plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old July 5th, 2002, 05:21 AM   #1
iknowsomeplc
Dubai
iknowsomeplc is offline
iknowsomeplc's Avatar
Flex frequency input module - problem with encoder connection
We are using 1794 -IJ2 Flex IO modules for taking Encoder feedbacks from Hubner- Berlin Encoders. When we are connecting one channel , the readings are good. The supply voltage from the module - to - Encoder drops to 5.6 VDC but it still works and we get the readings OK. ( the 24vdc supply at the Power Supply end stilll measures 24VDC !!).
But the moment we connect 2nd encoder to 2nd channel , both the readings are gone . I understand that the supply voltage 24vdc folds back inside the module ( In IJ2 ,the encoder supply has to routed through the module only)
The details of Encoder Name Plate is :
HUBNER - BERLIN
MODEL : POG9GD 150
Incremental Encoder
9-30 VDC
IP56
Current Intake : 22 mA
Anybody knows solution for this?
Old July 5th, 2002, 07:03 AM   #2
Terry Woods
United States
Terry Woods is offline
Is this the situation you are describing?
If so...
Then since the module voltage to the first encoder drops at all means that either...
1) the module can't supply the amount of current that the encoder needs. (a module problem)
-OR-
2) the encoder wants more current then the module can supply (an encoder problem)
So, which problem is it?
Insert a milliamp-meter between the module and the encoder.
If the current is greater than the specified 22mA then the Encoder is at fault - replace it.
If the current is substantially less than 22 mA then the Module is at fault - replace it.
It's an OHM's Law kinda thing.
You can't expect a device to deliver more power than it is capable of - it gets kinda tired (voltage drops).
At the same time, a down-line device should not demand more power (read that as more current, because of low resistance) than is available.
So, although the module and encoders seem to be "matched", one of them is not operating properly. You won't know which is failing until you read the mA.
Old October 30th, 2009, 05:37 AM   #3
jainil2210
India
jainil2210 is offline
jainil2210's Avatar
Exclamation 1794-IJ2 frequency module.
Hello,
i'm planning to use 1794-IJ2 frequency module for the first time in my new project.
My questions are:
1)can i use this module in place of dynalco speed monitor?
2)is it necessory to connect 2 inputs in this module?cant i use single magnetic pickup probe as single input in this module?(as catalog says that this module calculate speed with two probes only.)
3)what is the difference between gate input and frequency input?can i connect any input to frequency input?
Old October 30th, 2009, 11:18 AM   #4
Mickey
United States
Mickey is offline
Mickey's Avatar
Yes, but you will have to do some math to get speed. Module gives you frequency and direction.
No
Yes a single input is ok. Each channel has two inputs frequency and gate. Frequency input is used to calculate frequency and the gate input is used to determine direction.
Gate input is used to determine direction.
Not sure what you mean here, see manual for devices that can be connected. Link below for manual.
http://literature.rockwellautomation...m011_-en-p.pdf
__________________
Mickey
If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
1762-IF2OF2 Analog Input Problem davidgay LIVE PLC Questions And Answers 22 August 14th, 2013 05:25 AM
plc5 with AB 1771-DB basic module, its urgent plz help me nileshsurya LIVE PLC Questions And Answers 6 July 20th, 2005 02:45 AM
SLC 5/03 data loss andydaoust LIVE PLC Questions And Answers 1 October 10th, 2002 07:38 PM
AB Analog Input Module Wiring... Eric Nelson LIVE PLC Questions And Answers 3 May 6th, 2002 09:37 AM