Datatwist cable work for cc-link

I am wanting to know if a Belden CDT Datatwist FIVE 1624R (4 twisted pair shielded) will work as a communication cable for CC-link between QJ61BT11N to AJ65SBTB1-32D I/O.

Im getting the flashing ERR light on the QJ which is: A communication error station identified, or remote station No. duplicated.

I have my master set as station 0 and the I/O set to station 1.
Baud rate is set at 156 kbps and test cable is only 3ft long. I have went through and setup the cc-link parameters as the manual told me to do and says there are no errors when checked. Any help would be greatly appreciated.
  Reply With Quote
Old January 7th, 2008, 11:20 AM   #2
panic mode
Member
Canada

panic mode is offline
 
panic mode's Avatar
 
Join Date: May 2003
Location: Toronto, Canada
Posts: 1,961
will it work? it may...

as far as my experience goes, you can almost use pair of wet shoelaces but you should ensure that selected baud rate is low enough (that is 156kbps).
for example for bench testing i was using panel wires (not cable) without shileding or anything and they were about 3ft long.

i've posted one example not too long ago:
http://forums.mrplc.com/index.php?dlcategory=17
  Reply With Quote
Old January 7th, 2008, 05:06 PM   #3
RYAN A
Member
United States

RYAN A is offline
 
RYAN A's Avatar
 
Join Date: Nov 2002
Location: Bowling Green, KY
Posts: 6
Thanks for the info....It worked with the cable mentioned. Forgot to set my switch settings on the plc parameter for the QJ module.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
A link programming cable for Shihlin A-30MR PLC atish_bagchi LIVE PLC Questions And Answers 1 August 5th, 2010 03:00 AM
IF PC link PLC ,What kind of cable we need? Starter LIVE PLC Questions And Answers 2 April 14th, 2004 04:21 PM
1747-UIC Cable Requirement Philadelphia Frank LIVE PLC Questions And Answers 8 December 4th, 2003 07:38 PM


All times are GMT -5. The time now is 05:48 AM.


.