Old June 18th, 2003, 01:42 AM   #1
ashley
Australia
ashley is offline
ControlLogix IO Card Fault
Please look at the attached RSLogix5000 screen capture.
I am checking for IO card fault in a remote ControlLogix chassis. I have another 8 similar rungs above rung 8 for checking the status of the remaining IO cards.
Will this logic give me an IO card fault if a card is pulled out of it's slot or if a card is missing, i.e. will tag XA_0139B be set?
Thanks.
Old June 18th, 2003, 01:58 AM   #2
Ken Roach
United States
Ken Roach is offline
Ken Roach's Avatar
Yes, that looks like a good way to check the FaultCode objects for all of the I/O modules in your system. You can use it for modules in the local chassis as well as on ControlNet or EtherNet/IP networks.
I'd condition the logic to run occasionally instead of every scan. That FBC takes up a little scan time and you don't need to run it any faster than necessary to check on the I/O modules.
Old June 18th, 2003, 04:07 AM   #3
ashley
Australia
ashley is offline
Ken, I used this logic for checking IO card fault at one site. Didn't test the logic at that time. Later, the customer pulled out a couple of modules but says that he didn't get an IO card fault alarm. I need to go to site and check it.
My doubt is whether the fault code changes from 0 to some other value if a module is pulled out from its slot. Is a fault code generated if a module is not present in its slot?
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
ControlLogix 5000 Minor Math Fault Question rdrast LIVE PLC Questions And Answers 5 August 2nd, 2012 12:27 AM
AB PLC5/80B RIO Flex IO Fault corkers LIVE PLC Questions And Answers 9 September 4th, 2004 01:12 AM
1784-PCMK/B Card Health msinclair LIVE PLC Questions And Answers 6 August 13th, 2004 09:19 AM
ControlLogix Minor Fault Question gizmo LIVE PLC Questions And Answers 2 October 10th, 2003 07:53 AM
ControlLogix, SST Profibus DP Interface Card and Hesch Baghouse Controller Lamia LIVE PLC Questions And Answers 0 August 14th, 2002 12:35 AM