Both times the on-shift tech got it going without having to call in engineering support.

1 more vote for C-Net
Paul

EDIT: If you spring for the PC card for controlnet, you can plug into your remote rack and have ethernet speed to program your CPU 3280 feet away. This was very handy on our machines, to be able to park my PC right by the I/O I was working on and debug, and fine tune speed controls, etc...
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.

"You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway."

Last edited by OkiePC; October 18th, 2007 at 09:31 PM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Pepperl & Fuchs Profibus Remote I/O Slave Addressing martinAPD LIVE PLC Questions And Answers 3 August 14th, 2012 09:37 AM
AB SLC5/05 Remote I/O Block transfers Marc LIVE PLC Questions And Answers 7 January 19th, 2007 06:30 AM
Economical Remote I/O zmanvortex LIVE PLC Questions And Answers 19 February 17th, 2006 04:01 PM
Remote I/O Flex I/O Quick Change Tooling Fixture TamHoNutech LIVE PLC Questions And Answers 1 September 29th, 2005 05:46 PM
Slc-504 / Remote I/o // Flex I/o Viking03a LIVE PLC Questions And Answers 4 April 3rd, 2003 06:38 PM


All times are GMT -5. The time now is 10:30 PM.


.