RSlogix5000 Rung Comments
I would like to know when you download a program to a PLC using RSlogix5000 are the rung comments sent to the PLC. If they are how can you upload them?
|
|
|
|
#2 |
|
Lifetime Supporting Member
|
Rung comments (and tag comments) are not downloaded to the PLC.
|
|
|
|
#3 |
|
Member
![]() Join Date: Sep 2007
Location: Midwest
Posts: 36
|
Yes the rung comments are stored in controller, all you have to do is upload program. This was from AB website. The software can fully upload the program logic for all four programming languages, as well as tag names, directly from a controller. This simplifies maintenance because you can always obtain the original source directly from the controller. With structured text, you can also obtain the in-line descriptions (comments) from a controller.
|
|
|
|
#4 |
|
Lifetime Supporting Member
|
Greetings almshouse ...
can you please tell us where in the Allen-Bradley website you found that information? ... we don't doubt that you found it there - but it needs to be corrected ... thank you ...
__________________
|
|
|
|
#5 | |
|
Member
![]() Join Date: Oct 2005
Location: Chicago
Posts: 1,366
|
Quote:
Upload and rung comments will be part of your upload. |
|
|
|
|
#6 |
|
Member
![]() Join Date: Sep 2007
Location: Midwest
Posts: 36
|
|
|
|
|
#7 |
|
Lifetime Supporting Member
|
are we talking about the same thing? ... RUNGS as in "Ladder Logic" rungs - and the comments for those rungs ...
I think the confusion might be coming from "comments" for the "Structured Text" programming language ... that's different ... we don't normally refer to the "lines" in Structured Text as "rungs" ... maybe that's where we're getting confused ...
__________________
|
|
|
|
#8 |
|
Lifetime Supporting Member
|
no offense, but I think that you're misreading that ...
the "logic" is the actual programming code ... and you also get the "tagnames" ... but the "rung comments" aren't stored in the controller ... only with "structured text" will you be able to upload any "comments" ... PS Edit ... I actually have heard "salesmen" say something like: "With the new ControlLogix all of your documentation is stored in the controller - so you won't have to worry about those offline files like with RSLogix5 and RSLogix500" ... those salesmen were misinformed ...
__________________
Last edited by Ron Beaufort; February 1st, 2008 at 04:12 PM. |
|
|
|
#9 |
|
Member
|
I think the Compact Flash option is what is being referred to.
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Rung Comments? | Leadfoot | LIVE PLC Questions And Answers | 31 | August 4th, 2010 03:11 AM |
| DL-06 question..... | David_Emmerich | LIVE PLC Questions And Answers | 4 | September 11th, 2007 09:29 AM |
| define digital rung in RSLogix5000 | shaarawi1984 | LIVE PLC Questions And Answers | 4 | October 15th, 2006 07:43 AM |
| Rslogix5 | plcdb222 | LIVE PLC Questions And Answers | 21 | September 29th, 2006 09:32 AM |
| Jumpin' rung comments. RSLogix | Steve Kemp | LIVE PLC Questions And Answers | 5 | February 11th, 2005 01:38 PM |