PanelView 550 Comm problems

The other day, a SLC 500 had a 5/02 processor fail. We were using the 1747-AIC to communicate to a PanelView 550 (P/N 2711-B5A3).

I am now trying to utilize a 5/03 processor in place of the 5/02. I am using the DH 485 Comm protocol. The PanelView is telling me no nodes are found on the network. I am pretty darned sure I have all the nodes numbered correctly but I have found in the past making these sorts of asusmptions can be dangerous.

Don't be afraid to treat me like I'm stupid. These are the first A-B products I've used. I'm more of a GE kinda guy. We bought these machines very, very used and I'm just trying to keep 'em running.
  Reply With Quote
Old October 24th, 2008, 03:18 PM   #2
jshiepe
Member
United States

jshiepe is offline
 
jshiepe's Avatar
 
Join Date: Sep 2003
Location: Strongsville, OH
Posts: 227
You may need to use the PanelBuilder software to open your Panelview application and check the communication settings. In that section, you will find the node number that the Panelview expects the SLC to be, and you may also need to update those settings to tell the Panelview you are communicating with a 5/03 rather than a 5/02.

Good Luck,

Jeff
__________________
To the optimist, the glass is half-full.
To the pessimist, the glass is half-empty.
To the engineer, the glass is twice as big as it needs to be.
  Reply With Quote
Old October 24th, 2008, 10:09 PM   #3
jstolaruk
Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: SE Michigan
Posts: 2,089
You must have restored the 5/03 with the 5/02 program so just make sure the 5/03's node address is the same as the 5/02. It should be in the original program but you'll have to manually change the 5/03 to match what it was; downloading doesn't change the comm port settings IIRC.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Panelview - PC : Comm Problems mrhhassan LIVE PLC Questions And Answers 12 October 25th, 2009 02:03 AM
Panelview 550 problems DalTile LIVE PLC Questions And Answers 1 August 25th, 2006 07:26 AM
block transfers to panelview 550 bakerboy_99ca LIVE PLC Questions And Answers 1 February 15th, 2005 10:55 PM
PanelView 550 Problem Tom Jenkins LIVE PLC Questions And Answers 15 August 16th, 2004 12:42 PM
HMI to Database alarms & comm problems philjf LIVE PLC Questions And Answers 0 April 8th, 2004 09:34 AM


All times are GMT -5. The time now is 10:01 AM.


.