Lead/Lag/Standby SELECT from SCADA

Hello everyone.

I'd first like to say that I did in fact search the forums but I didn't find anything that really helped. I have somewhat of a unique situation here.

I'm working on an SBR and am programming a Disk Filter Feed Pump routine.

There are 3 pumps. Filter Feed Pump A, B, and C. I have programmed the Lead and Lag request conditions and now I must program a selectable (From RSVIEW32 SCADA)Lead/Lag/Standby routine.

I am somewhat of a novice at programming and could really use some help! Any reply would be greatly appreciated.

In the event of needing to service a pump, the client would like to be able to select one pump as standby and let the other two pumps operate on normal Lead/Lag sequence.

Kicker is they want to be able to select which pump is lead and which pump is lag as well! Also, the pumps are all on VFD's and if the lag pump is called on, they split the speed control.

I'm very frustrated and overwhelmed seeing as the boss returns tomorrow to see my work. After trying all day it seems I've become quite desperate. Does any one have any tips/templates that might help?

Thanks
  Reply With Quote
Old June 16th, 2010, 09:47 PM   #2
jrwb4gbm
Lifetime Supporting Member + Moderator
United States

jrwb4gbm is offline
 
Join Date: Apr 2002
Location: NC
Posts: 2,245
I know it is not SCADA but...
See the thread in this link, posts 39 and 61, might be some help:
http://www.plctalk.net/qanda/showthread.php?t=9499

Edit:

Last edited by jrwb4gbm; June 16th, 2010 at 10:10 PM. Reason: more info
  Reply With Quote
Old June 16th, 2010, 09:48 PM   #3
24fretslater
Member
United States

24fretslater is offline
 
Join Date: Aug 2007
Location: Washington
Posts: 32
There is one more thing. These pumps run all the time. The only thing that stops them is a Filter Feed Channel low level alarm.
  Reply With Quote
Old June 16th, 2010, 11:16 PM   #4
robo77
Member
United States

robo77 is offline
 
Join Date: Apr 2010
Location: Iowa
Posts: 323
post what you used for your lead/lag

try zipping your file and posting..it
  Reply With Quote
Old June 17th, 2010, 04:20 PM   #5
24fretslater
Member
United States

24fretslater is offline
 
Join Date: Aug 2007
Location: Washington
Posts: 32
Here's my first attempt. I think I'm probably way off.
Attached Files
File Type: zip Filter Feed Lead Lag Standby TEST.zip (33.5 KB, 72 views)
  Reply With Quote
Old June 18th, 2010, 07:09 AM   #6
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 6,029
We do this by having two sets of registers. One is designated as "current" lead/lag/standby and the other as "new". The operator enters his changes in the new fields, and the current fields are display only read from the PLC. We have an "execute" momentary push button on the HMI. When the operator is happy with his new entries he pushes it, and this sets a bit in the PLC. This bit moves the new lead/lag/standby values to the appropriate registers and initiates the stopping and starting of the appropriate equipment.
  Reply With Quote
Old June 18th, 2010, 10:19 PM   #7
Mike Lamond
Member
United States

Mike Lamond is offline
 
Join Date: Oct 2009
Location: Syracuse, NY
Posts: 87
I don't have a triplex sequencer handy in A-B, but the attached file is a PDF printout of a quad that I programmed with just about every possible feature, as specified by the Owner's Engineer. It's not just belt-and-suspenders, but an elastic waistband too.
  1. Auto-1-2-3-4 lead pump selector switch on the control panel door.
  2. In 1,2,3 or 4, run the pumps in order with the selected pump as lead.
  3. In Auto, the operator can select Auto or Manual alternation through the HMI.
  4. In HMI-Auto, the pumps run in order with the lead pump advancing at a preset time of day.
  5. The pumps can alternate only if one pump is running;
  6. If the lead pump is not available (fault or switches not in auto), alternate to the next pump.
  7. If a lag pump is not availble, move the remaining pumps up as required.
  8. If a lag pump becomes available, do not restore it to the sequence until the corresponding lag stage is off.
  9. In HMI-Manual, the operator can set the pumps in any order. I used the New and Current registers as Tom described and validate the New values by checking their product (24) and sum (10). The HMI limits the input range.
I've gone as high as 4 of 5 with straight order sequencing and 4 of 6 with a requirement to balance the odd and even numbered pumps in operation. In that case, the isolation transformers on the pump VFDs were split between delta-delta and delta-wye in order to cancel some of the harmonic noise on the 480 volt service.
Attached Files
File Type: pdf Quad_Pump_Rotation.pdf (172.1 KB, 239 views)
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
MEDOC For Mitsubishi adkeys2 LIVE PLC Questions And Answers 23 April 4th, 2017 05:40 PM
PLC that uses labview as language umlphysics LIVE PLC Questions And Answers 5 September 15th, 2009 12:14 PM
Best way to impliment a SCADA map godfrey LIVE PLC Questions And Answers 6 February 19th, 2006 04:16 PM
Best way to upgrade a SCADA system Johnny T LIVE PLC Questions And Answers 10 May 3rd, 2005 03:38 AM
Preparing a Practical SCADA course ayman metwally LIVE PLC Questions And Answers 11 October 16th, 2004 02:03 PM


All times are GMT -5. The time now is 05:56 AM.


.