I have this 2nd hand machine which uses 4 of this A1SJ71AT21B to communicate between 3 A1SCPU (1 as master station and 2 as local station) and 1 A1SCPU(S1).
I have no previous experience with this network module. The only reference I got is IBNA-66478 which I got from Mitsubishi website. To my surprise, the connection differs from what the machine originally had. The original connection of the machine for SDA/RDA and SDB/RDB are the same as manual. But the twisted pair cable shield are connected to SG(L) instead of FG. Also, there is no 110ohm,1/2W resistor connected in between SDA/RDA and SDB/RDB for the first and last station. Anyone with experience on this? Last edited by ckkhin; November 16th, 2008 at 09:22 PM. |
|
|
|
#2 |
|
Member
|
Hi ckkhin,
Worked on Mitsubishi PLC's with MELSECNET network many moons ago. Ideally the shield should be connected to the FG terminal for proper screening and end resistors should also be in place to prevent reflection and errors. I have however seen this type of network work without end resistors. What is the problem with your application? I assume that the PLCs are communicating with each other? If more help needed come back and I'll see if I can disturb the codwebs more.
__________________
ROTH |
|
|
|
#3 |
|
Member
![]() Join Date: May 2007
Location: Penang
Posts: 9
|
It was communicating until I changed the connection to follow the manual.I used 2 resistors of 1W each to get 110ohm as I'm short of resources and it caused the last station datalink unit hardware faulty.
So, I replaced the datalink unit and revert to original wiring. To my dismay, the datalink unit of the last station hardware faulty again. Do you know what is the different between LG and FG for A1S61P power supply unit? The last station wiring for A1S61P is different from other station. The Earth wire is connected to FG instead of LG. To reduce down other possibility, I already clean up all the A1S38B base units and the modules of the machine. Now I am waiting for the datalink unit and already placed order for 110ohm, 1/2w resistor. Hopefully everything will is fine by following the manual exactly. |
|
|
|
#4 |
|
Member
![]() Join Date: May 2007
Location: Penang
Posts: 9
|
For your information, this control is used for Crabtree 1290.
|
|
|
|
#5 | ||
|
Member
|
Quote:
Can you specify what LED's are on, cable distance approx. between nodes and what speed network is set to. Quote:
Generally the MELSECNET is pretty straight forward, once the cabling, resistors, addressing and speed are correct then it should work. Maybe replacing the troublesome network card or switching with a healthy one may help in narrowing down the problem.
__________________
ROTH |
||
|
|
|
#6 |
|
Member
![]() Join Date: May 2007
Location: Penang
Posts: 9
|
There isn't any error LED. But when I diagnose with MELSECNET, the BWY from master station Unreceived. The 2 faulty datalink unit also gave the same outcome. Distance from master to last station less than 100m. Baud is set to 3. The 4 stations are set to 00, 01, 02 and 03. Double confirm the ohm before connecting it in (somewhere between 106-107 ohm).
Now I am connecting exactly as what shown in the manual and changed the FG to LG for power supply grounding. Also replaced with a new datalink unit. Everything is fine and hopefully it won't have any problem. Having trouble modifying 1 of the PLCs program. I'm not sure why. Is there any write protect mode dip switch for A1SCPU? It is using A1SMCA-8KE memory cassette. Do you know the website where I can find user manual for A1SCPU PLC? Thanks for helping. |
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| datalogging project, panasonic PLC (FP Win PRo)... advice? | friendlyfire | LIVE PLC Questions And Answers | 0 | May 13th, 2008 01:38 AM |
| Need Career Advice | AGENTTINFOIL | LIVE PLC Questions And Answers | 7 | April 20th, 2006 05:32 AM |
| Advice Requested | gary68 | LIVE PLC Questions And Answers | 8 | April 6th, 2006 02:22 AM |
| Offtopic:Needs some career advice !!! | Tomsci | LIVE PLC Questions And Answers | 3 | February 15th, 2006 04:15 PM |
| need advice regarding pros and cons of devicenet- | wesley szymczyk | LIVE PLC Questions And Answers | 1 | January 4th, 2006 01:57 PM |