Analog (4-20mA) Reading Problem
Hi good day to all,
I'm Andrei and came from the Philippines. I had a project which deals with an Auma Actuator and Omron PLC (Analog Input Devicenet). The Auma Actuator outputs the Motor position 0%(Close) to 100%(Open) through 4-20mA. I've had success the first time reading the Analog Signal.
After few Months, I was called and the case is that the reading went OFF. When I checked the current (I) reading through Digital Multimeter (DMM), I can see 4-20mA clearly. But when I try to look in the PLC program, it can't read 4-20mA. I've tried to use other 4-20mA sensor to check if the Analog Terminal is the problem but I encountered no problem at all.
In our application, we have used two (2) Auma Actuator. I have no problem with the other one.
What can I possibly do to make the PLC read the 4-20mA Analog Signal from the Actuator? I'm already out of options and blanked right now. Hope you can help me. Thank you very much Automation experts and I'll so much appreciate any help I can get.
Old May 26th, 2010, 02:58 AM   #2
BryanG
United Kingdom
BryanG is offline
So just to confirm the problem:
If you connect another 4-20mA signal to the PLC - works
If you connect a meter to your existing 4-20mA signal - you get the right reading.
If you connect the existing 4-20mA source to the PLC - problem.
Have you tried connecting the second actuauot output to the first input on the PLC, if that works then the problem is in the actuator. Even though you get a right reading on the meter there may be a problem with something earthing where it shouldn't.
You may be able to 'fix 't things by adding a 4-20mA signal isolator, something like this:
http://uk.farnell.com/status/sem1020...1?Ntt=489-4881
You will need to make the PLC give a supply voltage for it's part of the loop, or choose an isolator with it's own supply terminals.
If the problem is in the actuator then the correct thing to do is to replace it rather than 'fix' things. The symptom may signal the start of a failure in the actuator.
Bryan
Old May 28th, 2010, 01:04 PM   #3
Roy Matson
Canada
Roy Matson is offline
Roy Matson's Avatar
As BryanG pointed out you probably have a grounding problem, something is now grounded that wasn't before. It might be un-related to the Auma actuator.
A simple test you can do is disconnect the actuator mA signal and see if you get mA from just one terminal with the other probe of your meter connected to ground.
You should always try to ensure that all field device signals are isolated from ground.
Old May 28th, 2010, 01:11 PM   #4
shooter
Netherlands
shooter is offline
shooter's Avatar
if below 4 mA it will stop reading so be sure it is above, is ground connected?
is program rerading correct value?
__________________
shooter@home.nl
skype shooter paul.deelen
Computer Shooter
Paul Deelen
J. Wassenaerstraat 29
NL 5224 GG 's-Hertogenbosch
+31653300739
Old June 7th, 2010, 06:22 AM   #5
Andreik
Philippines
Andreik is offline
Thank you all so much for the help. The problem was resolved and it was indeed a grounding problem. But I'm really wondering how the Ammeter was still able to read the I output from the actuator since there has been a grounding problem. I've already encountered countless tricky situations in automation. Applications is indeed more challenging than being a theorist.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Reading analog ouput from a PLC- 0to 10V duskndreamz LIVE PLC Questions And Answers 0 April 2nd, 2010 11:26 AM
Mitsubishi PLC analog problem roxtech LIVE PLC Questions And Answers 0 August 12th, 2009 03:06 AM
S5 Analog Scale problem!! glasdam LIVE PLC Questions And Answers 4 January 3rd, 2008 09:46 AM
Analog problem BoSChoW LIVE PLC Questions And Answers 11 December 3rd, 2006 10:09 AM
S7 300 SM331 Analog Inputs Problem; Relative DC leval of adjacent inputs. David Torrens LIVE PLC Questions And Answers 4 November 10th, 2004 10:14 AM