Omron ns8-tv01b-vs connection problems

Hi all
I'm installing a ns8 to a CQM1H (although right now i'm testing with a cqm1) I'm connected to the cqm1 to my laptop through the peripheral port and trying to connect the screen through the rs232c port, homemade cable (2,3 crossed and 4,5 jumped on both ends 9to 9 for sg ) this info comes from both cqm1 w226 manual and the v083 manual NS setup. I am running 15 to 20 meters through emt so i must make my own cable. i know this is longer than is recomended but at moment I have only 1 cj1w-cif11 so i'm doing this for testing, I have tried all the protocals and combos i can think of. what i cant find is the bit stuff for the screen. should it be 1,7,2,E or ??
thanks
Tom
  Reply With Quote
Old December 2nd, 2009, 08:25 PM   #2
BobB
Lifetime Supporting Member
Australia

BobB is offline
 
BobB's Avatar
 
Join Date: Jun 2002
Location: Sydney
Posts: 3,322
You can pass throught the PLC to the screen but it is painfully slow. I have given it away and just use a USB cable these days. Recommend you use USB - I have a long USB cable - not 30 metres but about 10 - and it works quite well.
__________________
The Old Pfhaart

  Reply With Quote
Old December 3rd, 2009, 06:58 AM   #3
gtsuport
Member
United States

gtsuport is offline
 
Join Date: Feb 2005
Location: Grand Rapids, MI
Posts: 812
You need to check the protocol for the port on the NS.
From memory it can be set for either Host Link or NT Link.
You will need to set the port on the CQM1 for the same.

Hope this will help.
  Reply With Quote
Old December 4th, 2009, 11:40 AM   #4
crankshanft
Member
Canada

crankshanft is offline
 
Join Date: Jan 2006
Location: ab
Posts: 38
36 hours without internet is long time when you're looking for info! I can talk to the ns through Ethernet and I can talk to the plc just not to each other. I've tried all the protocols available and no luck what i'm after is what cable should i be using? c200h-cn510 or a ? and what protocol would be best. the plc is always hooked to a pc (logging through dde) and the NS will be logged through ftp.
  Reply With Quote
Old December 4th, 2009, 03:23 PM   #5
gtsuport
Member
United States

gtsuport is offline
 
Join Date: Feb 2005
Location: Grand Rapids, MI
Posts: 812
What are the dip switch settings on the CQM1?
  Reply With Quote
Old December 4th, 2009, 04:13 PM   #6
PMCR
Member
United States

PMCR is offline
 
PMCR's Avatar
 
Join Date: Jul 2005
Location: Philadelphia
Posts: 62
For HMI to PLC comms, you want NT Link protocol, if the CQM1 has it. CQM1-CPU11 and CPU21 do not have NT Link, CPU41,42,43,44,45 do have NT Link.
If you can use NT Link:
There are 2 NT Link protocols: NT Link 1:1 and NT Link 1:N.
The CQM1 only supports NT Link 1:1.
The NS supports both, so make sure you are using NT Link 1:1 on the NS.
Make certain that DIP Switch 5 is in the OFF position on the CQM1. This lets the CPU use the 'internal settings' you make in CX Programmer or Syswin.
After downloading the PLC Settings (port setup), cycle power to the PLC to make theses changes take effect.

If you cannot use NT Link:
Then you must use Host Link setting on both the NS and CQM1.

If you are still having problems, please post or private message your NS and PLC project.
  Reply With Quote
Old December 4th, 2009, 05:34 PM   #7
crankshanft
Member
Canada

crankshanft is offline
 
Join Date: Jan 2006
Location: ab
Posts: 38
It works now thanks

went to and got a new rs232c cable cut it in half, spliced the wire together
9 ----9
2-----3
3-----2
4- -4
| |
5- -5
it works now
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Omron Dongle problems Billy_the_Kid LIVE PLC Questions And Answers 14 January 24th, 2013 03:14 PM
OMRON CJ1's Ethernet Networking problems castro LIVE PLC Questions And Answers 6 June 8th, 2009 05:57 AM
Omron c200hs problem ... marq LIVE PLC Questions And Answers 13 May 22nd, 2006 01:07 AM
Oh no, problems with OMRON touch screen BJR LIVE PLC Questions And Answers 7 June 4th, 2004 08:19 PM
Can You Help with Omron CX-Programmer Printing Problems LGropel LIVE PLC Questions And Answers 1 November 12th, 2002 05:43 PM


All times are GMT -5. The time now is 06:06 PM.


.