Question 1756-IF16 Scaling Issue

Hello Friends,

I am using 1756-IF16 modules in a chassis with CNBR module to communicate with L63 CPU.
I did my channel configuration for 4-20mA for Float Data-Single Ended Mode - No Alarm.

My channel scaling is 0 to 160 DegC. I can read current scaled value as 30 DegC. But when I change this scaling range to 0 to 100 or 0 to 500 or anything other than 0 to 160, the scaled value 30 DegC is never changing. This is the case for all channels.

I tried to recycle the power for this rack, but same problem persists.

Could any one help me out here?
I appreciate all your help in advance!

Best Regards,

Pramod
  Reply With Quote
Old November 3rd, 2009, 01:30 PM   #2
Doylen
Member
United States

Doylen is offline
 
Doylen's Avatar
 
Join Date: Dec 2007
Location: Virginia
Posts: 39
I had same problem with IF8 card, so it may or may not help.

*Make sure the property setting on IF16 card w/ "disable Keying"
*.InRawMax for Ctrlogix 5000 software scaling should be 30800.
*In your case, .InEUMax should be 160.
Make sure .InstructFault is 0. If 1 is found, change to 0 for reset.
On Function Block programming, make sure to have alarm setup to take faults and reset it.
I hope it helped...
__________________
Doylen from Virginia
Does your supervisor knows you're helping others not your company?
  Reply With Quote
Old November 3rd, 2009, 11:42 PM   #3
halburgepramod
Member
India

halburgepramod is offline
 
Join Date: Jun 2005
Posts: 54
Question 1756-IF16 Scaling Problem

Hello Doylen,
Thanks for your reply.

For scaling i have written PLC program as below:
IF INH_AI[0].AI_CONFIG_REQUEST
THEN RIO_01:1:C.Ch0Config.HighEngineering := INH_AI[0].AI_HI_SCALE;

RIO_01:1:C.Ch0Config.LowEngineering := INH_AI[0].AI_LOW_SCALE;
end_if;

IF INH_AI[0].AI_CONFIG_REQUEST
then
msg(RIO_01_S1_ModConfig_MSG);
end_if;

By this logic, I get new values upadated at 1756-IF16 module's properties-> Configuration tab -> High Engg and Low Engg.
Anyhow the Scaled value remains unchanged.

Best Regards,
Pramod
  Reply With Quote
Old November 4th, 2009, 07:21 AM   #4
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 2,872
The scaling parameters are contained in the ":C" tag for the module, and are only ever written to the module once, when the controller makes its "connection" to the module (i.e. at power-up).

Therafter, any online changes to the data in the :C tag will not cause the module to be reconfigured.

If you must change channel scaling online, then you will need to use the Configuration tab in the module's Properties dialog box, remembering to click on "Apply" when done. This will cause the ":C" tag to be re-transmitted to the module, and the changes will be permanent.

If you want you can change the parameters offline, then download the whole program again to the controller, then the new values will be transmitted to the module, and the channel scaling will perform as expected.

If you need to change parameters programmatically (i.e. with program code), then you will need to set your parameters, then execute a special CIP "Module Reconfiguration" message to the module, which has the same effect as hitting "Apply in the configuration dialog.
  Reply With Quote
Old November 4th, 2009, 07:26 AM   #5
Oakley
Member
United States

Oakley is offline
 
Oakley's Avatar
 
Join Date: Oct 2004
Posts: 1,083
Or if you are really desiring to rescale on the fly, set the card for maximum resolution and scale the value in code.

You could use an AOI to create a SCP instruction to do this.
__________________
Artificial intelligence never overcomes natural stupidity.
  Reply With Quote
Old November 5th, 2009, 08:31 AM   #6
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 2,872
Quote:
Originally Posted by Oakley View Post
Or if you are really desiring to rescale on the fly, set the card for maximum resolution and scale the value in code.

You could use an AOI to create a SCP instruction to do this.
Whilst I agree with this idea in principle, I believe it dramatically detracts from one of the best "features" of the 1756 Analog modules, that everything is (or can be) done inside the module, and everything else you do, (i.e. Process Alarms, Rate of Change Alarm), is specified in Engineering Units, and appears in the module tag as engineering units.

By doing what you suggest as an AOI, then all of the module's configuration parameters would have to be up-scaled, and the numbers appearing in the module's tag would be pretty meaningless without a dig into the AOI and its parameters. Anybody taking a casual look at the module tag would have a harder job understanding what is going on.

For clarity, I suggest the module is used as designed, then it will be a familiar scenario for anyone who has worked with them before. The MSG instruction for module reconfiguration would be transparently documentable, enabling all to see what is being attempted.

OP's code for reconfiguration looks as correct as i can tell.

halburgepramod are you monitoring the MSG tag to see if it is .DN ?

Last edited by daba; November 5th, 2009 at 08:37 AM.
  Reply With Quote
Old November 5th, 2009, 11:54 AM   #7
Oakley
Member
United States

Oakley is offline
 
Oakley's Avatar
 
Join Date: Oct 2004
Posts: 1,083
Being that the original poster did not specify what they were doing, I was offering another potential solution.

But I do agree that the module has much more to offer.
__________________
Artificial intelligence never overcomes natural stupidity.
  Reply With Quote
Old November 6th, 2009, 06:01 AM   #8
halburgepramod
Member
India

halburgepramod is offline
 
Join Date: Jun 2005
Posts: 54
IF-16 Scaling

Hello Friends,

Actaully the logic is to scale the AI channel from HMI.

I missed to give correct connection of IF-16 module in the network for the MSG instruction for Module Reconfigure. Correcting this the scaling is working fine.

Thanks all!
  Reply With Quote
Old November 9th, 2009, 01:48 PM   #9
mellis
Member
United States

mellis is offline
 
Join Date: Nov 2004
Location: Cincinnati, Ohio
Posts: 656
Quote:
Originally Posted by daba View Post
Whilst I agree with this idea in principle, I believe it dramatically detracts from one of the best "features" of the 1756 Analog modules, that everything is (or can be) done inside the module, and everything else you do, (i.e. Process Alarms, Rate of Change Alarm), is specified in Engineering Units, and appears in the module tag as engineering units.
I respectfully disagree that doing everything inside the module is desirable. I admit, on my first ControlLogix project I did the scaling on the card in engineering units. It seemed really cool.

Problem is, it's a pain to enter the data and it's a pain to modify later. As the OP found out, if you want to configure scaling from the HMI, it really makes life complicated. The same applies to alarm trip points etc. Triggering module updates is not simple or desirable. The whole module stops communicating, not good. Besides, it's self inflicted complication, just avoid it.

After many projects, this is my preferred setup. Scale on the card to 4.0 to 20.0. Scale in software to engineering units.

Benefits:
Makes it easy to setup so scaling can be modified from HMI. I like to use a UDT. You can make an AOI if you like, I don't have a problem with a CPT for each channel.

Intial setup is much easier because you setup one card then copy the configuration to all other cards. No more tedious keying in the values for each channel. And then doing it over during checkout when things invariably change.

During checkout, the raw value is in milliamps. If you are going to set the card scaling to the same value for all channels, this is by far the most useful scale.

My two cents
  Reply With Quote
Old November 9th, 2009, 02:45 PM   #10
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 2,872
Quote:
Originally Posted by mellis View Post
I respectfully disagree that doing everything inside the module is desirable. I admit, on my first ControlLogix project I did the scaling on the card in engineering units. It seemed really cool.

Problem is, it's a pain to enter the data and it's a pain to modify later. As the OP found out, if you want to configure scaling from the HMI, it really makes life complicated. The same applies to alarm trip points etc. Triggering module updates is not simple or desirable . The whole module stops communicating, not good . Besides, it's self inflicted complication , just avoid it.

After many projects, this is my preferred setup. Scale on the card to 4.0 to 20.0. Scale in software to engineering units.

Benefits:
Makes it easy to setup so scaling can be modified from HMI. I like to use a UDT. You can make an AOI if you like, I don't have a problem with a CPT for each channel.

Intial setup is much easier because you setup one card then copy the configuration to all other cards. No more tedious keying in the values for each channel. And then doing it over during checkout when things invariably change.

During checkout, the raw value is in milliamps. If you are going to set the card scaling to the same value for all channels, this is by far the most useful scale.

My two cents
I'll deal with the higlighted comments above.

0. "it's a pain to enter the data and it's a pain to modify later" - can't see that myself - having configured several hundred controllogix analog channels over the last 10 years, i don't find it a pain to set them, or modify them if need be.

1. "Triggering module updates is not simple or desirable" - what could be simpler than to trigger a "Module Reconfiguration" message in the code after setting the values to the Location:Slot:C tag elements. And what is undesirable about it, they've enabled the update feature via CIP service codes just for the purpose.

2. "The whole module stops communicating, not good" - no it doesn't. From the help text - "Use the Module Reconfigure message to send new configuration information to an IO module. During reconfiguration :- Input modules continue to send input data to the controller. Output modules continue to control their output devices"

3. "Besides, it's self inflicted complication" - i believe the opposite, that hiding the scaling in code is a self-inflicted complication. If I want to see a channel's scaling, I would naturally look at the channel scaling parameters in the module configuration dialog. Besides, if you are doing scaling in the code, you will stop reading analog inputs while in program or fault modes. That information may be being MSG read by another controller !!


The issues you raised with "on-the-fly" reconfiguration are non-existant, and your methods will involve a lot of unnecessary code, which is obviously wasteful in terms of memory used (not much of an issue i agree), and scan times, which may be more of an issue in time-critical applications, such as motion.

Your methods will also detract from one of the most useful techniques in Logix5000, that is Aliasing to the real I/O tag.

A maintenance engineer, who may not be as adept as you at deciphering your scaling code, will have a hard time debugging a fault like "The temperature reading has gone high". With aliasing he can simply look at the "Temperature" tag in the code, or in the tag database, and see exactly which channel on which card it is wired. He also knows (or may read in the manuals) exactly where to go to find channel scaling or alarming data, and can cross-reference from there to see where in the code it may be updated.

In short : "self inflicted complication"
  Reply With Quote
Old November 9th, 2009, 03:13 PM   #11
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 2,872
mellis, I've just had other thoughts on this subject.

Your methods will preclude the use of using module data state change to trigger Event Tasks, because your channel data will not be scaled when the ask executes. To overcome that, you would have to put your scaling code in the event task itself, AND in normal code, so that the channels are always scaled for all the code to see. Now you've got 2 places to modify if necessary

Your methods will also make it impossible to use the CST or rolling timestamp features of the modules, where the data-change can be logged to mS resolution.

And lastly, as a programmer, you should always have in the back of your mind that yes, you may be totally at ease with what you are doing.

But the end-user, who will have to maintain the system for many years to come, may only have cause to go into the system sporadically. He will inevitably consult A-B documentation when he has a problem, and will scratch his head trying to figure out what you have coded, and even why !

You should be making his life easier, not yours, although I suspect you are having to do so much rung and tag documentation that you are out-weighing the "benefits" you get from being ablr to Copy/Paste your module configurations. (At least I hope you are fully documenting it !).

Last edited by daba; November 9th, 2009 at 03:16 PM.
  Reply With Quote
Old January 14th, 2014, 05:40 PM   #12
gijoevaldez2010
Member
United States

gijoevaldez2010 is offline
 
Join Date: Feb 2010
Location: dklfjsdklf
Posts: 6
The config button doesnt show up for my module. I have 6 of them and it shows up for the first 4 but not for my last 2 modules. Is there something I need to do have this available?
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Mitsubishi GOT issue (long winded) Killercal LIVE PLC Questions And Answers 4 August 18th, 2009 07:28 PM
PLC-5 PID - Help With Input Scaling? skyfox LIVE PLC Questions And Answers 5 November 3rd, 2007 01:51 PM
AB 1734-AENT POint IO issue ettikudiappan LIVE PLC Questions And Answers 0 July 17th, 2007 09:42 PM
s7 scaling darren.s LIVE PLC Questions And Answers 5 June 22nd, 2005 06:45 AM
Scaling DaveyT LIVE PLC Questions And Answers 6 August 9th, 2002 08:37 PM


All times are GMT -5. The time now is 05:48 PM.


.