HOA with Start / Stop

So I'm installing 4 pumps (in a rather large system) and each will have an HOA switch as well as remote start/stop. I'm torn as to whether I should or shouldn't eat up 4 PLC inputs per station. 1 for Manual, 1 for Auto, 1 for start PB and one for stop PB. I know I can get away without using so many I/O, but what is best practice/Industry standards. Any help?
  Reply With Quote
Old May 26th, 2008, 06:17 AM   #2
controlled
Lifetime Supporting Member
Canada

controlled is offline
 
Join Date: Nov 2005
Location: bowmanville
Posts: 408
personally i would use all 4 per station. That will make it much easier in the future if you have to modify any single station.



Derek
  Reply With Quote
Old May 26th, 2008, 07:35 AM   #3
randylud
Member
United States

randylud is offline
 
randylud's Avatar
 
Join Date: Oct 2002
Location: Greensboro,NC
Posts: 933
Try this approach!

Quote:
Originally Posted by JEldreth
So I'm installing 4 pumps (in a rather large system) and each will have an HOA switch as well as remote start/stop. I'm torn as to whether I should or shouldn't eat up 4 PLC inputs per station. 1 for Manual, 1 for Auto, 1 for start PB and one for stop PB. I know I can get away without using so many I/O, but what is best practice/Industry standards. Any help?
You do not need two inputs for the Auto/Manual function. A single selector switch input, either NO or NC will suffice. When you program, it will reflect the condition of the selector as either being in Auto or not and if it is not, by default it is in manual if you write your program properly. As for the the start stop inputs for those PBs, you should have them. If you need further help, just show some of your work and I am sure many will be willing to help you.
__________________
Thunder is good, thunder is impressive; but it is lightning that does the work!
Mark Twain-8/28/1908
  Reply With Quote
Old May 26th, 2008, 08:01 AM   #4
krk
Lifetime Supporting Member
England

krk is offline
 
Join Date: Aug 2004
Location: Kent
Posts: 786
Quote:
Originally Posted by randylud
You do not need two inputs for the Auto/Manual function. A single selector switch input, either NO or NC will suffice. When you program, it will reflect the condition of the selector as either being in Auto or not and if it is not, by default it is in manual if you write your program properly. As for the the start stop inputs for those PBs, you should have them. If you need further help, just show some of your work and I am sure many will be willing to help you.
He's using 3 position selector switches ....
HOA = Hand - Off - Auto
  Reply With Quote
Old May 26th, 2008, 08:15 AM   #5
randylud
Member
United States

randylud is offline
 
randylud's Avatar
 
Join Date: Oct 2002
Location: Greensboro,NC
Posts: 933
Makes do difference, the hand or manual position is still only one input! If it is on, it could be in Auto, and Hand when it is not on. The off function could be hard wired into the output to prevent the coil from being energized and would not require an input to the PLC at all. Just takes two contact blocks on the operator for the selector.
__________________
Thunder is good, thunder is impressive; but it is lightning that does the work!
Mark Twain-8/28/1908

Last edited by randylud; May 26th, 2008 at 08:18 AM.
  Reply With Quote
Old May 26th, 2008, 08:34 AM   #6
Oakley
Member
United States

Oakley is offline
 
Oakley's Avatar
 
Join Date: Oct 2004
Posts: 1,083
All that you should need is the Auto. The hand position should go directly to the hard wired circuit, and the off should be off.

So, the only input that the controller needs is Auto - any other position should be manual.

Then have a running feedback to confirm operational status.

Now if you want to have a start stop auto from your SCADA system, the switch should be in auto for it to work.
Reviewing the modes with this setup:

Off
Hand
Auto - Auto
Auto - Start
Auto - Stop
__________________
Artificial intelligence never overcomes natural stupidity.
  Reply With Quote
Old May 26th, 2008, 08:45 AM   #7
tomalbright
Member
United States

tomalbright is offline
 
Join Date: May 2006
Location: Gonzales, LA
Posts: 691
I've seen "hand" used with minimal engine-damage type protection, so it's not out of the question to use the input. Sometimes you want to know when your switch is "OFF", as well. In that case, you do need both the H A positions wired.

JEldreth - which is safer - H and O being unwired, or knowing their positions?
__________________
"We really don't care how you program your PLC, just don't blow yourself up!"
www.GeekQuake.com Also on Facebook!

  Reply With Quote
Old May 26th, 2008, 09:06 AM   #8
Ken Moore
Member
United States

Ken Moore is offline
 
Ken Moore's Avatar
 
Join Date: May 2004
Location: Upstate South Carolina
Posts: 2,325
For mission critical applications, where you need to run something even if the PLC is off line, we do the following:

H-O-A

In auto the PLC output goes to the motor starter, in hand the local start/stop buttons control the motor starter, in off, neither go to the starter.

The Auto position has two contacts, both N.O. when in Auto the 1st N.O. tells the PLC that it has control, the other then allows current to flow from the PLC output module to the starter. The starter has feedback to the plc as well. If the plc is trying to start the pump and it is not in auto, an alarm is generated to the operator.
__________________
"To give real service you must add something that cannot be bought or measured with money; and that is sincerity and integrity."
- Donald A. Adams


Last edited by Ken Moore; May 26th, 2008 at 09:09 AM.
  Reply With Quote
Old May 26th, 2008, 09:08 AM   #9
Stationmaster
Member
United States

Stationmaster is offline
 
Stationmaster's Avatar
 
Join Date: Aug 2007
Location: Florida
Posts: 577
I concur with Oakley, as your question was about the "industry standard" for this situation.

The pump stations I have seen, and built, use only the "AUTO" position of the H-O-A switch as an input to the PLC. When the switch is in the "OFF" position or "HAND" position the PLC program translates the input as "NOT AUTO". The "OFF" position has no connection to anything. The "HAND" position is intended to run the pump even if the PLC has failed, has no power, or has been removed from the picture entirely.

That is: "HAND" is a completely independent circuit, separate from the PLC. You may consider including some safeties in this "independent" circuit by running "control power" through a set of contacts on the phase monitor and through a set of contacts on the low level sensor before it goes to the N.O. "HAND" switch contacts on its way to the contactor (or VFD).

Stationmaster
  Reply With Quote
Old May 26th, 2008, 06:03 PM   #10
JEldreth
Member
United States

JEldreth is offline
 
Join Date: Feb 2007
Location: Newark, Delaware
Posts: 3
Thanks for all the input. After reading the GDS it is critical to know all positions of all switches because there are a few valves that have to cycle before the pump can be started, even in the Hand position. I also need feedback to the HMI to know if it is Auto, Off or Hand so it looks like I will eat up 4 I/O for each station. Again, thanks for all the ideas and comments.
  Reply With Quote
Old May 26th, 2008, 08:49 PM   #11
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,333
What is/a "GDS"
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old May 26th, 2008, 09:31 PM   #12
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 3,768
Quote:
Originally Posted by Mickey
What is/a "GDS"
Gosh Darn Safety
Georgetown Day School
Global Delivery System
Geriatric Depression Scale
Global Dialing Scheme
.....
.....
need more?
__________________
www.PLCCable.com Save 5% on all cables and trainers, enter coupon code PLCTalk at check out... see our NEW line of PLC programming cables, smaller, cheaper, better....
  Reply With Quote
Old May 26th, 2008, 09:35 PM   #13
JEldreth
Member
United States

JEldreth is offline
 
Join Date: Feb 2007
Location: Newark, Delaware
Posts: 3
Sorry...A company acronym, General Design Specifications. It is a written synopsis of how the entire system should operate, what parts to use, what methods and software to use. About 300 pages for a small system.
  Reply With Quote
Old May 26th, 2008, 10:25 PM   #14
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,333
Quote:
Originally Posted by geniusintraining
Gosh Darn Safety
Georgetown Day School
Global Delivery System
Geriatric Depression Scale
Global Dialing Scheme
.....
.....
need more?
That one I understand.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old May 27th, 2008, 12:29 AM   #15
elitheei
Member
United States

elitheei is offline
 
Join Date: Nov 2004
Location: Atlanta
Posts: 81
In some places I have seen the Hand circuit used as a "jog" for field control. So in one aspect you actully hand a momentary (jog) - off - auto. I think this is quite common actually.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Start and Stop buttons help ayoung87 LIVE PLC Questions And Answers 6 August 8th, 2007 04:16 PM
E stop switch -- best design?? leitmotif LIVE PLC Questions And Answers 15 August 1st, 2007 10:12 AM
How a Ladder is Scanned Sarit LIVE PLC Questions And Answers 19 April 28th, 2005 10:42 AM
Lets Talk E-Stops plcman777 LIVE PLC Questions And Answers 15 October 25th, 2004 08:15 AM
N.O stop N.C start Ryan LIVE PLC Questions And Answers 7 March 5th, 2004 02:07 AM


All times are GMT -5. The time now is 10:20 AM.


.