Hello All,
I have S7-315-2DP w/ hardware interrupt module. Upon entering OB40 for the interrupt, I check and input and output a solenoid. Question is does this solenoid get updated at the end of OB40 scan or it gets updated at the end of OB1 scan? Thanks, |
|
|
|
#2 |
|
Supporting Member
![]() Join Date: Nov 2006
Location: UK
Posts: 4,540
|
End of OB1. If you want the output to update immediately, use the move QBx to PQBx method inside OB40
|
|
![]() |