Could anybody tell me if RS232(9-pin From a PC) network can be connected directly to a RS485 device without the help of a converter. Sorry for the silly question. |
|
|
|
#2 |
|
Member
|
The short answer is NO! The two protocols are different. You can configure a PLC processor for RS232 communication through RSLinx if the processor has an RS232 port and connector, also 9 pin. To use the DH485 connector you must configure your link for DH485 and use a converter that will handle USB to 485, as the old PIC module no longer functions with the latest versions of Windows, you have to use the UIC converter.
__________________
Thunder is good, thunder is impressive; but it is lightning that does the work! Mark Twain-8/28/1908 |
|
|
|
#3 |
|
Lifetime Supporting Member
![]() Join Date: Aug 2004
Location: Kent
Posts: 757
|
Hi,
Yes..it's possible to have a RS232 to RS485 without a converter...I've used it before on Siemens MM3 drives, drawing is attached. Note though that this shouldn't be used as a permanent solution. |
|
|
|
#4 |
|
Member
|
Once again no. Besides protocol differences found in comm products like RSLinx, there is a big difference in signal voltages and how each responds, 232 is single ended and 422/485 is differential. There are impedance differences as well. The cost of a simple converter can be as low as US$50. Don't waste time trying to get around this difference.
|
|
|
|
#5 |
|
Member
![]() Join Date: Apr 2008
Location: Bangalore
Posts: 7
|
Beginner
Thanks a lot for the reply.
But even now there is a twist to the PDF that was attached. So should I finally come to a conclusion that the answer is No? As the PDF too states that it’s only for Demo purpose and not a permanent solution. So I guess I will come to a conclusion that it is possible but is not the feasible solution. |
|
|
|
#6 |
|
Lifetime Supporting Member
|
Absolutely NO. That PDF is a quick and dirty hack, that only works at all because of an oddball configuration of the port on the MicroMaster drive. Honestly, it's just plain stupid that a company like Siemens even demonstrates nonsense like that.
|
|
|
|
#7 | |
|
Lifetime Supporting Member
![]() Join Date: Aug 2004
Location: Kent
Posts: 757
|
Quote:
|
|
|
|
|
#8 |
|
Member
![]() Join Date: Apr 2008
Location: Bangalore
Posts: 7
|
Beginner
Once again I would like to thank you for the reply.
now I Have got the right answer finally as a simple "NO". Thanks to all |
|
|
|
#9 | ||
|
Lifetime Supporting Member
![]() Join Date: Aug 2004
Location: Kent
Posts: 757
|
Quote:
Quote:
This afternoon, as a more generic test (than connecting to a Micromaster 3), I connected this lead to the RS485 side of a RS485/RS232 converter and used the finished assembly to connect 2 PC's together via their serial ports. I ran a terminal program on both PC's and established bi-directional communication immediately. Last edited by krk; April 22nd, 2008 at 10:02 AM. |
||
|
|
|
#10 |
|
Member
![]() Join Date: Apr 2008
Location: Bangalore
Posts: 7
|
Beginner
Thanks KRK for the answer. I can understand that you have performed a test on this matter.
So I thank you so much for the answer. I also would thank all the others for the answers that you have provided. |
|
|
|
#11 | ||
|
Lifetime Supporting Member
![]() Join Date: Aug 2004
Location: Kent
Posts: 757
|
Quote:
But I'd like to re-iterate that it's just a (handy?) trick and not an engineered solution...you were correct when you said: Quote:
Last edited by krk; April 24th, 2008 at 03:49 AM. |
||
|
|
|
#12 |
|
Member
|
This afternoon, as a more generic test (than connecting to a Micromaster 3), I connected this lead to the RS485 side of a RS485/RS232 converter and used the finished assembly to connect 2 PC's together via their serial ports. I ran a terminal program on both PC's and established bi-directional communication immediately
probably up to 50' seriously doubt it will work up 1000' yes it will work because it still has a differential voltage change but the rs 232 port does not have the driving current for long distances |
|
|
|
#13 |
|
Lifetime Supporting Member
|
The problem is with the signal levels. RS-485/422 are well defined line-driver signal levels. RS-232 is just about completely random, with potentials of up to 25 volts, positive and negative, for a potential 50 volt differential.
I'm just not going to trust mixing signals like that. The devices cost much more than a proper converter. |
|
|
|
#14 |
|
Member
|
Trust me Rdrast neither do I reminds me of simplex networks
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| help a protool beginer | Escumalha69 | LIVE PLC Questions And Answers | 6 | April 1st, 2008 05:15 PM |
| basic beginer, needing help | buckshot | LIVE PLC Questions And Answers | 2 | March 3rd, 2007 02:52 PM |
| RSLogix500 beginer | Krcedinac | LIVE PLC Questions And Answers | 4 | August 16th, 2006 02:14 AM |
| a beginer likes to learn | mutaz | LIVE PLC Questions And Answers | 4 | February 21st, 2006 07:40 AM |
| beginer needs help | seeking info | LIVE PLC Questions And Answers | 2 | March 13th, 2005 06:58 PM |