Old January 13th, 2009, 08:34 AM   #1
parvezl
Member
India

parvezl is offline
 
Join Date: Aug 2006
Location: mumbai
Posts: 4
2-wire and 4-wire sensor wiring for analog module

Hi,

Is it possible to connect 2-wire sensor and 4-wire sensor together in an analog module of a PLC, where COM terminal is only one single. For eg, i am using twido TWD AMI 4LT module.

I need to connect 3 loop powered sensors and 1 externally 230VAC powered sensor.

Is there something wrong here in the connection ???

Regards,
Foo
Attached Images
File Type: jpg sensor connection 4LT.JPG (24.5 KB, 472 views)
  Reply With Quote
Old January 13th, 2009, 12:49 PM   #2
abdallah mohasseb194
Member
Egypt

abdallah mohasseb194 is offline
 
Join Date: Dec 2008
Location: suez
Posts: 2
4-wire sensor wiring

Am not aware about your analog card but from my previous experience in automatic controll i think you are right because all y0u need in case of non-two wire transmitter is to share the common-return between transmitter and receiver good luck
abdallah
  Reply With Quote
Old January 13th, 2009, 02:27 PM   #3
BobB
Lifetime Supporting Member
Australia

BobB is offline
 
BobB's Avatar
 
Join Date: Jun 2002
Location: Sydney
Posts: 3,643
Be extremly careful using 2 wire non-isolated sensors/transmitters into analogue cards of this type - they can interfere with each other.
YES!! I have been caught and now only use isolated sensors/transmitters.
__________________
The Old Pfhaart

  Reply With Quote
Old January 13th, 2009, 05:00 PM   #4
panic mode
Member
Canada

panic mode is offline
 
panic mode's Avatar
 
Join Date: May 2003
Location: Toronto, Canada
Posts: 1,962
bob can you elaborate please?
  Reply With Quote
Old January 13th, 2009, 05:05 PM   #5
Roy Matson
Member
Canada

Roy Matson is offline
 
Roy Matson's Avatar
 
Join Date: Apr 2004
Location: Vancouver
Posts: 463
It looks perfectly OK to me
Regards
Roy
  Reply With Quote
Old January 13th, 2009, 05:41 PM   #6
mellis
Member
United States

mellis is offline
 
Join Date: Nov 2004
Location: Cincinnati, Ohio
Posts: 656
The wiring is fine as long as all the transmitter outputs are isolated like BobB said. By isolated, I mean neither transmitter output terminal is referenced to ground. For the 4-wire transmitter the output terminals may not be referenced to the incoming power either.

High quality 2-wire instruments are isolated. It's been a while since I ran into one that wasn't. I think if I did come across one today, that not being isolated pretty much says "poor quality".

4-wire instruments are also usually isolated, but I still find ones that aren't. If I had a problem with mixed 2-wire and 4-wire instruments, I'd disconnect the 4-wire signals first to try to find the offending transmitter. "Low cost" drives both DC and AC sometimes have analog speed signals that are referenced to the incoming line. I recall one incident where a 0-10vdc speed signal was actually 90-100vdc when referenced to ground. Hooking that one up as shown would definitely let some smoke out.
  Reply With Quote
Old January 13th, 2009, 05:59 PM   #7
muusic_man
Member
United States

muusic_man is offline
 
Join Date: Nov 2008
Location: Delaware
Posts: 96
I believe either it will not work or you will cause interference. The reason I say this is the 230 VAC 4 wire transmitter you are using produces its own 24VDC and therefore has it's independent DC common. In your drawing you are using the DC common of one power supply to act as the return for a different 24VDC power supply. Please let me know how you made out with this.
  Reply With Quote
Old January 13th, 2009, 06:12 PM   #8
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,005
Quote:
Originally Posted by mellis View Post
I recall one incident where a 0-10vdc speed signal was actually 90-100vdc when referenced to ground. Hooking that one up as shown would definitely let some smoke out.
If it were me, I'd connect the three 2 wire transmitters as shown; chances are they are isolated and all will work fine.

But before connecting either output wire from the 4 wire device, I'd check each of the output wires for common mode voltage with respect to the 0v terminal on the Siemens, to see how much common mode there is. Hopefully, less than a couple volts.

I, too, have had problems like Mellis cites, with 4 wire outputs. I never trust a 4 wire output. His example has wildly excessive, damaging common mode, but other times it's 15Vdc common mode, enough to saturate the other inputs, while not destroying the input card.

Dan
  Reply With Quote
Old January 13th, 2009, 09:33 PM   #9
BobB
Lifetime Supporting Member
Australia

BobB is offline
 
BobB's Avatar
 
Join Date: Jun 2002
Location: Sydney
Posts: 3,643
Explanation
I often use 4-20ma inputs into an analogue card in swimming pool systems for reading temperature, Ph, FAC, TDS etc. Normally there is only 1 temperature input and the rest are driven, isolated outputs from a chemical controller. I normally use a loop powered head mounted RTD transmitter (also called a hockey puck transmitter).
PLC analogue cards are usually isolated from the PLC bus but the inputs are quite often not isolated from each other and have a common negative connection.
Had a job where I required 3 x 4-20ma inputs to read temperature - used hockey pucks - readings all over the place - they interfered with each other via the common negative connection.
Advice - use isolated transmitters and it does not happen - or has not happened to me anyway. It is possible to buy isolated hockey pucks by the way - my client had only run 2 wires to each transmitter - he then had to run 4 wires to each transmitter when I changed them to isolated hockey pucks - +/-24VDC and 4-20ma return. There is a big difference in price by the way but not worth the agro.
__________________
The Old Pfhaart

  Reply With Quote
Old January 14th, 2009, 10:10 AM   #10
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 823
Personally I would add an isolator for the 4 wire circuit and unless the SMPS is only about 200mA and short circuit protected I would add some fuses.

Bryan
  Reply With Quote
Old January 15th, 2009, 03:51 AM   #11
parvezl
Member
India

parvezl is offline
 
Join Date: Aug 2006
Location: mumbai
Posts: 4
The loop powered sensors are 3 nos of RTD, with 4-20 transmitters which are head mounted. the 4-wire transmitter is a Mettler Toledo M-300 conductivity transmitter.

The problem i am facing now is that, when i connect the 4-wire transmitter, all my 2-wire transmitters give max reading at 11 to 12 mA instead of 20mA.

The same configuration when connected with Mitsubishi FX2N-4AD does not cause a problem. Where all 4 commons are different for each AI. Is it because of that?

Can someone clarify?

--
Foo
  Reply With Quote
Old January 15th, 2009, 05:09 AM   #12
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 823
So either the M-300 is pulling the SMPS down or there is a ground loop problem. Ground loop problems never seem logical until you draw everything out and calculate currents and voltages. The answer is as I wrote above, add a signal isolator between the M-300 and the PLC and hopefully your problems will go away. I had similar issues with two guided radar level sensors that worked fine with only one connected but gave bad readings if both were used. Adding signal isolators fixed the problem, something like this from Status.

Bryan
  Reply With Quote
Old January 15th, 2009, 05:10 AM   #13
Ken Moore
Member
United States

Ken Moore is offline
 
Ken Moore's Avatar
 
Join Date: May 2004
Location: Upstate South Carolina
Posts: 2,325
Quote:
Mitsubishi FX2N-4AD does not cause a problem. Where all 4 commons are different for each AI
Yes, if all of your AI's were isolated you would not have the problems you are experiencing.
Fast solution (as already mentioned) would be installing a signal isolator on the 4-wire device connections.
__________________
"To give real service you must add something that cannot be bought or measured with money; and that is sincerity and integrity."
- Donald A. Adams

  Reply With Quote
Old January 15th, 2009, 02:09 PM   #14
BobB
Lifetime Supporting Member
Australia

BobB is offline
 
BobB's Avatar
 
Join Date: Jun 2002
Location: Sydney
Posts: 3,643
Read my last post - I have been caught - I no longer use non-isolated transmitters!!
__________________
The Old Pfhaart

  Reply With Quote
Old January 18th, 2009, 09:34 PM   #15
panic mode
Member
Canada

panic mode is offline
 
panic mode's Avatar
 
Join Date: May 2003
Location: Toronto, Canada
Posts: 1,962
Quote:
Originally Posted by BobB View Post
Be extremly careful using 2 wire non-isolated sensors/transmitters into analogue cards of this type - they can interfere with each other.
YES!! I have been caught and now only use isolated sensors/transmitters.
Hi Bob,

Can you please post part number of the 2-wire device that you had problem with? I think the confusion is part of possibly different naming convention. I asked for explanation of above statement since I did not understand how is it possible that two wire transmitter is not isolated (well it's not after it's installed of course, but it can be wired either as sink or source and I don't see how two-wire sensor can be cause of trouble). The problem with shared commons is normal for 3 wire and non-isolated 4-wire devices (but 2-wire...?). The explanation in second post suggest that original device was replaced with 4-wire transmitter (not 2-wire device).

Quote:
Originally Posted by BobB View Post
Explanation
...... Had a job where I required 3 x 4-20ma inputs to read temperature - used hockey pucks - readings all over the place - they interfered with each other via the common negative connection.....I changed them to isolated hockey pucks - +/-24VDC and 4-20ma return....
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 07:18 PM.


.