Hi everybody,

I would like to use a Panel view HMI with a S7 314. We would like to do that to reduce our spare part inventory.
What communication protocol do I use and how do I tie in the Panel view Project in to the PLC program.

I hope somebody can help me with that an I appreciate every idea I can get.

Thanks
Andy
  Reply With Quote
Old June 30th, 2009, 01:43 PM   #2
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 7,585
What protocol does the Panelview support? Post the complete catalog number.

What protocol does the S7 314 support? I'm not a S7 guy so others will have to check in here.

They both must support the same protocol.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old June 30th, 2009, 02:38 PM   #3
andreas
Member
United States

andreas is offline
 
Join Date: Jun 2009
Location: USA
Posts: 2
They both support
EtherNet and
Profibus DP
But I don't know how to assign the Variable to the PLC from the Panelview Project.

Thanks

Andreas
  Reply With Quote
Old June 30th, 2009, 07:38 PM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 8,712
PanelView Plus terminals can connect to Siemens S7-300 series controllers using an RS-232 to MPI converter.

To my knowledge the PV+ cannot use the USB/MPI converter.

The communication driver is KepServer Enterprise. You can find Siemens addressing help in the KepServer documentation.

In my very limited experience, the MPI interface is more straightforward and less expensive than using Profibus DP.
__________________
"Intelligence is the capacity to know what we are doing and instinct is just instinct. The results are about the same."
  Reply With Quote
Old June 30th, 2009, 09:44 PM   #5
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is online now
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 3,467
What are the full part numbers for both... if you have a Ethernet on both then you would just connect it that way and you would not need any cables (other then a Cat5).... not that I think you buying cables is such a bad idea

Ken or someone else would have to help with the PV+ and the drivers but I would think that KepServer would have them.

Assuming that you would just load them to the PV??
__________________
www.PLCTrainer.net

PLC Trainers, Communication Cables and Automation Supplies, Allen Bradley ~ Siemens ... YouTube PLC help videos.. http://www.ind-concepts.com/Support_and_Downloads.htm
  Reply With Quote
Old June 30th, 2009, 11:11 PM   #6
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 8,712
I re-checked the KepServer Enterprise driver list. I only have a small amount of experience with the Serial -> MPI converter and PV+, and can't offer advice on Siemens Ethernet.

The listed drivers are:

Siemens S5
Siemens S7-MPI
Siemens S7-200
Siemens TCP/IP Ethernet

Again, documentation is part of the KepServer Help files. It should be the same as this driver from Kepware:

http://www.kepware.com/Spec_Sheets/S...PEthernet.html

To load a KepServer Enterprise driver into a PV+ terminal, you perform a firmware upgrade with the driver included. I only ever load one driver of any given type (serial or ethernet or expansion card).
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
AB panelView Plus MMI with Siemens S7 314 iknowsomeplc LIVE PLC Questions And Answers 0 November 18th, 2003 12:52 AM


All times are GMT -5. The time now is 07:42 AM.


.