hour counter instruction (rslogix 500
hi guys, i would like to put an running hour counter in the program of a ml1200 plc to be viewed on a hmi, but i am not to sure what instruction to use has anyone done this before?all
the best stu
Old April 24th, 2009, 08:13 AM   #2
bernie_carlton
United States
bernie_carlton is offline
bernie_carlton's Avatar
Have a contact representing the ON condition that you wish to time enable the input of an RTO timer. Timebase 1 second, Preset of 3600.
When it's done (DN) increment a Long type word and reset the timer. Then display the Long.
__________________
Controlling outputs is the PLC's way of getting its inputs to change.
www.thePLCguy.com
Old April 24th, 2009, 09:01 AM   #3
stu
England
stu is offline
stu's Avatar
hi bernie
thanks for that, what do you mean by increment a Long type word ? i am to to sure about this bit.
thank for you help
stu
Old April 24th, 2009, 09:10 AM   #4
jimbo3123
United States
jimbo3123 is offline
Quote:
Originally Posted by stu View Post
hi bernie
thank for you help
stu
The micrologix doesn't have a long (or dint) data type.
You can probably get away with using an integer for your hour accumulator. I typically add logic to roll-over the accumulator when it gets near its maximum value of 32767.
With a maximum of 32767 hours, your meter will roll-over with 3.7 years of continuous usage.
If you need a longer elapsed time record, you will need to use more than one integer.
For example, your timer would count up to 3600 seconds (1 hour), then increment an integer N7:10 (hours). When that integer reached 10,000, you would increment a second integer N7:11 (hours x 10,000) and set the N7:10 to 0.
Old April 24th, 2009, 05:49 PM   #5
TConnolly
United States
TConnolly is offline
TConnolly's Avatar
The op is using an ML1200, which does support a Long data type. Use an L file.
//timer
XIC Running RTO T4:0 1 3600 0
//hour counter
XIC T4:0/dn bst Add L9:0 1 L9:0 nxt RES T4:0 bnd
You could also use a preset of 36 seconds and count hudredths of hours instead.
A long will count to 2,147,483,547.
__________________
True craftsmanship is only one more power tool away.
That's the beauty of processors, they don't have emotions they just run code - The PLC Kid.
Old April 27th, 2009, 01:07 AM   #6
stu
England
stu is offline
stu's Avatar
[[/ladder]
Quote:
//timer
//hour counter
Hi Alaric
thanks for that, i am still trying to get to grips with programming can you put in idiots terms please? what does the nxt mean? and do i use the L9:0 as the display tag? if i would like minutes to i do the same formula. all the best stu
Old April 27th, 2009, 04:38 AM   #7
Kidblue
England
Kidblue is offline
Kidblue's Avatar
Hi Stu,
You can copy the syntax that a lot of the guys post here straight into the ladder editor of Logix500 (and others)
[Rung 0000] XIC B3:0/0 RTO T4:0 1.0 3600 0
[Rung 0001] XIC T4:0/DN BST ADD 1 L9:0 L9:0 NXB RES T4:0 BND
Just double-click the left of the rung until the cursor appears and paste the above into it (without the words in square brackets)...
Just replace B3/0 with your relevant input contact as the 'Motor Run' signal.
Hope this helps!
Rob
__________________
Rob Howdle
.........For the Boys in Royal Blue !!
Old April 27th, 2009, 10:03 AM   #8
stu
England
stu is offline
stu's Avatar
hi what if i wanted to reset the counter on the hmi (display)how would i go about that, if i put a -(res)- that only resets the timer /counter?
Old April 27th, 2009, 10:09 AM   #9
bernie_carlton
United States
At the same time that your reset the timer also CLR the Long data.
__________________
www.thePLCguy.com
Old April 27th, 2009, 10:12 AM   #10
Controls_Engineer79
Canada
Controls_Engineer79 is offline
Controls_Engineer79's Avatar
well do you want it to reset automaticly once it reaches a set value?? if so then i would use a compairson instruction and a move instruction to move a value of Zero into your display address once it reaches the value you want to reset at, if you want it to be manualy reset then have the move triggered by a Bit from a pushbutton on your HMI
__________________
Cuda Automation and GC conveyors -for all your material HAN-DLI-NG needs!
Old April 27th, 2009, 10:31 AM   #11
stu
England
stu is offline
stu's Avatar
what i want to do is a manual reset, if i used a = instruction and moved it to the screen ( XIC EQU N7:0 3600 MOV 0 N7:1 ) would that work?
thanks for your help.
Old April 27th, 2009, 10:39 AM   #12
TConnolly
United States
TConnolly's Avatar
Stu,
If you are doing minutes then still use the L word to count hours using a 3600 second retentive timer and compute the elapsed minutes for display. Minutes = T4:0.ACC/60 Use two separate adjacent display fields on the HMI screen, one displays hours, the other minutes, with a static : between them. Right justify the hours display, make sure you include enough digits, and configure the minute display for two digits with a leading 0 so that you have a HHHHHH:MM format.
__________________
Old April 27th, 2009, 10:58 AM   #13
stu
England
stu is offline
stu's Avatar
hi yes i was going to use two displays, but i am trying to put a button on the hmi to zero the displays?
Old April 27th, 2009, 11:04 AM   #14
Roy Matson
Canada
Roy Matson is offline
Roy Matson's Avatar
I have a related question for RSLogix5000 with Structured Text add on.
I tried making hour counters, they worked fine but would reset to zero if I downloaded a configuration change.
Is there somewhere in the PLC memory that is not over-written and how do I address that?
My PLC is 1756L61
Roy
Old April 27th, 2009, 11:04 AM   #15
TConnolly
United States
TConnolly's Avatar
XIC pushbutton BST CLR L9:0 NXB RES T4:0 BND
__________________
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
RSLogix 500 & SLC 500 bga6418 LIVE PLC Questions And Answers 10 March 30th, 2016 08:21 AM
RSlinx Lite and RSLogix 500 Starter... FREE geniusintraining LIVE PLC Questions And Answers 21 February 24th, 2012 05:11 PM
RSLogix 500 - How to write to more than one output card with a single instruction? Warren Boswell LIVE PLC Questions And Answers 4 March 26th, 2008 08:03 AM
RSLogix 500 and Standalone Security Server pimpim32 LIVE PLC Questions And Answers 4 August 23rd, 2007 11:03 AM
Instruction manuals for AB RSLogix 500 and Siemens S7 dbonniwell LIVE PLC Questions And Answers 5 May 14th, 2005 03:41 PM