Suitable PLC module for totalizer signal
flyers
Sep 2006
Amk
295
Hi guys,
We've a client that need to monitor the totalizer signal in the PLC (HMI). According to the client, the output is frequency/pulse. Does anyone know what is the suitable input module to receive this kind of signal?
The client has 2 system, one system is using MLX 1500, another is SLC 500.
I guess it's 1769-IQ16F for MLX 1500 system, am I right?
depends on the frequency or duration of the pulse. not sure what hz input the mlx1500 or slc500 can handle with their normal inputs. what do they want to totalise? if it exceeds a specified hz for ur normal inputs a high speed counter card might be needed
Can we use high speed input module instead of high speed counter? What is the difference?
High speed input has 16 points/module, while high speed counter only supports 1 channel/module, right?
Answer these comments and we might be able to help you...
How often are your pulses coming?
How long are your pulses?
Hi, I had a client upgraded their system to use a set of redundant PLC system with GE PLC CPE400, and a Citect 8.0 (2016) SCADA to get data with...
1,446
Hi, I frequently demonstrate automation product (that we make) to various customers. The system uses an AB7007 Anybus gateway that connects to...
5,286
we have plcs in our plant as given : Control logix 1756, Controller name : Logix 5571 HMI : Panelview Plus 1000 please suggest all required soft...
1,913
Hi, Is there any cheap PLC (less than 100 USD) that has 4 digital inputs/outputs (not relays), RS 485 communication, ethernet port (if possible)...
19
5,644
Can anyone recommend 12V PLC , to be used in a car. That is robust and can handle variations in normal car voltage? Bit on a budget side to :)
25
9,257