I am wanting to know if a Belden CDT Datatwist FIVE 1624R (4 twisted pair shielded) will work as a communication cable for CC-link between QJ61BT11N to AJ65SBTB1-32D I/O.
Im getting the flashing ERR light on the QJ which is: A communication error station identified, or remote station No. duplicated. I have my master set as station 0 and the I/O set to station 1. Baud rate is set at 156 kbps and test cable is only 3ft long. I have went through and setup the cc-link parameters as the manual told me to do and says there are no errors when checked. Any help would be greatly appreciated. |
|
|
|
#2 |
|
Member
|
will it work? it may...
as far as my experience goes, you can almost use pair of wet shoelaces but you should ensure that selected baud rate is low enough (that is 156kbps). for example for bench testing i was using panel wires (not cable) without shileding or anything and they were about 3ft long. i've posted one example not too long ago: http://forums.mrplc.com/index.php?dlcategory=17 |
|
|
|
#3 |
|
Member
|
Thanks for the info....It worked with the cable mentioned. Forgot to set my switch settings on the plc parameter for the QJ module.
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| A link programming cable for Shihlin A-30MR PLC | atish_bagchi | LIVE PLC Questions And Answers | 1 | August 5th, 2010 03:00 AM |
| IF PC link PLC ,What kind of cable we need? | Starter | LIVE PLC Questions And Answers | 2 | April 14th, 2004 04:21 PM |
| 1747-UIC Cable Requirement | Philadelphia Frank | LIVE PLC Questions And Answers | 8 | December 4th, 2003 07:38 PM |