ERROR - Address must be specified to the bit level

I must admit that it's been awhile since I've written a PLC program so please excuse my ignorance. I am using RSLogix 500 with a SLC. I'm creating a data file for cross-referencing my analog inputs. I thought that I had to use an integer data file for doing this AND that the addresses must be specified to the word level. Because I don't have actual input and output locations yet, I'm just pointing the integer inputs to themselves. An example would be:

---][N30:3------------------------------------------------()N30:3

This is causing the error specified in the title. What am I doing wrong? I'm sure it's something simple. Thanks for your help!
  Reply With Quote
Old August 24th, 2010, 06:00 PM   #2
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is online now
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 5,040
You have only specified the address to the word level. N30:3 is the fourth word of the integer file N30. N30:0 is the first, N30:1 is the second, etc.

The contact insruction (XIC) and the coil instruction (OTE) can only be on or off. Consequently they must be referenced to a single bit. You need to append the bit number to the word address like N30:3/00 which would be the first bit of the fourth word on the integer file N30. Adresses at the bit level of N30:3 will range from N30:3/00 through N30:3/15.
  Reply With Quote
Old August 24th, 2010, 06:02 PM   #3
harryting
Lifetime Supporting Member
United States

harryting is offline
 
harryting's Avatar
 
Join Date: May 2002
Location: Puget Sound
Posts: 969
N30:3 is an integer, N30:3/X where X = 0 to 15 is a bit. A integer in RSLogix500 is made up of 16 bits. You need to specify to the bit level for the type of instruction you are using above.
  Reply With Quote
Old August 24th, 2010, 06:02 PM   #4
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,725
Quote:
Originally Posted by lonegator View Post
I must admit that it's been awhile since I've written a PLC program so please excuse my ignorance. I am using RSLogix 500 with a SLC. I'm creating a data file for cross-referencing my analog inputs. I thought that I had to use an integer data file for doing this AND that the addresses must be specified to the word level. Because I don't have actual input and output locations yet, I'm just pointing the integer inputs to themselves. An example would be:

---][N30:3------------------------------------------------()N30:3

This is causing the error specified in the title. What am I doing wrong? I'm sure it's something simple. Thanks for your help!
The instructions you are specifying are Bit Level Instructions, addressed to a Single Binary Bit, with a State of Zero or One. The address you are specifying to go with them is a Word Address which can be either -32768 to 32767 or 0 to 65536. (Hope my memory is good) This is incompatible, and RSLogix is warning you this can't work.

I am not sure what you mean by Cross Referencing your Analog Inputs. Perhaps you can give us some details of what you are trying to do.

Stu....
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message. However, many electrons were terribly inconvenienced.
  Reply With Quote
Old August 24th, 2010, 06:02 PM   #5
Mickey
Lifetime Supporting Member
United States

Mickey is online now
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,472
You are using a word address ( 16 bit word e.g. N30:3)
You have to use a bit address with those instructions e.g. N30:3/0 for your XIC
and N30:30/1 for your OTE.

See pdf below for a little info on data file addressing.

Edit: sthompson types faster then I do.
Attached Files
File Type: pdf DataFileAddressing.pdf (117.4 KB, 78 views)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old August 24th, 2010, 06:05 PM   #6
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,725
Wow! I actually typed faster than Mickey for a change.

Edit: I am sure between the two of us, he will have a better idea what is causing his problem.

Stu.....
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message. However, many electrons were terribly inconvenienced.

Last edited by sthompson; August 24th, 2010 at 06:07 PM.
  Reply With Quote
Old August 24th, 2010, 06:08 PM   #7
Mickey
Lifetime Supporting Member
United States

Mickey is online now
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,472
Quote:
Originally Posted by sthompson View Post
Wow! I actually typed faster than Mickey for a change.

Edit: I am sure between the two of us, he will have a better idea what is causing his problem.

Stu.....
I haven't had my beer yet, but I think its time for one.
Attached Images
File Type: jpg Warm.jpg (24.1 KB, 102 views)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old August 24th, 2010, 06:14 PM   #8
STL???
Member
United Kingdom

STL??? is offline
 
Join Date: Sep 2005
Location: UK
Posts: 879
Here's mine lol
Attached Images
File Type: jpg weather.JPG (26.6 KB, 100 views)
  Reply With Quote
Old August 24th, 2010, 06:15 PM   #9
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,725
Well it only 82 and very sunny here, but I agree with you.
I am heading for the door now. Enjoy a cool one Micky, you've earned it.

Stu.....
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message. However, many electrons were terribly inconvenienced.
  Reply With Quote
Old August 24th, 2010, 06:27 PM   #10
lonegator
Member
United States

lonegator is offline
 
Join Date: May 2008
Location: West Plains, MO
Posts: 12
Many of these integers are going to be capturing/displaying various drive speeds, pressure amounts, etc. If I address to the bit level, that data won't properly display, will it? Again, sorry for my ignorance.
  Reply With Quote
Old August 24th, 2010, 06:33 PM   #11
lonegator
Member
United States

lonegator is offline
 
Join Date: May 2008
Location: West Plains, MO
Posts: 12
I'm writing the program for a plant start up. Because I'm not onsite until next week and because they want a copy of the program NOW (of course), I'm trying to do what I can to "make up" the inputs/outputs that will be used. We're using an I/O scanner and some ASB module so I can't put in any actual addressing until I'm successfully communicating with the system (right??). I made four data files (DI, DO, AI, AO) for my data. Currently I'm just pointing a data point to itself (as I showed in my example). Once I have actual address locations from the scanner/ASB module set up, I was going to substitute in the cross reference data files I'm setting up now to save having to search thru the program to change everything. (Let me know if all that does/doesn't make sense).
  Reply With Quote
Old August 24th, 2010, 06:35 PM   #12
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,725
Quote:
Originally Posted by lonegator View Post
Many of these integers are going to be capturing/displaying various drive speeds, pressure amounts, etc. If I address to the bit level, that data won't properly display, will it? Again, sorry for my ignorance.
No, it won't display properly. You will want to use an Integer Word to capture/displaying the Data. i.e. N7:0.

Stu......
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message. However, many electrons were terribly inconvenienced.
  Reply With Quote
Old August 24th, 2010, 06:38 PM   #13
lonegator
Member
United States

lonegator is offline
 
Join Date: May 2008
Location: West Plains, MO
Posts: 12
But that's how I'm doing it, I thought. I created a data file of N30 and have been addressing them as N30:1, N30:2, etc. It's giving me the error.
  Reply With Quote
Old August 24th, 2010, 06:39 PM   #14
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is online now
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 5,040
Is there any particular reason why you want to use words in an integr file for bit-level instructions instead of the B3 file?

If you feel you must use bits from N30 words for bit-level instructions be careful not to use bits from words that are being used for numeric data.
  Reply With Quote
Old August 24th, 2010, 06:42 PM   #15
lonegator
Member
United States

lonegator is offline
 
Join Date: May 2008
Location: West Plains, MO
Posts: 12
I need words though for the data I'm trying to transfer/display.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
RSSQL: specifying trigger to bit level geoplc LIVE PLC Questions And Answers 5 March 15th, 2010 05:48 AM
fishenguy fishenguy LIVE PLC Questions And Answers 54 November 13th, 2007 08:33 PM
Rotary Index Table app. gpdc LIVE PLC Questions And Answers 1 September 20th, 2007 12:22 PM
Tidbits, finding the bit number or index Peter Nachtwey LIVE PLC Questions And Answers 10 February 9th, 2006 03:17 AM
Latch a Bit then Bit Shift Left jthornton LIVE PLC Questions And Answers 2 August 22nd, 2003 06:35 AM


All times are GMT -5. The time now is 01:57 PM.


.