Analog Input as Multiple Digital Input
Hi all, I need to add 2 or 3 digital inputs to an existing PLC but have no spares and the cabinet is so tight that I cant add any IO. I have 2 spare analogs and was thinking of switching some sort of resistor combination into it and use the PLC code to view the analog value and switch internal bits to simulate the inputs.
I just need to add a selector switch for 3 different product sizes. Normally I'd have a 3 pos. switch with 2 inputs. LHS input 1/size 1, RHS input 2/size 3, centre pos no input size 2.
Does anyone know how to get a resistor combination to work on this?
PS analog input is configured for 0-10V
I can work this out with a little looking around but Iím just trying to get a quick fix with minimal input J
Thanks.
__________________
If I Knew then what I know now I probably would have written the code a little different!
Old July 4th, 2010, 02:50 PM   #2
Bob O
United States
Bob O is offline
What PLC and I/O? I know AB has high density cards that you could switch out.
Old July 4th, 2010, 03:17 PM   #3
69FIREBIRD
New Zealand
69FIREBIRD's Avatar
Hi Bob, fixed IO - MLX1100 w no space to add on.
__________________
Old July 4th, 2010, 03:59 PM   #4
keithkyll
United States
keithkyll is offline
From 24DC supply. 4 resistors in series.
R4=10K. R1, R2, R3 = 560. +24 to 10K. Last 560 Ohm to common.
This should give a signal about 1.15V per step. 2 mA current.
10K should be 1 watt. 560's can be half watt.
Series string is:
Common, R1, Tap 1, R2, Tap 2, R3, Tap 3, R4, +24V.
Old July 4th, 2010, 05:31 PM   #5
69FIREBIRD
New Zealand
69FIREBIRD's Avatar
Thanks Keith. So as I see it, it all makes sense - simple V=IR
See attached PDF of how I see it working as per your written description.
__________________
Old July 4th, 2010, 05:55 PM   #6
L D[AR2,P#0.0]
United Kingdom
L D[AR2,P#0.0] is offline
What is the input resistance of the analogue input ?
Old July 4th, 2010, 06:11 PM   #7
69FIREBIRD
New Zealand
69FIREBIRD's Avatar
MLX 1100 Voltage input impedance 210 Kohm. will there be enough current flow through the resistors for it to be detected by the analog input 2mA is what is anticipated so I would expect yes to be the answer?
__________________
Old July 4th, 2010, 08:01 PM   #8
keithkyll
United States
Schematic is correct. 10K is 5% of 200K. That means there will be a 5% drop in voltage output. 1.15 * .95 = 1.0925. If this becomes a problem, change 10K to 5K. That will double voltages (2.xx - 6.xx) and current (4 mA), and reduce error to 2.5%.
Old July 5th, 2010, 03:03 PM   #9
69FIREBIRD
New Zealand
69FIREBIRD's Avatar
Worked a treat! thanks to all.
__________________
Old July 5th, 2010, 03:46 PM   #10
shoelesscraig
United States
shoelesscraig is offline
shoelesscraig's Avatar
I understand this setup perfectly. What I'm upset about is the fact that I never would have thought of it on my own! Just when I'm feeling pretty good about my skills (which are NO WHERE NEAR as good as many others on this forum) I get taught a new trick.
Makes me wonder how much I'd know if the internet didn't exist.
__________________
"It's better to be hated for who you are than be loved for who you're not"
-Van Zant Brothers
Old July 5th, 2010, 05:27 PM   #11
bernie_carlton
United States
bernie_carlton is offline
bernie_carlton's Avatar
Conceptually it's a potentiometer with fixed stops.
__________________
Controlling outputs is the PLC's way of getting its inputs to change.
www.thePLCguy.com
Old July 5th, 2010, 07:30 PM   #12
rpoet
United States
rpoet is offline
I've done something similar, but in reverse. I needed one more digital output, but only had an analog output available; AutomationDirect DL-05 with an combo analog I/O card. I used the spare analog out to drive the base of an NPN resistor (2N2222, or equivalent) through a 10k resistor; the load (an LED indicator light) was low-side switched.
It worked perfectly. It gave me another digital output without having to replace the PLC with a larger unit or resort to something else of equal overkill, like remote I/O.
I realize this post isn't exactly on topic, but I hope it gives someone else a little help in a pinch.
-rpoet
Old July 5th, 2010, 08:56 PM   #13
Plastic
United States
Plastic is offline
Necessity is the mother of Invention
At the 11th hour when functionality is added to the original design, we all scramble to make it work with what we have in hand.
One came to mind regarding this issue. Years ago we implemented one of the first generation Micrologix 1000 digital I/O only. The customer added a 2nd product model to the existing machine that needed different machining positions. We added a linear transducer O-10v to measure the axis, but were stuck as no analog expasion was available yet for the ML1000. We found a third party DIN rail module that was a analog-to-freq converter, and fed the frequency into the ML100 Digital Input 0 which was capable of high speed counting.
The axis moved slowly, so we merely interrogated how many counts happened in a given period, and found our anaolg actual position.
Old July 6th, 2010, 12:13 AM   #14
basharath
India
basharath is offline
only if we can use the digital inputs as analog inputs by some setup.
__________________
"My choice of prophet muhammad(pbuh) to lead the list of most influential persons in history may surprise some and might be questioned by others but he was the only man successfull on both religious and secular levels."MICHEAL H.HART,THE 100 MOST INFLUENTIAL PERSONS IN HISTORY.
Old July 6th, 2010, 04:06 PM   #15
Mike Lamond
United States
Mike Lamond is offline
Quote:
My version used a 10-turn pot with 3-digit dial to retrofit a 16-position product selector on a few dual-pump mixing machines. They had Bailey Loop Command controllers which had all three digital inputs used but one spare analog input.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Analog input filtered value riouxhugo LIVE PLC Questions And Answers 3 November 5th, 2009 07:44 PM
Resetting Digital Input module automatically from RS Logix 5000 hasan_ali LIVE PLC Questions And Answers 3 October 1st, 2009 05:39 PM
PowerFlex 70 digital input issue Ike LIVE PLC Questions And Answers 2 November 17th, 2007 06:51 PM
Logic Question : Tracking Parts knichols LIVE PLC Questions And Answers 26 November 16th, 2005 11:34 PM
Analog Input Fluctuations Steve Etter LIVE PLC Questions And Answers 18 October 20th, 2004 06:34 AM