Micrologix 1200 after power failure

I have a microligix 1200 processor for some valve control Im trying to stop it from powering up the outputs that were on prior to power failure on start I want it to execute the program as if it were just loaded checking input conditions to prevent all the valves from opening at one time when power returns can this be done through processor status file I tried changing the mem module bits but it did not change any help would be appreciated Thanks
  Reply With Quote
Old December 23rd, 2009, 03:09 PM   #2
bernie_carlton
Lifetime Supporting Member + Moderator
United States

bernie_carlton is offline
 
bernie_carlton's Avatar
 
Join Date: Apr 2002
Location: Yakima, Washington
Posts: 6,239
You will probably have to deal with the logic itself. S:1/15 is a 'First Scan' bit and can be used to preset conditions on a power-up or program to run transition.
__________________
Controlling outputs is the PLC's way of getting its inputs to change.

www.thePLCguy.com
  Reply With Quote
Old December 23rd, 2009, 08:33 PM   #3
gmferg
Lifetime Supporting Member + Moderator
United States

gmferg is offline
 
gmferg's Avatar
 
Join Date: Feb 2008
Location: Modesto, CA
Posts: 334
You may want to also research using "seal-in" logic versus Latch/Unlatch. I'm making an assumption here without seeing your code.

More suggestions may be provided if we can take a look at your program. Can you post it?
  Reply With Quote
Old December 24th, 2009, 12:15 AM   #4
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,838
Quote:
Originally Posted by gmferg View Post
You may want to also research using "seal-in" logic versus Latch/Unlatch. I'm making an assumption here without seeing your code.

More suggestions may be provided if we can take a look at your program. Can you post it?

That is a good point. Real world Outputs should almost never be latched. Internal Bits can be latched, and then buffered with other conditions to decide if an output should go true. Only you know the specifics of your machine, and there exceptions to ever rule. An MCR Relay with a reset that kills all Output Power is a must on machines where un-commanded restart could cause machine damage or personnel injury.

Stu......
  Reply With Quote
Old December 27th, 2009, 02:51 AM   #5
e27978
Member
United States

e27978 is offline
 
Join Date: Sep 2006
Location: washington pa
Posts: 35
Dont know why but I never thought of using seal in logic insted of latch I changed program and it works fine now


Thanks to all
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
To Latch Or Not To Latch BOWRIDER LIVE PLC Questions And Answers 43 October 21st, 2015 04:19 AM
How to put MicroLogix 1200 in Run Mode Philadelphia Frank LIVE PLC Questions And Answers 8 August 22nd, 2011 04:02 PM
Plant Power Failure justin lutz LIVE PLC Questions And Answers 11 September 29th, 2008 02:00 PM
micrologix 1200, and 1000 question darrentpi LIVE PLC Questions And Answers 4 July 24th, 2008 04:42 AM
1746-P4 Power module for SLC 501 failure Amitava LIVE PLC Questions And Answers 0 February 22nd, 2006 06:45 PM


All times are GMT -5. The time now is 12:48 PM.


.