slc 500 Problems with serial communication

I have an SLC500 1747-L541 running OS401 and I'm having a problem with serial communication once I have completed loading a ladder to it.

RS Linx works fine with out error but once I place the unit in run mode it will not see the serial communication.

Any help would be appreciated.
  Reply With Quote
Old February 17th, 2009, 05:08 PM   #2
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,499
Perhaps your changing the serial ports configuration with the downloaded file. Compare your RSLinx's configuration with the file your downloading.
Tell us how you have RSLinx configured and post your .RSS file and someone can take a look. ( zip it first then post if you can)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old February 17th, 2009, 05:13 PM   #3
dms1808
Member
United States

dms1808 is offline
 
Join Date: Feb 2009
Location: North Carolina
Posts: 3
The interface I am using opens the ladder prior to downloading. I have matched all the parameters I can get to with an operable system. I even pulled a ladder from a known good system.

The problem started when we replaced the CPU.

Is it possible we have a newer version CPU that has closed a port down on me?
  Reply With Quote
Old February 17th, 2009, 05:19 PM   #4
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,499
Quote:
Originally Posted by dms1808 View Post
The interface I am using opens the ladder prior to downloading. I have matched all the parameters I can get to with an operable system. I even pulled a ladder from a known good system.

The problem started when we replaced the CPU.

Is it possible we have a newer version CPU that has closed a port down on me?
No, that doesn't make sence. When you say ver. do you mean a different SLC500 i.e SLC5/03 to SLC5/04 or what please explain.
Are you using the DF1 driver in RSLinx? If so after you download go back to RSLinx and click on autoconfigure.
Again if you can post a snap-shot of RSLinx and post your SLC
code.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb

Last edited by Mickey; February 17th, 2009 at 05:22 PM.
  Reply With Quote
Old February 17th, 2009, 05:57 PM   #5
dms1808
Member
United States

dms1808 is offline
 
Join Date: Feb 2009
Location: North Carolina
Posts: 3
Same systems SLC5/04. Here are some pics
Attached Images
File Type: bmp Channel config - Copy.bmp (294.9 KB, 62 views)
File Type: bmp controller - Copy.bmp (267.9 KB, 47 views)
File Type: bmp I-O config - Copy.bmp (285.2 KB, 42 views)
  Reply With Quote
Old February 17th, 2009, 06:58 PM   #6
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 11,001
When troubleshooting configuration problems, posting the actual files rather than screenshots is far more effective. I realize it's not always possible, but since you are a new Forum member (welcome !) I thought I'd mention it.

Why did you change the controller in the first place ? Was the original controller an SLC-5/04, or an SLC-5/03 ? Your answers are not clear on that.

The good news is that there's no firmware revision or hardware change that would shut down the communications port when you enter run mode.

When you download a program to an SLC family controller, the last thing the RSLogix 500 software does is check the Communications channel configurations and compare them to the current settings in RSLinx. If these are different, the software presents a warning letting you know you *may* lose communications on the current or the other channel of the controller.

It is absolutely vital that you pay attention to those messages when they appear.

The label "KF3" on your DF1 Full Duplex driver is unusual. It appears that you might have been using "DF1 to DH+" or "DF1 to DH485" pass-through communications, which requires you to select a different Device Type in your RSLinx DF1 Full Duplex driver, as well as requiring specific Status bit settings in the controller.


Do you recall "going online" with the other DH+ connected controllers while plugged into the serial port of this SLC ?

Check the configuration in RSLinx for the "known good" controller to see what the "Device Type" is. Examine the Processor Status -> Chan.1 tab in RSLogix 500 to see if any of the passthrough configuration bits are set.
  Reply With Quote
Old February 18th, 2009, 06:38 AM   #7
Archie
Member
United States

Archie is offline
 
Archie's Avatar
 
Join Date: May 2002
Location: Orangeburg, SC
Posts: 949
Does your program use an AWT instruction?

If your SLC's com port is in System Mode, the AWT will still work, but if you are online and teh AWT writes something to the port, it will knock you offline.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PanelView Plus ---> SLC L551 Ethernet Communication Issues celichi LIVE PLC Questions And Answers 11 August 28th, 2008 06:59 AM
most common problem using SLC 500 gakpapa LIVE PLC Questions And Answers 2 April 8th, 2008 01:05 AM
SLC 500/RSLogix 500 Communications kerch LIVE PLC Questions And Answers 25 October 15th, 2006 12:19 AM
A/b Slc 500 Johnny Rotten LIVE PLC Questions And Answers 11 September 28th, 2005 11:27 PM
Slc 5/05 Problems ? RADKON LIVE PLC Questions And Answers 4 August 19th, 2002 03:47 AM


All times are GMT -5. The time now is 04:44 PM.


.