Connecting to SLC through Com port on Compactlogix
When connected to a L32E via ethernet, is there a way to view a device such as a SLC connected to the Compactlogix's serial port.
PC>ETHERNET>COMPACT>SERIAL>SLC Can I view the SLC in RSlinx via the DF1 Com port associated with the Compactlogix. Any help would be great thanks!!! |
|
|
|
#2 |
|
Member
|
Yes, I certainly think so. Attach a null-modem cable between the CompactLogix and the SLC serial port, and be sure to set the port data rates and error checking for the same settings.
|
|
|
|
#3 |
|
Member
![]() Join Date: May 2006
Location: edmonton
Posts: 127
|
OK, but what would each port be set to besides baud rate, DF1 Master at the compact and DF1 Slave at the SLC???
Has anyone completed this? |
|
|
|
#4 |
|
Member
|
Leave the CompactLogix and SLC serial ports set for DF1 Full Duplex.
I tried this to be sure and it works. I was using ControlLogix, but CompactLogix will work the same way. The only change I made to ports from default was to set the ControlLogix DF1 setting to CRC error checking, to match the SLC. You can see that the SLC-5/03 is in out-of-the-box condition, with the program name DEFAULT. |
|
|
|
#5 |
|
Member
![]() Join Date: Nov 2009
Location: johor
Posts: 4
|
does this application applicable with compactlogix and micrologix?
if so what are the settings require? |
|
|
|
#6 |
|
Member
|
This will work with CompactLogix and MicroLogix exactly the same as it does with ControlLogix and SLC-500.
The settings are exactly the same as described above: Use the default DF1 Full Duplex configuration on both the CompactLogix and the MicroLogix serial ports, with the following notes: Be certain the baud rate is the same on both controllers (Default should be 19200). Be certain the Error Checking method is the same on both controllers. By default, ControlLogix and CompactLogix use BCC and the SLC/MicroLogix uses CRC. I recommend setting the CompactLogix for CRC so that they match. |
|
|
|
#7 |
|
Member
![]() Join Date: Nov 2009
Location: johor
Posts: 4
|
if that how do i write A MSG instruction in RSLOGIX500 to send data to compactlogix??
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| slc 5/05 rs232 port | eastkodakguy | LIVE PLC Questions And Answers | 8 | October 2nd, 2009 12:12 AM |
| SLC5/04 and DPS2 Port Splitter | Andy Thornton | LIVE PLC Questions And Answers | 12 | July 17th, 2009 08:41 AM |
| Connecting to an SLC 5/03 | LMDAVE | LIVE PLC Questions And Answers | 5 | June 10th, 2008 10:11 AM |
| Cellular Modem to SLC 504 via serial port | RKaighen | LIVE PLC Questions And Answers | 0 | March 14th, 2008 07:59 AM |
| RS-232 Port on SLC 5/03's / 5/04's | Dave McGlynn | LIVE PLC Questions And Answers | 9 | May 15th, 2003 08:55 PM |