EM 277 as a slave in a 315-2DP Master

Dear Folks,

I have a 315-2DP master that have several EM 277 slaves attached to it, a typical I/Q address for two EM's is as follows: Slave 1:1344-1407(32 word out/32word in)for their I/Q addresses
slave 2:1536-1599(32 word out/32word in)for their I/Q addresses

Now I want to reflect the status of one bit in slave 1 to be read in slave 2 , I tried to write a code in the 315, but the CPU doesn't accept an address of (I 1536.0 or Q 1536.0) for instance.

Waiting to get your help as usual.

Regards
Hagos
  Reply With Quote
Old May 30th, 2010, 05:03 AM   #2
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,116
Thw two adresses are probably outside the proces image of the CPU.

I recommend that you read all data from each slave with SFC14 DPRD_DAT, and write all data with SFC15 DPWR_DAT.
You must set aside some memory for use in you code. Preferably a DB.
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old May 31st, 2010, 01:06 AM   #3
hagos
Member
Sudan

hagos is offline
 
Join Date: Oct 2004
Location: Africa
Posts: 204
Thanks Jesper for the reply,

This is what I texpected too, but I thought it is ok when the HW configuration allowed me to enter the address I/Q 1536.

Can the SFC15/15 let the slave to put the data in a DB at the master side? If so I appreciate if you can show me how.

Best regards
Hagos
  Reply With Quote
Old May 31st, 2010, 02:56 AM   #4
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,116
I suggest that you transfer the i/o data from the two slaves to one or more DBs by means of SFC14 and SFC15.
Then in code, you manipulate the i/o in the DBs.

Like this:

Read all DP slave input data with SFC14.

Do something in code.
Like:
A "DP_IO".inp.word1536.bit00
= "DP_IO".outp.word1536.bit00

Write all DP slave output data with SFC15.

An alternative if there is not so much data from each slave is to simply place the i/o inside the proces image.
Then you can simply write:
A I36.0
= Q36.0
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
CompactLogix as a Modbus slave AND master? mainstreetmark LIVE PLC Questions And Answers 3 November 9th, 2009 05:16 PM
is it possible to commutate from Slave to master in MODBUS Protocol baidimed LIVE PLC Questions And Answers 8 November 19th, 2008 08:07 AM
Redlion G303 Slave -> Master -> Slave Modbus Issue Marc_U LIVE PLC Questions And Answers 6 April 17th, 2008 01:44 PM
master slave configuration rameshgurav31 LIVE PLC Questions And Answers 1 November 6th, 2007 05:39 AM
Master Slave al_d LIVE PLC Questions And Answers 32 July 4th, 2006 07:42 AM


All times are GMT -5. The time now is 09:28 PM.


.