How to go to the terminal config screen on PanelView Plus 600
Hi, im trying to go to the config mode on PanelView Plus 600 series A rev. B, but have no luck. Somebody downloaded his own application with no go to config screen button in it, so when it powers up application automatically runs, and u cant go to config screen.
Tried to establish communication via Ethernet, but dont know its ip address.. ![]() Tried to establish communication via RS-232 printer port using NC-13 cable, RSLinx doesnt see it or doesnt want to see it.. ![]() Tried to update firmware with a COMPACT FLASH UPDATE CARD, during the update process error appears "not enough space, please remove current applications" ![]() ![]() ![]() Does anybody know how to solve it????!!!! ![]() ![]() ![]() ![]() |
![]() |
![]() |
#2 |
Lifetime Supporting Member
![]() ![]() Join Date: Sep 2006
Location: Alabama
Posts: 199
|
Plug a keyboard into the USB port and press the Ctrl, Shift, Alt, and Windows key simultaneously.
|
![]() |
![]() |
#3 |
Member
|
Touch Only Screens: Press and hold the box until the unit boots to config mode.
Keypad Only Screens: Hold the F1 key until the unit boots to config mode. |
![]() |
![]() |
#4 |
Lifetime Supporting Member
|
If the method offered by smoke does not work, you can download a utility from ab.com that you can put on a memory card and it will force the PV to the config screen on power up.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants. |
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Feb 2009
Location: Baltimore
Posts: 9
|
There is no white box to press and hold during boot process, i think because of the firmware ( too old)
Pluged in a keyboard as SMOKE adviced, and got access to PanelView Transfer Utility, and there were 2 ways to download serial and Ethernet, tried serial, had no luck, seems like this PV hates serial type connection ![]() Tried ethernet, communication established but only with Firware Upgrade Utility, finally again "not enough space message" appeared. File Download and Upload utility (part of RSView Studio) that what i would use to delete application doesnt communicate with PV i dont knw why... RSLinx doesnt see PV when Ethernet driver is running. So i decided to do next: 1. find a smaller firmware that can be downloaded to PV without not enough space message. 2. find a utility on ab.com to force the PV to go to config screen |
![]() |
![]() |
#6 |
Member
![]() ![]() Join Date: Aug 2006
Location: south carolina
Posts: 76
|
As it boots you should see a little white box pop up on the lower left hand corner of the screen. When this pops up just touch it and it should go into config mode.
__________________
PROGRAMMABLE WHAT?!? |
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Feb 2009
Location: Baltimore
Posts: 9
|
There is no white box to press and hold during boot process, i think because of the firmware ( too old)
|
![]() |
![]() |
#8 |
Member
![]() ![]() Join Date: Feb 2009
Location: Baltimore
Posts: 9
|
Can somebody send me that application to force PV+ to go to config screen? I cant find it on ab.com...
![]() ![]() ![]() |
![]() |
![]() |
#9 |
Member
![]() ![]() Join Date: Aug 2006
Location: south carolina
Posts: 76
|
This should help
Problem: If an application has accidentally been set to autorun with no means of exiting the project, it will continue to run that application even on reboot of the terminal.
Solution: The following utility will bring up the RSView ME Configuration screen where the user can set ME to disable the project autorun option. Steps: Method
File is attached..
__________________
PROGRAMMABLE WHAT?!? |
![]() |
![]() |
#10 |
Lifetime Supporting Member + Moderator
|
And here's the same application for the PV700 - 1500 sizes. It uses a different file but work it the same way.
|
![]() |
![]() |
#11 |
Member
|
Another way is to add a shutdown button (one of the menu items in RSView Studio). I add a popup on the first screen that opens. This allows me to go back to a previous revision without downloading.
Roy |
![]() |
![]() |
#12 |
Lifetime Supporting Member
|
|
![]() |
![]() |
#13 |
Member
![]() ![]() Join Date: Aug 2006
Location: south carolina
Posts: 76
|
Was wondering if everything was OK with this issue?
__________________
PROGRAMMABLE WHAT?!? |
![]() |
![]() |
#14 |
Member
![]() ![]() Join Date: Feb 2009
Location: Baltimore
Posts: 9
|
Everyone thanks for replies, and HUUUGEEE thanks goes to daba and DUNK. That utility really saved my time and nerves!!!! I did everethn as u described in ur post
![]() |
![]() |
![]() |
#15 |
Lifetime Supporting Member + Moderator
|
And just a quick note that the AUTORUN.EXE file you create as in DUNKs post also works from a USB memory stick, as well as from a CF card, same procedure.
|
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
how to access panelview plus config screen | GotQuestions | LIVE PLC Questions And Answers | 6 | August 29th, 2012 07:51 PM |
Panelview Config Screen (Topic 1 of 3) | akreel | LIVE PLC Questions And Answers | 14 | November 17th, 2011 05:31 PM |
Panelview 1400 touch screen terminal config mode | Proplas | LIVE PLC Questions And Answers | 4 | August 14th, 2011 11:28 PM |
Panelview Plus 600 reading from SLC5/03 via NET-ENI story... | Jawmunji | LIVE PLC Questions And Answers | 4 | June 20th, 2007 11:30 AM |
Panelview Plus 600 Config Problem | Meeks | LIVE PLC Questions And Answers | 8 | January 23rd, 2007 12:58 AM |