plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old February 19th, 2008, 01:20 AM   #1
dmun
Indonesia
dmun is offline
dmun's Avatar
SLC RIO setting???
Hello world.
Let me introduce, my name is Kalis.
i'm newbie in this forum.
I need help.
Recently i have a project using SLC 5/05 with RIO (its new for me).
Here is hardware configuration.
Chassis 0 (4 slot)
1747-L551
1747-BSN
Chassis 1 (10 slot)
1747-ASB
1746-NI8
1746-NO4I
1746-NI8
1746-NO4I
1746-IV8
1746-OW16
1746-IV8
1746-IV8
I have already connecting RIO network just like the ASB & BSN manual.
- RIO/DH+ BSN line 1 to line 1 ASB
- RIO/DH+ BSN line 2 to line 2 ASB
- RIO/DH+ BSN line SH to line SH ASB
- termination using 87ohm in each node(ASB and BSN side)
DIP switch setting in ASB:
1 2 3 4 5 6 7 8
SW1 ON ON ON ON ON ON ON ON
SW2 OFF ON OFF ON ON OFF OFF OFF
SW3 OFF ON ON ON OFF OFF ON ON
DIP switch setting in BSN:
1 2 3 4 5 6
SW1 OFF ON OFF OFF OFF OFF
SW2 OFF OFF OFF OFF
G data:
1/4 rack
1/4 rack
1/4 rack
1/4 rack
1/4 rack
1/4 rack
1/4 rack
1/4 rack
Everything is ready, then power up.
In the ASB, status nOC (which means no RIO communication)
in the BSN, FLT LED is flashing red (which means not configured properly)
when i try to run/online from RSLogix, its FAULTED.
I dont know where is my mistake?
Please give me any help.
How should i configure this module.
Thanks.
File Type: txt configure.txt (762 Bytes, 58 views)
Old February 19th, 2008, 01:53 AM   #2
Ken Roach
United States
Ken Roach is offline
Ken Roach's Avatar
Well, there are a lot of things wrong with your configuration.
First, the 1747-BSN is a Backup scanner. It's made to be installed in a pair with another controller and another 1747-BSN. Do you have a pair of "redundant" controllers and two 1747-BSN modules, or only one ?
Next, there are some problems with your RIO configuration, mostly on the 1747-ASB adapter. The problems are in red.
1 2 3 4 5 6 7 8
Logical Rack 00, Starting Group 00
230.4 kb/s, 16 logical Groups
Do not hold last state, Automatically Restart, restricted link response (no effect at 230.4 kb/s), Not Last Chassis, 2-slot addressing, Discrete Mode analog modules, Module Keying in Save Mode.
1 2 3 4 5 6
230.4 kb/s, RIO, User ID = 0, Not last module on local status link
SW2 OFF OFF OFF OFF
Local Status Link Address 1
Old February 19th, 2008, 02:05 AM   #3
dmun
Indonesia
dmun is offline
dmun's Avatar
thank you, Ken Roach.
actually, i will use redundant processor.
so, there is another BSN and L551 in the other 4-chassis.
i think to try that configuration first before move on to redundant part.
is it a MUST to try a redundant configuration if using BSN?
so, how should i configure the DIP switch (red)?
__________________
REDUNDANCY, its lyk a PLAYBOY thing.
if one fail, there's another one.
but, its HARD to try...
Old February 19th, 2008, 02:17 AM   #4
Steve Pali
New Zealand
Steve Pali is offline
Steve Pali's Avatar
Are you using decimal or octal? The processor SLC or PLC will change your image bit numbers. SLC numbers are 0-7 8-15 PLC numbers are 0-7 10-17 when using 1747-ASB module.
Steve Pali
Old February 19th, 2008, 02:26 AM   #5
Ken Roach
United States
Ken Roach's Avatar
Take a look at the composition of your remote I/O chassis:
1747-ASB
1746-NI8
1746-NO4I
1746-NI8
1746-NO4I
1746-IV8
1746-OW16
1746-IV8
1746-IV8
There is no addressing scheme that will provide 8 words of data per slot in a 1747-ASB remote chassis. "2-slot" addressing provides 1 input word and 1 output word per two slots". "1-slot" addressing provides 1 input word and 1 output word per 1 slot, and "1/2 slot" addressing provides 1 input word and 1 output word per 1/2 slot. 1/2 Slot addressing gets closest; if you pair up 4-channel analog Input and Output cards, they can "borrow" each others I/O data in pairs and you can get 4 Words of Input and 4 Words of Output per pair.
With your system, just make it simple and use 1-Slot Addressing and set the specialty module mode for Block Transfer.
Your 1747-ASB in a 10-Slot chassis will support 9 I/O modules, which in Single-Slot addressing is 1 Full Logical Rack plus one leftover card.
Set up your "G-Files" for just one checkmark in the top box, and select "Full Rack".
The "noC" error is about wiring, not configuration. Try switching the 1 and 2 wires on the 1747-ASB RIO network plug.
Old February 19th, 2008, 03:31 AM   #6
dmun
Indonesia
dmun is offline
dmun's Avatar
how do i know this is dec or oct?
thx steve.
Quote:
Steve Pali
__________________
Old February 19th, 2008, 04:06 AM   #7
Steve Pali
New Zealand
Steve Pali's Avatar
I agree with Ken, just use 1 slot addressing, and if your using a SLC processer your in decimal numbered 0-15.
Steve Pali
Old February 19th, 2008, 04:23 AM   #8
dmun
Indonesia
dmun is offline
dmun's Avatar
thx.
now, i already understand how to count logical rack.
hmm, i've tried to switch the wire (1 & 2). nOC still appears.
i will try to re-wire the connection.
is it right, if i'm using termination 87ohm, in each end of node (total 3 node -> 2 BSN & 1 ASB)?
how about FLT blinking in BSN?
it is indication of wrong configuration, isn't it?
Kalis
__________________
Old February 19th, 2008, 06:22 PM   #9
dmun
Indonesia
dmun is offline
dmun's Avatar
Hello, Ken.
I've already re-wiring the connection.
2 Processor, 2 BSN & 1 ASB (RIO) with hardware configuration just like before.
Then DIP switch as you suggested.
(8, logical groups, 1-slot addressing, Block Transfer)
Setup "G files" just one checkmark and "Full Rack"
The problem is still the same as before.
FLT LED blinking in the BSN
nOC in the ASB
How should i do next?
Is there any programming that i should download to the processor first (except the G files)?
Thanks.
Kalis
__________________
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Slc 500 - Bsn - Rio - Pv capriconian20 LIVE PLC Questions And Answers 34 May 19th, 2007 08:22 AM
Ab Plc5 Rio Problem. fernandes LIVE PLC Questions And Answers 5 March 7th, 2004 01:25 PM
RIO 1771 rack to SLC Jezz LIVE PLC Questions And Answers 1 November 17th, 2003 10:36 AM
Trouble setting up NPORT express with SLC 5/04. PLEASE HELP! wlemst88 LIVE PLC Questions And Answers 46 June 25th, 2003 03:05 PM
Trouble setting up NPORT express with SLC 5/04. PLEASE HELP! wlemst88 LIVE PLC Questions And Answers 1 April 10th, 2003 02:00 PM