CPU Fault SLC 5/03
techimnot
Jan 2008
TN
17
We are running an AB SLC 5/03. The machine will run for awhile and then stops due to a CPU Fault. I can usually clear it right away with the RSLogix, but it eventually comes back. When I "go to error" from the drop down the error message reads
"Remote power failure of an expansion I/O occurred"
Would this be coming from an I/O card, or as I suspect, the power supply or CPU itself? Any help is appreciated.
From AB if it is a 21h error
Error code 21H indicates that one of the modules in the slc 500 chassis is faulting.
The exact description is "A remote power failure of an expansion I/O chassis has occurred.
The customer should download a blank program and force the program into run mode.
Adding one module at a time to the I/O and placing the program in run mode.
I would say its a card... but just a guess, the above would take a long time to figure out in your case, I would power down and re-seat all of them just to make sure its not a bad connection
The controller is detecting a power failure in an extended I/O chassis.
The main chassis in which the CPU resides can be cabled to up to two additional chassis. It's the power supply in one of those remote chassis that's failing.
It could be a bad power supply, but it's more likely a loose power connection.
There is no remote chasis. What I have is the power supply, CPU, Triac AC output, DC source output, 115v input, and a DC sink input. And empty slots.
Would these cards be directly replaceable with a like card. Or would I need to get into the configuration. Been about ten years since I've done this.
Any help GREATLY appreciated.
OK, then the SLC is mis-identifying a major backplane failure.
I've seen this caused by spikes that come in from inductive loads (usually relays, sometimes ordinary AC outputs) and from damaged backplanes. There's an active chip on the backplane that can get damaged and fail progressively. It's not common, but it happens.
Another cause can be contamination on the PC board of the backplane bus itself, or in the connector that would plug into an expansion chassis.
The last two most common things are a failing power supply or a failing CPU.
It is unlikely to be a failing I/O module. The SLC can usually identify a failing I/O module by slot number, and if it can't identify the slot number it blames the last configured slot. But an individual module failure shouldn't be misinterpreted as a chassis failure. I can't say its impossible, but I have not seen it.
Thanks Ken and Genius. It is a 21h error and I will take your facts and ideas with me to work later. I will clean up the slots and re-seat the cards again. I have a used power supply on the shelf and will start there. Also have another 5/03 CPU. Hopefully won't have to go there. Will repost after applying your comments and suggestions.
Thanks,
Jim
Success!
OK, cleaned up the 7-slot(dusty), faulted--replaced Power Supply, had a dark almost burned area on a board, no joy. Replaced the 5/03 and have been running for 30 hours. I believe it's reasonably safe to say that was it. Thanks for all the help. Next up, MicroLogix 1000, but that's a new thread later today. Thanks again!:p
hello at work we have a machine controlled with an SLC 500 fixed, model 1747-l30c at fault, i plan to migrate to a micrologix controller. I'm...
3,010
Hello everyone, I got called down to a plant to service a powdered metal press. It has an SLC 500 5/02 CPU that was faulted for the code 0002h...
1,796
Hi, New guy here. We have older Allen Bradley SLC 150s in our six Automated mini-load supply units. One unit tripped a CPU fault, and will not...
5,130
Hi, I have a CPU Fault on my AB SLC500, although i can clear the fault, but when i do a test run, the fault came back. I'm not a PLC guy, and i...
2,029
I'm new to these boards and was wondering if someone can shed some light on my problem, Started up our Jensen cleaning machine and only half of it...
6,646