Old May 26th, 2009, 03:57 PM   #1
jimmycooker
Member
Ireland

jimmycooker is offline
 
Join Date: Sep 2008
Location: Cork
Posts: 65
Contactors and PLC 24VDC

Hi,

Just wondering if anyone can tell me what kind of signal I need for this contactor.

http://www.tlc-direct.co.uk/Products/HGES220.html

It's 24VDC, just wondering about the mAmp rating, the 24VDC PWR OUT and VAC NEUT don't energise it when connected up (is the VAC NEUT ok to complete the circuit?)

Total newbie, just trying to get my head wiring up some AB input / output cards and bought this contactor to make things a bit more interesting!

Thanks,
James.
  Reply With Quote
Old May 26th, 2009, 04:09 PM   #2
Kidblue
Lifetime Supporting Member
England

Kidblue is offline
 
Kidblue's Avatar
 
Join Date: May 2003
Location: Worcester
Posts: 611
You have a 230VAC coil 2 pole contactor (as stated - typically used in consumer units).

Not sure if i should advise at all based on the little knowledge you sseem to have! (No offence - i know we all have to start somewhere!!).

You need to give us more info on the PLC hardware you are trying to configure...manufacturer, type, part no. etc.

The terminals you describe sound a little like an SLC power supply terminals but can't be sure. If you had a RELAY output module/card you could then switch 230VAC to the coil of your new contactor - but like i said above, it would help us to help you if we had more info!

Hope this helps (a little)!

Rob
__________________
Rob Howdle

.........For the Boys in Royal Blue !!
  Reply With Quote
Old May 26th, 2009, 04:21 PM   #3
jimmycooker
Member
Ireland

jimmycooker is offline
 
Join Date: Sep 2008
Location: Cork
Posts: 65
Ha ha, a little bit of info can be very dangerous!

I have an 1746-P2 PSU, SLC 5/03 CPU, DC Sink Input & Output Cards (and a fe few others0 in front of me which i bought to mess around with, i'm a process engineer but want to get into automation as I find it interesting.

I'm basically trying to write a simple program and wire up a switch to an input & a contactor to an output. If I can get this far i'll be able to focus a bit more on the ladder logic side of things and maybe use the PLC for zoning my heating system at home or something.

I bough a contactor so i could wire up a lamp or something, it's encouraging to see things turning on and off!

I'm trying to get the contactor to energise directly from the PSU by connecting two of it's poles to the 24VDC & VAC NEUT terminals on the PSU. From looking at this,

http://www.eod.gvsu.edu/~jackh/books...plc_wiring.pdf

it appears to me that the input card is acting as a switch? Therefore I just wanted to energise the contactor to make sure it was suitable / possible running from the PLC PSU without anything in between....
  Reply With Quote
Old May 26th, 2009, 04:32 PM   #4
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,391
STOP. If you are trying to use 24VDC with a VAC neut to pull in a 240V contactor coil. Then you have no idea what you are doing and are going to kill yourself or worse someone else. GET SOME HELP.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old May 26th, 2009, 04:37 PM   #5
mellis
Member
United States

mellis is offline
 
Join Date: Nov 2004
Location: Cincinnati, Ohio
Posts: 656
The problem is that unless you gave a link to the wrong part, your contactor requires 230vac (240v coil) to pull in the coil! Hooking it up to 24vdc isn't going to work.

You can use a small interposing relay with a 24vdc coil to pull in the contactor with 230vac. See figure 18 in the Jacks book.

Or there may be a different model contactor available with a 24vdc coil. However, the extra 24vdc output on the SLC power supply is VERY limited and probably couldn't drive it. You probably need a separate 24vdc power supply.

Oh, if you want to use the extra 24vdc output from the SLC power supply for something else (like the input card), the proper terminals are: 24VDC PWR OUT and 24VDC PWR COM. As others have pointed out, using the VAC NEUT is bad. Lucky you didn't let the smoke out or worse.

And for the record, I agree with them... You're sounding like an accident statistic about to happen. Hope things don't get TOO interesting.

Last edited by mellis; May 26th, 2009 at 04:47 PM. Reason: 2nd thoughts
  Reply With Quote
Old May 26th, 2009, 04:39 PM   #6
bernie_carlton
Lifetime Supporting Member + Moderator
United States

bernie_carlton is offline
 
bernie_carlton's Avatar
 
Join Date: Apr 2002
Location: Yakima, Washington
Posts: 5,316
Look again at the contactor whose link you posted. Its coil voltage is not 24 volts DC (as available from the PSU) its 240 volts and that's probably AC.

If you are set on using this unit you will have to have a source of 240 VAC.

And the 'VAC neutral' is not the common side of the 24 volt DC supply. The 'PWR OUT COM' is the common side.
__________________
Controlling outputs is the PLC's way of getting its inputs to change.

www.thePLCguy.com
  Reply With Quote
Old May 26th, 2009, 04:46 PM   #7
jimmycooker
Member
Ireland

jimmycooker is offline
 
Join Date: Sep 2008
Location: Cork
Posts: 65
Mellis / Bernie,

Thanks for your response, that explains that...it's just that this datasheet mentioned 24VDC on page 4.30

http://download.hager.com/hagergroup...larDevices.pdf

Didn'c click that there would be a contactor using the same voltage on the coil as the load, that might seem silly as i'm sure there are other factors to consider.

Thanks for telling me the PWR OUT COM is the common side too, I thought I had it wired as instructed.

Thanks again lads, this really is an excellent forum.
  Reply With Quote
Old May 26th, 2009, 04:48 PM   #8
jimmycooker
Member
Ireland

jimmycooker is offline
 
Join Date: Sep 2008
Location: Cork
Posts: 65
Could either of you give me an example of a relay / contactor i could use directly from the output to switch a small domestic central heating pump, does this exsit? Or do i need to use a relay and contactor?
  Reply With Quote
Old May 26th, 2009, 05:02 PM   #9
mellis
Member
United States

mellis is offline
 
Join Date: Nov 2004
Location: Cincinnati, Ohio
Posts: 656
In the catalog you linked, I couldn't find what you wanted. All the units on page 4.30 that say 24V control were 24vac when I checked the spec sheet for that model. I didn't spend a lot of time at it, just checked those models.

The heat pump in my house is on two 30A breakers. One for the pump and one for the fan. I suggest you avoid taking on such a heavy load to experiment with. A wiring error in that ciruit is not going to be forgiving. I think a 24vdc light would be a LOT safer.
  Reply With Quote
Old May 26th, 2009, 09:34 PM   #10
leitmotif
Member
United States

leitmotif is offline
 
Join Date: Nov 2004
Location: Seattle Wa. USA
Posts: 3,679
Jimmy - from having been in your position I can safely say you are clearly in over your head.
I am an electrician so I tried to learn PLC at home - I decided that I was clear over my head and had a total ignoramous for an instructor.

You need to get a qualified instructor - just like I did. So I went to a night school to learn about PLC. I recommend it highly. Otherwise unless you got lots of money and are willing to blow stuff up and zap or kill yourself or burn the house down you can try learning this at home.

Also get yourself a good class on basic electricity, basic motor control. If you keep fooling around with this stuff you are gonna tear up expensive equipment like a heat pump

Oh yes welcome aboard and have fun learning. PLCs are actually a lot of fun AFTER you pretty much know what you are doing.
Dan Bentler

Last edited by leitmotif; May 26th, 2009 at 10:16 PM.
  Reply With Quote
Old May 26th, 2009, 09:58 PM   #11
Viks
Member
New Zealand

Viks is offline
 
Viks's Avatar
 
Join Date: Jun 2008
Location: Hamilton
Posts: 136
I agree with Dan's suggestion.You must have heard that electricity is dangerous and especially when you dont have enough knowledge of it. The point is,if you do it wrong,things will go wrong unpredicted. It safe to learn the basics first so you are at least able to predict what is going to happen to the load when the circuit is energized. Different components have different voltage and current rating/types. Its better to view a product datasheet/catalogue before you purchase anything so you can select the product which suits your application. Something like this should be helpfull. http://static.schneider-electric.us/digest/17418.pdf

Look at pages 2 & 23 for the various types of contactors and relays.

Good luck,
__________________
Vikash Kumar
  Reply With Quote
Old May 27th, 2009, 11:28 AM   #12
Controls_Engineer79
Member
Canada

Controls_Engineer79 is offline
 
Controls_Engineer79's Avatar
 
Join Date: Mar 2009
Location: oakville, ontario
Posts: 88
Jimmy I'm going to have to agree with what everyone else here has said.
But i will tell you this much when it comes to motor contactors you have to know the following info to size it properly

What is the voltage for the contactor COIL?: usally 24VDC or 120-240VAC or 12VDC are 3 of the most common ones. This is NOT the voltage thats going to turn on ur pump its just the voltage to pull in the plunger coil of the contactor.

What is the current load of the contactor coil?: this is how many amps you need your power supply to provide to the coil. this depends on the size of the contactor itself - but typicaly for contactors that are rated for 1-5HP motors your looking at about 200mA (0.2A)

What are the HP, voltage and current rating for the motor your trying to start?: These can be anything from 240VAC single phase to 460-575VAC 3 phase, heck theres even DC motors but you don't see them to often.

Your contactor has to be matched with those 3 items, which are usally found on the motor nameplate

Fuseing and overloads?: to size your overloads for your contactor you have to look at the FLA (full load amps) rating on the motor.

small motors in the 1-5 HP range typicaly all use the same size contactor the only items that would change would be the size of your fusing and your overloads which would be based on the FLA rating of that particular motor.

But again as the other guys have said - i think all of thise falls into the "don't try this at home catagory" for newbies - - - powering up a LED pilot light is alot more forgiving then powering up a 575V 5 HP motor :-p
__________________
Cuda Automation and GC conveyors -for all your material HAN-DLI-NG needs!
  Reply With Quote
Old May 27th, 2009, 11:43 AM   #13
rwy34ils
Member
Canada

rwy34ils is offline
 
Join Date: Mar 2009
Location: Edmonton, Alberta
Posts: 73
I would suggest buying a small 12 volt DC PLC (try Ebay)and then play around with that to your heart's content to get familiar with PLCs and programming, etc. Can't cause too much damage with 12 volts!
  Reply With Quote
Old May 27th, 2009, 11:47 AM   #14
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,391
Quote:
Originally Posted by rwy34ils View Post
I would suggest buying a small 12 volt DC PLC (try Ebay)and then play around with that to your heart's content to get familiar with PLCs and programming, etc. Can't cause too much damage with 12 volts!
My car battery will put out over 500 amps !! Damage??
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old May 27th, 2009, 12:14 PM   #15
Controls_Engineer79
Member
Canada

Controls_Engineer79 is offline
 
Controls_Engineer79's Avatar
 
Join Date: Mar 2009
Location: oakville, ontario
Posts: 88
lol hummmm mickey i dono - how bout you stick your tongue on the terminals like people do with a 9V battery lol if anything else ti should be entertaining for anyone else near by ;-)
__________________
Cuda Automation and GC conveyors -for all your material HAN-DLI-NG needs!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PLC Fusing Bolt LIVE PLC Questions And Answers 11 February 14th, 2008 01:08 PM
Hard wiring the PLC Doug Hylton LIVE PLC Questions And Answers 46 October 23rd, 2007 12:21 PM
Plc control of WYE/Delta motor? timbo4255 LIVE PLC Questions And Answers 14 May 31st, 2006 02:42 PM
Quick question about PLC testing Edgar LIVE PLC Questions And Answers 38 December 30th, 2004 12:26 PM
comparison between plc and conventional control joel LIVE PLC Questions And Answers 8 August 5th, 2002 09:08 AM


All times are GMT -5. The time now is 06:24 AM.


.