Old June 11th, 2008, 12:34 AM   #1
Patrick
Lifetime Supporting Member
United States

Patrick is offline
 
Join Date: Apr 2007
Location: Washington State
Posts: 96
Trying to program a 1761-NET-ENI

Ok. A long time ago I had a similar problem that drove me up the wall. The answer was right in front of me, but I couldnít see it. The problem was programming my first DH+ message. I just new I had to have a command at the other end. Yes I read several times that the address had to be available. But I just couldnít see it tell someone call my attention to it. Now I think I have the same problem.



Trying to program a 1761-NET-ENI. Let me back up. A new control cabinet came in to replace an out dated cabinet. It has a MicroLogix 1500 a NET-ENI and a panelview plus 600. The program for the MicroLogix has no documentation. The panelview plus program is a mer. not APA. I have never programmed a NET-ENI. And this is the second panelview plus that I have seen, and the first I have program.



I have the ENI/ENIW Utility. I can change the Ethernet address. How do I set the RS232 address? I see all kinds of examples in the utility manual. But I an not sending any messages.



It is late. Iím tired and confused. I hope it is something as simple as the DH+ problem was.
  Reply With Quote
Old June 11th, 2008, 12:44 AM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,917
I'm not totally clear on what your question is.

The 1761-NET-ENI's usual function is to take incoming EtherNet/IP messages and translate them into DF1 format on the RS232 port.

The RS232 port needs very little configuration; you just set up the serial framing (speed, data bits, stop bits, parity) and error checking mechanism, and plug it into a controller RS232 port with the same configuration.

What exactly is the problem that you are trying to solve ? Describe more about how each of these devices are connected to one another.
  Reply With Quote
Old June 11th, 2008, 12:49 AM   #3
Patrick
Lifetime Supporting Member
United States

Patrick is offline
 
Join Date: Apr 2007
Location: Washington State
Posts: 96
I can see how to program the Ethernet address. Where do I program the RS232 info? Is this program in the Utility Software?


By the way. Glad to see your back. May be i'm looking too hard at the problem.

Last edited by Patrick; June 11th, 2008 at 12:55 AM.
  Reply With Quote
Old June 11th, 2008, 12:51 AM   #4
Patrick
Lifetime Supporting Member
United States

Patrick is offline
 
Join Date: Apr 2007
Location: Washington State
Posts: 96
Sorry should have read the whole post.

Micrologix thought Ethernet to panelview plus.

Last edited by Patrick; June 11th, 2008 at 12:56 AM.
  Reply With Quote
Old June 11th, 2008, 01:05 AM   #5
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,917
I ought to look at the utility before posting my memory....

The first tab of the utility has a "232 Baud Rate" drop-down menu. The default is Auto (it will auto-detect the RS232 baud rate) or you can set it for a specific baud rate.

The framing (data bits, stop bits, parity, error checking) is non-settable with the 1761-NET-ENI. It uses the defaults that SLC and MicroLogix controllers use: 8 data bits, 1 stop bit, no parity, CRC Error Checking. Those are also the default settings of a MicroLogix 1500.

If the 1716-NET-ENI plugs into the Channel 0 port of the MicroLogix 1500 controller, you can leave the DF1 baud rate in the -NET-ENI on Auto, and press the "DCOMM" button on the MicroLogix 1500 and they will definitely communicate correctly over DF1 Full Duplex.

One thing that has been a gotcha for me is that the Net-ENI utility can sometimes run at a different serial rate than the
controller, which I think requires a power cycle of the Net-ENI in between disconnecting your PC and connecting the PLC.
  Reply With Quote
Old June 11th, 2008, 01:08 AM   #6
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,917
As far as the PV+ is concerned, it will treat the MicroLogix 1500 as though it was an SLC-5/05.

Create a shortcut in RSLinx Enterprise (the comms driver inside RSView Studio, not RSLinx Classic that you use for everything else) and RSView Studio should easily browse the addresses of the MicroLogix.
  Reply With Quote
Old June 11th, 2008, 01:12 AM   #7
Patrick
Lifetime Supporting Member
United States

Patrick is offline
 
Join Date: Apr 2007
Location: Washington State
Posts: 96
As mention before I have the mer. file not the apa file.

As to the net-eni all I have to do is program the ethernet address and make sure that the 232 baud is set at auto then depress the dcomm button on the micrologix. Is that correct?

Last edited by Patrick; June 11th, 2008 at 01:17 AM.
  Reply With Quote
Old June 11th, 2008, 01:18 AM   #8
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,917
Yes, connecting the Net-ENI really is (usually) that simple.

So, there's this new cabinet. And there's this PV+, this MicroLogix, and this Net-ENI.

Are you being asked to add to or modify the PV+ ? I'm not sure from your post what about the system isn't working or needs to be changed. No need for a lengthy explanation here if it's not germane, I'm just curious.
  Reply With Quote
Old June 11th, 2008, 01:26 AM   #9
Patrick
Lifetime Supporting Member
United States

Patrick is offline
 
Join Date: Apr 2007
Location: Washington State
Posts: 96
The system can in brain dead. I was ask to load the programs and test it out. The micrologix is no problem. Just that the program has no documentaion to it. And the input output wiring does not match the print. As to the panelview plus I have not ever program one or set it up from sretch. On top of that, all I got was the mer. file not the apa file.
  Reply With Quote
Old June 11th, 2008, 01:27 AM   #10
Patrick
Lifetime Supporting Member
United States

Patrick is offline
 
Join Date: Apr 2007
Location: Washington State
Posts: 96
Well it's 11:30 Quiting time. It was nice chatting. If it still is not working I'll bug Walt.


Bye
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Wierd thing with 1761 net eni AndrewB LIVE PLC Questions And Answers 0 August 30th, 2007 10:53 PM
1761 Net Aic Module phil hughes LIVE PLC Questions And Answers 1 June 18th, 2007 08:13 PM
Urgent!!! Ultimate Traffic Light Program Needed!!! TWControls LIVE PLC Questions And Answers 34 May 15th, 2007 07:15 AM
PLC Program Management zmanvortex LIVE PLC Questions And Answers 5 November 1st, 2004 10:03 AM
ENI question Williyb LIVE PLC Questions And Answers 6 July 11th, 2004 02:21 AM


All times are GMT -5. The time now is 08:51 AM.


.