Old February 1st, 2008, 04:25 PM   #1
fons04
Member
Canada

fons04 is offline
 
Join Date: Nov 2007
Location: Quebec
Posts: 52
Host link unit lk201

Hi Guys,
I've a problem to connect my C200H CPU01 (host link unit lk201). I've a cable DB9 to DB25 wired like Omron Specs:
PC PLC
2------2
3------3
5------7
7-| |-4
8-| |-5

I've set dips switch like Omron sheet

I'm using CX-Programmer, I've entered my plc on it but when I'm trying to connect, the RCV led on the host link flash and it fail.
Thanks to help me
  Reply With Quote
Old February 1st, 2008, 05:38 PM   #2
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 3,452
Have you tried this one...this is the one that I make and everyone likes it

http://www.plctrainer.net/Omron_Universal_Cable.jpg
__________________
www.PLCTrainer.net

PLC Trainers, Communication Cables and Automation Supplies, Allen Bradley ~ Siemens ... YouTube PLC help videos.. http://www.ind-concepts.com/Support_and_Downloads.htm
  Reply With Quote
Old February 1st, 2008, 06:12 PM   #3
Durango
Member
Canada

Durango is offline
 
Join Date: Feb 2008
Location: Quebec
Posts: 8
What is the software you have to communicate?
  Reply With Quote
Old February 1st, 2008, 06:49 PM   #4
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 3,452
I know nothing... about Omron but I did find this at http://forums.mrplc.com/index.php?download=750 (not sure if you had it or not) its there different cables, but your cable may not be your issue...
__________________
www.PLCTrainer.net

PLC Trainers, Communication Cables and Automation Supplies, Allen Bradley ~ Siemens ... YouTube PLC help videos.. http://www.ind-concepts.com/Support_and_Downloads.htm
  Reply With Quote
Old February 2nd, 2008, 01:08 AM   #5
svn
Member
India

svn is offline
 
svn's Avatar
 
Join Date: Jul 2004
Posts: 69
fons04,
have you tried the following -
1)Link Selector (at back of LK201 ) in ON position
2)SW4 (Command Level) in position 2
3)Baud rate in your software same as per SW3 of LK201
4)Match LK201 unit number with that in software (default - 0)

Omron default comm settings are 7 data bits, 2 stop bits, even parity, 9600 baudrate.

Hope this helps

SVN
  Reply With Quote
Old February 2nd, 2008, 08:33 AM   #6
fons04
Member
Canada

fons04 is offline
 
Join Date: Nov 2007
Location: Quebec
Posts: 52
I'm using CX Programmer
  Reply With Quote
Old February 2nd, 2008, 10:34 AM   #7
fons04
Member
Canada

fons04 is offline
 
Join Date: Nov 2007
Location: Quebec
Posts: 52
SVN,
I've tried your tips and it make the same thing. I've a LK-201, it exist LK-201-V1, what's the difference and could be the problem?
  Reply With Quote
Old February 3rd, 2008, 11:23 PM   #8
svn
Member
India

svn is offline
 
svn's Avatar
 
Join Date: Jul 2004
Posts: 69
fons04,

I think the -V1 should not be a problem. If the RCV LED lights but XMT doesn't, it means that the comm settings are not matching (assuming cable is correct as mentioned by you). I think if you post the snapshots of comm settings in CX-Programmer and positions of all the switches (front and back) of LK201-V1 then it will be easier to find out the problem.

SVN
  Reply With Quote
Old February 7th, 2008, 07:23 PM   #9
fons04
Member
Canada

fons04 is offline
 
Join Date: Nov 2007
Location: Quebec
Posts: 52
I, on the host link LK201:
the RCV not light,it flash when i tried to connect, the RUN does'nt light, the XMT not, the ERROR not.
SW1=0
SW2=0
SW3=5
SW4=2

The dips switchs at back are:
1=off
2=off
3=on
4=off
and 0V at vertical one

Setting:
#card host link= 0
Port COM1
9600
7
Even parity
bit stop 2
response delay 2
thanks
  Reply With Quote
Old February 8th, 2008, 06:17 AM   #10
svn
Member
India

svn is offline
 
svn's Avatar
 
Join Date: Jul 2004
Posts: 69
fons4, for Host Link Unit to work , the RUN LED should be ON.

Check the following for "RUN Indicator does not light" from the section 5-4 of W143-E1-6 (Host Link Units System Manual)
If you don't have the manual then you can download it from Omron USA site.
Possible Causes:
1) Faulty contact in the connector between the PLC and the Host Link Unit.
2) PLC is resetting the Host Link Unit.
3) Host Link Unit is defective.
Remedies:
1) Check and repair connections.Turn the PLC OFF, then ON.
2) If necessary, check the PLC for an error or abnormal reset.
3) Replace the Host Link Unit.
SVN
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Omron #3G2C7-LK201-EV1, Host Link Unit rlmuirhead LIVE PLC Questions And Answers 17 January 12th, 2007 01:11 PM
about omron plc host link command : MB machelec LIVE PLC Questions And Answers 7 July 8th, 2005 11:40 AM
Host link thanhnhan2811 LIVE PLC Questions And Answers 2 April 13th, 2005 07:26 AM
Omron Host Link & Cimplicity rmor LIVE PLC Questions And Answers 1 February 4th, 2005 11:32 PM
omron c40k host link ready961 LIVE PLC Questions And Answers 1 January 23rd, 2003 09:38 AM


All times are GMT -5. The time now is 03:55 AM.


.