VFD Pump Control PID question

Just looking for some opinions on VFD PID control design. What would you consider a better design for a VFD pump controlling pressure.

1. PID: Actual pressure (PV) compared to pressure setpoint (SP), output (CV) scaled directly to VFD 4-20ma. (Optionally, Actual pump speed and commanded speed are compared to generate an alarm if deviation is too large.)

2. PID: Actual pressure (PV) compared to pressure setpoint (SP), output (CV) scaled 0-100%. This 0-100% value is sent to another PID to control actual pump speed 0-100%(PV) to speed setpoint (SP), output (CV scaled directly to VFD 4-20ma.

I like the practice of comparing actual pump speed to desired speed, but both seem to accomplish the same thing, with the first being more simple. I'm interested in hearing opinions on this.

Thanks
  Reply With Quote
Old February 26th, 2008, 12:52 PM   #2
averytc
Member
United States

averytc is offline
 
averytc's Avatar
 
Join Date: Jul 2002
Posts: 114
I use option 1. What would be a reason to use option 2?
  Reply With Quote
Old February 26th, 2008, 01:40 PM   #3
ttichy
Member
United States

ttichy is offline
 
Join Date: Jul 2006
Location: strongsville, OH
Posts: 74
What pump are you using? How close are you able to regulate the pressure? There is one (somewhat pricey) system (http://www.kadantunigy.com/index.html) that does pump modeling and torque control to give you pressure and flow control
  Reply With Quote
Old February 26th, 2008, 05:08 PM   #4
DickDV
Member
United States

DickDV is offline
 
Join Date: May 2002
Location: Kalamazoo MI
Posts: 2,071
If you are trying to regulate pressure, why fuss with pump/motor speed?

Set your PID loop up to feed back pressure to a pressure setpoint comparator and that's it!

We do it all the time here and the system works just fine.
  Reply With Quote
Old February 26th, 2008, 06:27 PM   #5
SCADA_Dude
Member
United States

SCADA_Dude is offline
 
Join Date: Feb 2008
Location: California
Posts: 115
Thanks for the feedback. The system has very accurate pressure control, with high capacity VFD drives (1500GPM H2O Pumps), so it works great as described in option 1 above.

I am glad everyone seems to think option 1 is better. I have seen option 2 used on some old RTU controls and it seemed like a kludge to me. I am somewhat new to VFD PID's and just wanted to make sure I wasn't overlooking something. Peer review is a great way to build confidence in a design.

Thanks again
  Reply With Quote
Old February 28th, 2008, 05:58 AM   #6
danesh
Member
Iran

danesh is offline
 
Join Date: Jul 2005
Location: Teh
Posts: 88
Quote:
Originally Posted by DickDV
If you are trying to regulate pressure, why fuss with pump/motor speed?


Set your PID loop up to feed back pressure to a pressure setpoint comparator and that's it!

We do it all the time here and the system works just fine.


Dear DIKDIV,

Are you having any experience in VFD submersible pump? I use a VFD for submersible pump and cause damage in bearings pump.

Could you please help me?

Danesh
  Reply With Quote
Old February 28th, 2008, 03:26 PM   #7
DickDV
Member
United States

DickDV is offline
 
Join Date: May 2002
Location: Kalamazoo MI
Posts: 2,071
I guess my earlier post wasn't very clear. I meant to say that I would use a VFD but only put PID control on the pump discharge pressure. I don't see any benefit in closing up the speed loop in addition to the pressure loop.

Danesh, you need to start a new thread. You probably don't mean any harm but injecting a new question like you have done is called "hijacking a thread" and is not considered acceptable.
  Reply With Quote
Old February 29th, 2008, 10:36 PM   #8
danesh
Member
Iran

danesh is offline
 
Join Date: Jul 2005
Location: Teh
Posts: 88
Quote:
Originally Posted by DickDV
I guess my earlier post wasn't very clear. I meant to say that I would use a VFD but only put PID control on the pump discharge pressure. I don't see any benefit in closing up the speed loop in addition to the pressure loop.

Danesh, you need to start a new thread. You probably don't mean any harm but injecting a new question like you have done is called "hijacking a thread" and is not considered acceptable.
,

I am Very Sorry, Excuse me. I will start new thread.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
VFD to control heaters ?? leitmotif LIVE PLC Questions And Answers 24 March 30th, 2014 04:14 PM
PID Loop question tgaljar LIVE PLC Questions And Answers 13 June 14th, 2006 07:46 AM
PID process control theory vs practice Pandiani LIVE PLC Questions And Answers 13 September 20th, 2005 11:55 AM
Difference between Proces Control PID and Temperature Control PID. JesperMP LIVE PLC Questions And Answers 1 May 14th, 2004 02:18 AM
VFD Question harryg LIVE PLC Questions And Answers 28 January 23rd, 2003 06:24 PM


All times are GMT -5. The time now is 03:06 PM.


.