PRofibus network with more than 1 Master

Hello Guys

i may ask directly Jesper but maybe someone else can give an interresting answer

I have a project with a PN/DP plc and the customer would like to use my profibus network to connect instead of the Ethernet availaible

The 315pn/DP is configured as a DP master and control 8x S7-200 slave. Can it be possible to include a Scada system as a MAster also on this network....

I not sure but i think as long as it is a Scada/HMI it may work but if 2 PLC are Master on the same network it won't work ? i'm i right ? I believe that because i used an S7-317 2DP to get 2 separate DP network the last time i did that and it worked fine with the 317 being master on 1 and slave on the other....
__________________
Siemens Addict
  Reply With Quote
Old July 8th, 2010, 02:07 PM   #2
tim2
Member
United States

tim2 is offline
 
Join Date: Nov 2004
Posts: 201
Basically, I think you're right.

Typically an HMI On the network is not considered the same type of master as the 315. I think the HMI is considered a Master Class 2 and the CPU a master class 1. They can co-exist fine.

Two CPUs as master's don't play together so well.
  Reply With Quote
Old July 8th, 2010, 03:27 PM   #3
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 11,654
Yes, several masters can co-exist on the same profibus cable, and each master can have its own slaves, and the masters can send data to each other. Additionally, one or more HMIs which are also masters (but with no slaves attached) can poll data from the PLCs.

There are some gotchas though.

The performance is much decreased with respect to how fast the masters can update the i/o of their slaves. Something like a factor 5-10 slower (!).

The combined multi-master system is much less flexible with respect to how it can be modified on the run, and how nodes can be attached or removed dynamically.

And, one fault can bring the all master systems down.

Because of this, I really recommend to at least put the higher level comms (CPU to CPU, HMIs and SCADAs) on ethernet, and if needed i/o on lower level Profibus (mono-master) or Profinet.
Today, ethernet is the answer. It is also not expensive. Think ahead. Will profibus be as widespread just a few years from now ?
And as your CPU already has a PN port, and your SCADA most certainly has ethernet, why even start to consider to put the SCADA on Profibus ?
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old July 9th, 2010, 11:21 AM   #4
Jeff23spl
Member
Canada

Jeff23spl is offline
 
Join Date: Jan 2010
Location: Canada
Posts: 734
thanks for ideas

Profinet is a futur option but this project as already been designed, installed and started with S7-200 as profibus slave.
DP module VS ETH module on the 200 have a 3x price difference factor to be considered too...

The other factor is that this project is actually at many hundred miles from my office....
Project sold in 2005 but started only last year....

So i was right to tell the customer to stay away from my Profibus network and try to connect to Ethernet instead...

I will...make new project with 1200 on eth as slave and maybe using profibus port for Scada or also using Eth....i'm looking at that and, to play safe: Waiting for a while to see improvement on the 1200 itself and the software
__________________
Siemens Addict

Last edited by Jeff23spl; July 9th, 2010 at 11:23 AM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Hilscher DPM (Profibus Master) on AB Compactlogix. shaunn LIVE PLC Questions And Answers 5 April 28th, 2009 07:16 AM
2 Master PLC's and 45 slaves on same Profibus lauwerstim LIVE PLC Questions And Answers 6 April 1st, 2009 02:00 AM
Profibus FMS: is there a master on it or not sinanissa LIVE PLC Questions And Answers 4 December 16th, 2008 02:28 PM
S7400 and S7300 Profibus Network ylade LIVE PLC Questions And Answers 3 October 10th, 2008 09:06 AM
profibus network between Siemens S5 and S7 PLC Leonardo LIVE PLC Questions And Answers 3 June 25th, 2002 09:05 AM


All times are GMT -5. The time now is 02:28 AM.


.