USB connection not selectable for Simatic PC adapter USB, only COM is accessible
There is no “USB” item in the Set PG/PC Interface – Local Connection – Connection to, only serial port RS-232 (COM3) connection is there.
I experienced the same problem before, when the drivers of PC adapter USB where installed _after_ Step7. Consequently the problem was solved by changing the sequence: first the drivers of PC adapter USB, then Step7. Now any sequence doesn’t help, also keeping the PC adapter on or off during/after the installation. Also tried to check without Step7 installed (used to work like that before). Now the same installation distributives are used (all latest versions), only a different laptop – without COM port. Reference information: Old laptop: Asus A3Ac New laptop: Acer Aspire 5572 ZNWXMi SIMATIC PC Adapter USB V1.2 V01.02.00.00_02.02.00.03 V1.2.0.0 STEP 7 V5.4 + SP3 K5.4.3.0_9.5.0.1 K5.4.3.0 OS: Ms Windows XP Pro Eng. Adapter firmware - 1.2 Please help. |
|
|
|
#2 |
|
Member
|
Set PC adaptor
Go to PC Adaptor Select Properties Select USB rather than COM |
|
|
|
#3 | ||
|
Member
![]() Join Date: Apr 2007
Location: Nikolaev
Posts: 6
|
Quote:
Quote:
It has cheered me up, you have a good sense of humor. Just in case it was serious - it is NOT possible to select USB, there's no such selection item in the combo box. Last edited by DrewBul; November 1st, 2007 at 12:54 AM. |
||
|
|
|
#4 |
|
Member
|
OK to spell it out:
In Set PG-PC Interface Select PC Adaptor (Auto) In Set PG-PC Interface Select Properties In Properties - PC Adaptor (Auto) Select Local Connection Then Select USB instead of COM1 |
|
|
|
#5 | |
|
Member
![]() Join Date: Apr 2007
Location: Nikolaev
Posts: 6
|
Quote:
In fact, there's no "USB" selection item in the "Local Connection – Connection to" combo-box. And that was my question. You must be sick and tired already of stupid questions here. I would never post a message to a forum without spending several days trying all things myself and searching for the answer in Internet. I've re-installed Windows and Step7 a dozen times already. I'll be grateful if you suggest how I should have formed my question in order to make it 100% explicit and clear, and prevent such misunderstandings. I've spent quite some time making the optimal wording for the question, so your feedback will really be helpful. Well, thank you anyway. |
|
|
|
|
#6 |
|
Member
|
Your question is fine.
But is your USB PC Adaptor working now? |
|
|
|
#7 | |
|
Member
![]() Join Date: Apr 2007
Location: Nikolaev
Posts: 6
|
Quote:
But now I’ve found the solution. The problem was in the way Windows was installed. After re-installing Windows completely it is OK (before I used to restore the image of installed OS). The main suspicion is for Windows Updates: I’d installed the critical updates (KB873339-KB932168, 75 in total) before the drivers for PC adapter USB. Now I installed first the drivers, and then the updates – everything is OK. There’s still a small probability that the reason is different, but, having spent about 30 hours installing and re-installing, I don’t want to experiment any more. Also I'd like to express my opinion, based on 6 year experience, that Simatic soft is very heavy, slow, and capricious. Every new installation is a challenge, and if you don’t have the image of your hard drive with all the software properly installed, you risk spending several days on reinstalling every couple of months. |
|
|
|
|
#8 |
|
Member
|
I agree Simatic net is always a challenge. I havn't figured out whether that is just Siemens or a different way of thinking by the Germans. Probably a bit of both. Even something simple like a German proximity switch seems to have been made as difficult as possible in its instructions which often serve many models.
I have been told the German language Siemens manuals are much better, but that doesn't help me unfortunately. I also agree regarding making an image of Drive C: I always do that and have very few problems once I have sorted out a new PC with all the drivers I need and installed all my Siemens and Citect software. |
|
|
|
#9 | |
|
Member
![]() Join Date: Dec 2007
Location: Texas
Posts: 15
|
Quote:
R |
|
|
|
|
#10 | |
|
Member
|
Quote:
Actually I don't notice a lot of difference, sometimes it's the other way round, presumably the stuff originally developed in the US. |
|
|
|
|
#11 |
|
Member
![]() Join Date: Mar 2010
Location: Buchanan, MI
Posts: 6
|
Sorry to bring this thread up from the dead. I had the same problem as the OP and this thread showed up when I was searching for a solution.
In my situation it turned out that the installer that auto-runs on the CD is kind of funky. You know the one. Its the one that insists on rebooting your computer before it installs anything. In my case it rebooted my computer and still did not install anything even though it said it did. I found that out when out of frustration I tried the installer on the CD at D:\PC_Adapter_USB\Software\Setup\Setup.exe That's a whole lot easier than re-installing windows as DrewBul did. Hope this helps the next guy who gets stuck here. |
|
|
|
#12 |
|
Member
![]() Join Date: Apr 2007
Location: Nikolaev
Posts: 6
|
Simatic installers insist on rebooting if the rebooting was skipped after the previous installation. This shouldn't be connected with the fact that nothing was actually installed. That was probably due to a faulty installer or maybe some settings in the INI-file. Here's the link to the latest version (v2.0)
http://support.automation.siemens.co...ew/en/27062840 In my case re-installing Windows with the proper order of updates was inevitable: I executed "PC_Adapter_USB\Software\Setup\Setup.exe" from the beginning. Though in version 2.0 I never experienced the problem (USB option not selectable in combo-box). |
|
|
|
#13 |
|
Member
![]() Join Date: May 2012
Location: Sydney
Posts: 5
|
It's an old thread now, but maybe my recent experience with this problem can help someone else.
I had the same symptoms - no USB setting available in the local settings drop down menu for the PC adaptor. After trying a lot of different options, all I had to do was firstly uninstall the PC adaptor (with the add/remove interfaces setting in the Set PC/PG interface dialog), then make sure the adaptor is not plugged into your PC. Plug the adaptor in to the PLC. This powers it up. Then plug the USB in. In my case Windows then automatically recognised the PC adaptor and did the necessary installation. Afterwards the USB option was available for the PC adaptor. Hope this can help someone. |
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Siemens S7 with Scada using PC adapter USB | Marie | LIVE PLC Questions And Answers | 8 | November 7th, 2007 02:09 AM |
| Programming Simatic panels with USB PC adapter? | Gromit | LIVE PLC Questions And Answers | 1 | November 5th, 2007 01:40 AM |
| USB to RS-485 converter adapter | danw | LIVE PLC Questions And Answers | 4 | July 31st, 2006 03:48 AM |
| Can the 'Simatic PC adapter USB' be used with S7200? | Gromit | LIVE PLC Questions And Answers | 2 | June 19th, 2006 07:49 PM |
| Siemens PC adapter USB. | JesperMP | LIVE PLC Questions And Answers | 9 | March 16th, 2005 02:01 AM |