traic question
did a search on triac outputs since i didnt know anything about them. learned alot, ecspecially about leakage problems and potential shock hazards and such. but what i havent fount yet is what the advatage to using one is versus an isolated relay output. is there one? or is there a condition in which you MUST use one? thanks as always.
|
|
|
|
#2 |
|
Lifetime Supporting Member
![]() Join Date: Jun 2005
Location: Miami Beach
Posts: 289
|
The TRIAC output is a solid state device that if sized correctly for the switched load has an almost unlimited ON/OFF lifetime.
The RELAY is an electromechanical device. The mechanical components of the relay eventually wear out so it has a limited lifetime. The frequency of switching the outputs needs to be evaluated for each application and compared with the published specifications. From this one can determine if they will last the lifetime of the machine. |
|
|
|
#3 |
|
Lifetime Supporting Member + Moderator
|
Also I have been told that the majority of the time that the triacs fail, they fail closed.... if you have it on a heater application this could be trouble... make sure that the over temp safeties are NOT in the PLC and will drop out the heater
__________________
www.PLCTrainer.net PLC Trainers, Communication Cables and Automation Supplies, Allen Bradley ~ Siemens ... YouTube PLC help videos.. http://www.ind-concepts.com/Support_and_Downloads.htm |
|
|
|
#4 |
|
Member
![]() Join Date: Jul 2005
Location: Lucas, TX
Posts: 1,150
|
Another point is switching at zero-crossing. The triac will turn on and off when the sine wave passes through zero. A nice feature for resistive loads such as heaters because it reduces line noise. A relay switches any time, and can generate sparks when the contacts open or close.
|
|
|
|
#5 |
|
Member
![]() Join Date: Oct 2007
Location: cincy, OH
Posts: 27
|
great info. thanks all
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Integrator Business Question | mjrx | LIVE PLC Questions And Answers | 3 | April 12th, 2007 05:37 AM |
| How to Ask Questions The Smart Way | Ken Roach | LIVE PLC Questions And Answers | 14 | March 26th, 2007 08:12 AM |
| OT..Question for Elevator Mike!! | darrenj | LIVE PLC Questions And Answers | 35 | March 30th, 2006 02:09 AM |
| Data Display Software Question | markzb | LIVE PLC Questions And Answers | 3 | March 15th, 2006 04:41 AM |
| Omron PLC and ethernetmodule question | wwauters | LIVE PLC Questions And Answers | 3 | February 21st, 2005 11:35 PM |