Your 1756-DNB scanner is just another node on the network, and should be connected to the network trunk-line just like any other node, therefore it should not have a terminating resitor attached.
The resistors (2 only) should be at the extreme ends of the trunk-line.
You are not getting data to/from nodes up to #11 - but the numbers don't mean anything, check the physical location of devices on the network, I would hazard a guess node 12 is the first node away from the scanner, and a break in the network wiring AFTER node 12.
There's a couple of quick checks to perform to troubleshoot network cabling problems.
1. Power-down the network and measure the resistance between CAN-H and CAN-L (the signal wires). You should get 60 ohms (or slightly less if quite a few devices attached), but not less than 50 ohms. Any higher than 60 and you have a missing or bad termination resistor.
2. With the network powered-up, measure the V+ to V- voltages at the extreme ends of the network, and where the network power supply is located. The maximum allowable voltage drop is 4.75 volts in each supply line, so a V+ to V- voltage of 15.5 V is deemed to be acceptable, although I would not be happy with less than 20 V