PLC Back-up and Restore Test

I am in the process of writing a OQ (Operation Qualification) protocol for testing the back-up and restore of Siemens PLC -S7/400. Appreciate if some one could let me know the test procedure.

The procedure I have written is:

Test #1: Use a Laptop with Step 7 software installed to take the back-up. Create a directory, namely C:\backupcp2.2. Back up the software onto the created directory.

Expected Result for Test#1: PLC software is backed-up

Test#2: Download the software by reloading the back-up software from :/bckupcp2.2(Software backed-up from previous test). Confirm that after reloading the software PID Loop (FIT 400-02) of AHU-600400 is operating satisfactorily.

Expected Result for Test#2: PID Loop FIT 400-02 action is correct.

Any comments on the above test procdure.

Prasanna
  Reply With Quote
Old May 28th, 2003, 05:34 AM   #2
Alan Case
Lifetime Supporting Member
Australia

Alan Case is offline
 
Alan Case's Avatar
 
Join Date: Apr 2002
Location: Wagga Wagga
Posts: 1,260
Well if the program you backed up is corrupted when you restore to the original PLC the first thing it does is wipe the memory of the PLC, then tries to download the new program. Program corrupted, original program wiped, dead PLC, you looking for new job.
Make the back up then try to go online, if the programs match it will happen, if you backup is no good it wont. This info is valid for ABs so I am not sure of a Siemens.
  Reply With Quote
Old May 28th, 2003, 06:09 PM   #3
Allen Nelson
Member
United States

Allen Nelson is offline
 
Join Date: Apr 2002
Location: West Chester, PA
Posts: 1,368
Why OQ

Why are you trying to the Step 7 software? This is essentially what you are trying to do. Verifying that one group of parameters is retained (e.g., your PID settings) doesn't prove that ALL settings are retained.

Is Downloading a new PLC program part of the normal functioning of the process? Will operators be downloading different programs depending on what batch is being run?

If not, all you need to do is write up an SOP on how to backup and restore, and be done with it.

No one (even the FDA) cares how the program gets into the PLC. What they care about is that the program that was in the yesterday (or rather, on the day that it was validated) is the same program as when the batch was made. I don't know Step 7, but if there is a method of getting a serial number (checksum, download date) or some other identification from the downloaded program, then record it, just as you would record the serial number of the PLC. If there is not, then have a section that verifies that the program is the desired one by recording the off-line timestamp (or other info if the pharma has a document control system) and just DO the download. That way, you KNOW what program you are doing your OQ against.

But a test to upload and then down?, forget it.

Of course, that's my take on things. Everyone's validation department is slightly different. But trying to validate Step 7's upload/download ability would be like trying to validate Window's Explorer. At some point, you just have to assume that it works (even though, at times, it crashes.)
__________________
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 12:49 PM.


.