We have been having alot a problems with our Ultra 3000 servo drives faulting out on E20 error. I was wanting to see if anyone else is having this problem. We are using a high res. encoder for feedback with the specified shielded cable. We have three different machines with this setup and have tried everything imaginable to resolve this issue but have been unsuccesful. One machine has the encoder cable in conduit from motor to drive, two are in cable tray with only other shielded cables. One of the machines with the cable in tray does not have the issue but the other does. I can not find any difference in the two of them. We have tried it with shield grounded and ungrounded. All machines have the encoder cable spliced about 10 ft from the motor. This is done for quick changeout of damaged cable due to harsh environment. AB's solution is below: Changing out encoder/motor does not help.
E20
Motor Encoder State Error The motor encoder encountered an illegal transition.
• Replace the motor/encoder.
• Use shielded cables with twisted pair wires.
• Route the feedback away from potential noise sources.
• Check the system grounds.
• Verify that the unbuffered encoder signals are not subjected to EMI in the CN1 cable. Remove these signals from the CN1 cable if they are not being used.
• Verify that the motor has a high-frequency bond to the drive’s enclosure panel.
• Verify that any stage connected to the motor shaft (for example using a ball screw) has a high-frequency bond to the machine frame and the drive’s enclosure panel.
Motor power color code
Make sure that the motor POWER leads are connected properly at the drive. If not it messes up the commutation and you will get encoder faults.
Amen to that. I once spent hours troubleshooting this problem. More than once we have received cables that are marked wrong (U, V, W on wrong colors). Always go by the colors, not the labels.
How long are the cables? Can you swap motors or drives with other machines to narrow down the problem? Can you measure the encoder power at the motor plug?
Hello All, Question about an AB Ultra 3000 servo drive (with DeviceNet), perhaps someone has seen this before... On power-up, the green LED for...
1,627
We are pulling our hair out trying to figure out this issue. We have an AB*MPL-A330P-HK22AA servo motor that started randomly throwing E22 and E24...
2,580
Hello All, I am having an issue with a Ultra 3000 jumping while stopped. It seem to be intermittent. I am using RS5K to control the servo. It...
2,583
Hello everybody, I need some help. I have flying shear application and trying to upgrade drive. Here is parts I planning to use: Ultra 3000 wit...
1,449
Hello everybody, have a question, is anybody try to use serial port to control Ultra 3000 Drive, I have project where customer want to upgrade old...
2,625