Procedure for changing battery on S7-400 and S7-300

Hi

Would anyone have a procedure for replacing batteries on Siemens S7-300 and S7-400 PLC's.

Thanks
__________________
Mikey
  Reply With Quote
Old July 13th, 2010, 09:16 AM   #2
dchartier
Member
Canada

dchartier is offline
 
Join Date: May 2003
Posts: 1,519
Hello Mickey;
There are no batteries in the newer S7-300 CPU modules, so that question is answered easily (they use MMCs for program and data retention nowadays).
Batteries for the S7-400 are inside the power supply module. In case you have an older S7-300 CPU with battery, the procedure is the same as the one for the S7-400: remove the defective battery while power is on (or you might lose your program memory)and insert replacement battery into the free slot(s).
If you have any doubts, look at the section on battery replacement in the S7-400 hardware and Installation manual:
http://support.automation.siemens.co...iew/en/1117849
Hope this helps,
Daniel Chartier
  Reply With Quote
Old August 9th, 2011, 05:15 PM   #3
Farnesi
Member
Brazil

Farnesi is offline
 
Join Date: Jun 2009
Location: Brazil
Posts: 37
Hi

Sorry for reviving the subject but I thought it would be better than creating other topic. The deal is my S7-400 PS 407 has battery failure and I replaced the battery 5 times already in a row - so I'm 100% sure it's not the battery fault. What could it be? The power supply itself? Is it in danger of failing completely?
  Reply With Quote
Old August 10th, 2011, 02:03 AM   #4
rohan tandon
Lifetime Supporting Member
United Arab Emirates

rohan tandon is offline
 
Join Date: May 2005
Location: Dubai
Posts: 190
The battery should last for a year atleast, provided you are using the original battery. What was the interval between failures?

If the failure is happening too frequently then you should change the power supply.


i hope you are resetting the fault on the power supply after changing the battery.
  Reply With Quote
Old August 10th, 2011, 02:08 AM   #5
iant
Lifetime Supporting Member + Moderator
Australia

iant is offline
 
iant's Avatar
 
Join Date: May 2002
Location: Melbourne
Posts: 3,522
where did you get the battery from
SHelf Life is limited
Also CHange over while power is on
it shoul be a lithium Ion 3.6v battery
definately not a std AA 1.5 v

Once you change it you may need to reset the fault
Don't power down under any cirmstances you will loose the program
__________________

Give all the answers
- People seldom learn.

Guide People to the posibilities
- Their Answers will come easily.
- Their Knowledge will grow.

They will then teach others

Regards
Ian Trost
  Reply With Quote
Old August 10th, 2011, 11:33 AM   #6
Farnesi
Member
Brazil

Farnesi is offline
 
Join Date: Jun 2009
Location: Brazil
Posts: 37
It is a Saft LS-14500 battery AA 3.6V

SIEMENS told me to check it's current and it is around 0.20mA. According them it should be 1.5A but I doubt it cause i m using the same battery on other S7-400 rack which doesn't point out battery failure.

Yes I reset BAF after replacing.

I'm scheduling a power supply replacement but I'm not 100% sure... Any tips?
  Reply With Quote
Old August 10th, 2011, 02:21 PM   #7
rohan tandon
Lifetime Supporting Member
United Arab Emirates

rohan tandon is offline
 
Join Date: May 2005
Location: Dubai
Posts: 190
I think changing the power supply is a good idea as the frequent battery failure is unusual.

You will loose the PLC memory on changing the power supply so make sure you upload the program. Incase you have a flash memory card then the program can be reloaded from the flash memory but the memory bit and actual values of the DB will be lost and set to initial values. If you are sure that the program on the flash memory is a working program then you dont have anything to worry about.

After changing power supply, the CPU will go into a fault on first startup requesting memory reset and then take a couple of minutes to go to run as it will do a complete memory test.
  Reply With Quote
Old August 10th, 2011, 10:24 PM   #8
iant
Lifetime Supporting Member + Moderator
Australia

iant is offline
 
iant's Avatar
 
Join Date: May 2002
Location: Melbourne
Posts: 3,522
This can damage meters so be careful
with a new battery
1. measure the battery voltage
2. set the meter to Current (10A) range
3. place the battery leads on either side of the battery and read the current - the meter could peek high - if so stop test.

do the same with the old battery

I agree with Rohan's comment.
This will confirm the battery condition
__________________

Give all the answers
- People seldom learn.

Guide People to the posibilities
- Their Answers will come easily.
- Their Knowledge will grow.

They will then teach others

Regards
Ian Trost
  Reply With Quote
Old August 11th, 2011, 10:15 AM   #9
dchartier
Member
Canada

dchartier is offline
 
Join Date: May 2003
Posts: 1,519
Quote:
Originally Posted by rohan tandon View Post

You will loose the PLC memory on changing the power supply so make sure you upload the program.
A very good suggestion, it is always preferable to do an upload of the program before attempting any major hardware change on a PLC.
However, there is a way to maintain power to the PLC RAM (we are discussing S7-400 CPUs here), using the EXT. BATT. connector on the front of the CPU module. I used to connect a 9V battery to a simple audio jack and plug it to this EXT. BATT. connector, that would give me a few hours autonomy for the program memory. There is a link to the complete procedure in this FAQ from Siemens, for those who could be interested:
How do you provide an external backup supply for an S7-400 CPU?
Hope this helps,
Daniel Chartier

Last edited by dchartier; August 11th, 2011 at 10:19 AM.
  Reply With Quote
Old August 15th, 2011, 12:16 PM   #10
Farnesi
Member
Brazil

Farnesi is offline
 
Join Date: Jun 2009
Location: Brazil
Posts: 37
I replaced the power supply and installed a flash memory card... Yes it was the power supply faulting the battery.

Thank you all

Nice to know dchartier about the ext.batt "tweak"... I thought I had to buy the battery but I can build one...
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Choosing S7 300 or 400 Plc_User LIVE PLC Questions And Answers 19 December 10th, 2009 05:48 PM
Chinese S7 300 / 400 MPI Adapter Cables John Teachout LIVE PLC Questions And Answers 5 August 5th, 2009 09:58 PM
S7 300 / 400 Arrays, How to loop it through.. adfox LIVE PLC Questions And Answers 17 July 26th, 2009 08:23 PM
S7 400 battery not work njdujian LIVE PLC Questions And Answers 4 November 4th, 2008 01:01 AM
s7 300 and 400 master slaving moazzim LIVE PLC Questions And Answers 16 April 10th, 2007 05:52 AM


All times are GMT -5. The time now is 11:27 AM.


.